I have a heat pump unit where the entire unit is one

Customer Question
complete piece outside. I am...
I have a heat pump unit where the entire unit is one complete piece outside. I am getting 24v to my R and O from the thermostat which should be telling it to kick on the heat. When I trace back to the contactor I am not getting a 24v signal on the sides of it. I have a brand new thermostat and a new wire from the tstat to the unit
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
2/20/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

hello,

did you program the thermostat for heat pump?

R is 24v and O is reverse valve...but we still need the compressor to kick on which is Y.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. So I just checked and I am not getting 24v at Y on my unit. Would this be an issue on the tstat wiring?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

depends...did you program the thermostat for heat pump operation?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The tstat is wired as:
R from unit to R on tstat with jumper to Rc
Y1 from unit to Y on tstat
G from unit to G on tstat
W2 and W3 from unit to aux/e on tstat
O from unit to O/B on tstat
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

I understand....but...in the thermostat menu....did you set the thermostat for heat pump? It comes shipped for gas furnace and must be changed..what is thermostat make/model

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Honeywell RTH6350D
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

start at page 13 HERE

function 1 must be set for your heat pump system

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. I had to step away from my house for a little bit. I will try that when I get back. Would my unit be a 5 or a 7 under the function 1 since I have W2 and W3 put together at the unit
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

that will be 5.

also if the outdoor unit is a rheem the changeover valve is B.

If NOT a Rheem or Ruud it is set for O

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. Once I get back to my house and try it I will let you know
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

just respond or rate when ready

Billy

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
23,154 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I just installed a new rth3100c non programmable heat pump
I just installed a new rth3100c non programmable heat pump thermostat replacing a thermostat that was not for a heat pump. The non heat pump thermostat had been on the wall from the builder, I suppose… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heat pump based heating system died overnight. Robertshaw
heat pump based heating system died overnight. Robertshaw stat said -AC. No power at stat. Checked 24v transformer - good. Found blown fuse on control board and replaced. Still won't fire up… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a Rheem A/C Heat Pump and am trying to replace th
I have a Rheem A/C Heat Pump and am trying to replace th ethermostat. Unfortunately the old tstat was pulled off without marking any of the wires. I have traced the cable to the inside and outside uni… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Steve, Im Steve as well. My question is, I have a Nordyne
Hi Steve, Im Steve as well. My question is, I have a Nordyne h/p condenser, that I'm attempting to wire for straight cool only. Can you tell me how it's done?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi I just bought a new Therm. and it does not have a connector
Hi I just bought a new Therm. and it does not have a connector for my "o" wire. What is the "o" wire for? The connectors on the new Therm list: Y2, w2, G, W, not used, Y, R, RC conventional L ,aux/E, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
It is cold here so I am running heat. Compressor runs but air
It is cold here so I am running heat. Compressor runs but air handler will not come on even if turned to on at Tstat. I do hear a click when turned on, but nothing more...… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
experienced DIY'r & electrical engineer 2.5 Ton heat pump
experienced DIY'r & electrical engineer 2.5 Ton heat pump (split system) first symptom was AC not turning on at all Found 24VAC fuse blown in air handler and replaced it turned FAN to ON and blower wo… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
Carrier 25HBR360A310 heat pump with a HK32EA001 defrost board
Carrier 25HBR360A310 heat pump with a HK32EA001 defrost board in it. When thermostat (TSTATCCPHP01-B) is set to heat or cool, the inside blower motor (on Carrier model 58MCB120) works just fine, but t… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a HEIL Heat Pump Unit AMA004AHA1NNN-NN-NNNN4E079 My
I have a HEIL Heat Pump Unit AMA004AHA1NNN-NN-NNNN4E079 My problem I am having is the other day I heard a pop sound coming from the furnance. I opened the it up and found the fuse had popped on the tr… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
Have a Janitrol heat pump in my 400 square foot outbuilding.
Have a Janitrol heat pump in my 400 square foot outbuilding. I don't know how old but I'd say at least 10-15 years. Went out to the building and the fan was running but not heating. Themostat was set … read more
rpen7111
rpen7111
119 satisfied customers
I have a York (Honeywell) heat pump with strip heat emergency
I have a York (Honeywell) heat pump with strip heat emergency heat. New thermostat is Vision Pro 8320 3h/2c. Need where to put wires from heat pump , W,R,O,B,G,Y are wires from heat pump. Old thermost… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
I have a Trane Xe1200 heatpump with aux heat strip, currently
I have a Trane Xe1200 heatpump with aux heat strip, currently it will cool the house down, however, after it does this, the compressor continues to run unless you shut off the thermostat. Also, if you… read more
SWFLHVAC
SWFLHVAC
67 satisfied customers
i have a low voltage problen with my ducane heat pump. the
i have a low voltage problen with my ducane heat pump. the indoor unit works when thermostat set to cool but outside unit does not come on. depressed contactor and it came on. where do i go from here?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have a ducane hvac unit model FPBB100A4B. The air handler
I have a ducane hvac unit model FPBB100A4B. The air handler fan blows but the unit fan outside does not turn. Not getting low voltage signal from ducane control board. Checked thermostat and it appear… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
i have a heat pump with poor cooling poor heating. indoor fan
i have a heat pump with poor cooling poor heating. indoor fan runs constantly. in cooling i can manually close the contacts the compressor kicks on and fan runs fine i have replaced the tstat and cont… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have an older Ruud heat pump unit and it is shorting out
I have an older Ruud heat pump unit and it is shorting out the control transformer 24v side. What would would be the problem. Also the thermostat is old and has mercury tubes in it and I would like to… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Model #38YCC048-301, SN #2901E25036 Carrier Heat Pump.
I have a Model #38YCC048-301, SN #2901E25036 Carrier Heat Pump. I was away on business for a week and shut it off completely. When I returned I energized the entire system, ie: Breakers, etc. The ther… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I need a good thermostat wiring diagram that will mate a Rheem
I need a good thermostat wiring diagram that will mate a Rheem RPKA-036JAZ heat pump unit with a Rheem RBCA-1J15sFAA inside unit with heat strips to a RObert Shaw model 9515 Tstat. I would like a simp… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x