Customer Question
We have a Tranquility...

We have a Tranquility 27 geothermal heat pump system which is malfunctioning in the heating mode system and gives an error code (E2 high pressure). It is not an air flow problem (new filter), installer suspects high pressure sensor, but it is a NC switch and when the system is not operating (ie thermostat does not demand heat) it is closed. The system will generate this error after operating for a day, could this problem be generated by the TXV valve?

Contractor's Assistant: Sometimes HVAC issues that that you think will be really complicated end up being easy to fix. The HVAC Technician I'm going to connect you with knows all the tricks and shortcuts. Is there anything else important you think the HVAC Technician should know?

The system shuts itself down after generating a couple of these.

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 31 minutes by:
2/19/2016
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,512
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the problem is most common in systems over 5 years old, due to dirt accumulations in the heating coil and blower wheel... if there are furry pets in the home, or the home is located near a freeway or a farming environment that exacerbates the problem.

First step is to remove the blower access door and feel for dirt inside the concave sides of the blower wheel vanes.... if you notice any build up the solution will be to have the indoor coil cleaned professionally... or you can do it your self if you have those sorts of skill sets

Next step is make sure that the air filters are clean, and that none of the warm air vents are blocked or shut down more than 50%.

Let me know about all that, we can go from there without any time limit, If you miss me tonight I will pick your response up first thing in the morning.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Also, please let me know the last time anyone worked on the system.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The filter is new and the heating coil is a radiator style that the blower sucks air thru. It is very clean, and air flow does not seem to be a problem. The installer, who does not seem to familiar with diagnosing electrical problems, suspects that the high pressure sensor is defective. This switch in NC, do they go out of calibration and signal high pressure erronously by opening when there really is no high pressure?
Customer reply replied 2 years ago
Also, what would be the effects of a TXV malfunctioning?
Customer reply replied 2 years ago
Please respond by email, I do not have an internet connected phone.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello again.

A faulty TXV will not cause the problem. (a common misconception is that if the TXV closes too much it will back liquid up in to the heating coil and raise the head pressure seems logical, except the a restricted TXV also lowers the suction pressure and that lowers the compressor capacity so the head pressure will actually *drop in that case...that is what we observe also on these projects).

The way to tell if the pressure sensor is defective is to run the system with the service gages on it, and notice at what pressure the pressure sensor is cutting out at... ask you technician about that in detail, ask him what the exact head pressure reading is when the pressure sensor cuts out.

That pressure varies with the refrigerant used... look on the model number label and it will say Refrigerant R 410a or R-22 most likely.

Get back to me on all those details and we can go from there without a time limit.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The refrigerant is R410a, and nobody has actively done anything to the system, other than replacing the closed ground loop water pump shortly after installation, more than 4 years ago. What effect would insufficient water flow have on this problem?
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Insufficient water flow would cause high head pressure, but ONLY in cooling mode.

In heating mode, insufficient water flow would cause the *low pressure switch to trip.

Have you been dealing with the original installation contractor? or someone else for these repair issues?

If you can tell me which direction you are from the center of the nearest city I might be able to help you find a well qualified

geothermal heat pump specialist contractor.

.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
We are dealing with the original contractor, but he is not a qualified technician for this kind of detective work. His advice comes from some person in Enderby, BC. We are located in Clearwater, BC, and the closest cities would be Kamloops, and Vancouver.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks, ***** ***** a sophisticated system in a location where those sorts of service people are scarce.

You best bet is to Have me coach the contractor, with enough training so that he can diagnose your system properly, without risk of messing it up ... that will take me a few hours on line, talking with him by email, and an hour or so on the phone, etc. That is a bit more time consuming than a 'just an answer' format allows.

So, I am permitted to offer you an additional service offer that you are free to accept or decline.

It will be for $250, and take me a few days of working with your contractor to get it all sorted out.

If you accept I will send you my private email address and you can send me yours, and that of your contractor along with

his name and phone number, we can begin immediately in that case.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,512
9,512 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,512 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The head pressure slowly raises as the suction pressure
The head pressure slowly raises as the suction pressure stays steady in the cooling mode … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a 113 condenser and the suction pressure is only 15
I have a bryant 113 condenser and the suction pressure is only 15 psi and the liquid line is 198 #. is there a problem with the txv? … read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
What is the suction side pressure to be on a MR24C3F it's
What is the suction side pressure to be on a MR24C3F it's the only port and after a leak was repaired and everything vac down to 500M and new charge weighed in. It runs cool but not cold … read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
1.5 ton system brand new, lineset length is 60feet,
1.5 ton coleman system brand new, lineset length is 60feet, subcooling is 3 superheat is 72, suction pressure 40 head pressure 220 factory charge is 5 ibs 11 oz, added 1 ib 6 oz for lineset length, ev… read more
hvacdave84
hvacdave84
53 satisfied customers
I am on a service call to a system that is a brand new
I am on a service call to a system that is a brand new system. It's less then a month old. I just got a call saying that the system isn't working and I figure I was going to have a leak in the system … read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
Refilling a unit 1YO that had a very small leak but never
Refilling a unit 1YO that had a very small leak but never found it so I vacuumed and installed ProSeal super stop leak, then I started the unit and I refill with a new 25lb R410A but after several min… read more
Bill
Bill
Service Mgr
103 satisfied customers
I have a Trane XL13xi outdoor unit that has been not keeping
I have a Trane XL13xi outdoor unit that has been not keeping up with the thermostat for the past 3-4 days. It's been unusually hot but I'm unsure if I need a charge or the compressor is going out. The… read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
Carrier, 9 yr old 3 ton residential heat pump (R410a)....not
Carrier, 9 yr old 3 ton residential heat pump (R410a)....not cooling. Suction pressure drops rapidly to about 10 psig when I turned it on. High side pressure only reached about 300 #. Compressor was v… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
My outside HVAC compressor is making a vibrating noise that
My outside HVAC compressor is making a vibrating noise that I need help diagnosing. Has been going on for a couple of weeks now. Unit works but the noise is concerning. I have a video recording of the… read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
I have a new installation of a heil heat pump heat pump
I have a new installation of a heil heat pump heat pump model # NXH536000A air handler model # FEM4X3600A aux. heater model # EHK15AKB thermostat Honeywell RTH 2300/RTH221 SERIES when attempting to st… read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
This question is for Phil only please *** It's getting ready
This question is for Phil only please ***It's getting ready to warm up here in Virginia. It is supposed to be hitting 80 degrees today. You said previously you wanted the temperature in the house to b… read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
I installed a walk in cooler,compressor wont kick off on low
I installed a walk in cooler,compressor wont kick off on low pressure cut out,pulls down to 0 set to cut out at 10psi? … read more
Don T.
Don T.
President
Associate Degree
179 satisfied customers
I have a rheem unit. Cannot get supply duct temp below 62
I have a rheem unit. Cannot get supply duct temp below 62 degrees 410-ref? … read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having trouble getting more that 10 degrees of cooling between the return and the vent. I've adjusted the charge to the spec in the manual for a pi… read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
If the reversing valve has a internal short like you said is
if the reversing valve has a internal short like you said is that why my suction psi is ;low… read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
Is the head pressure & discharge pressure same thing? And
Is the head pressure & discharge pressure same thing ? And what about back pressure & suction pressure !… read more
Phil
Phil
Mechanical Engineer
9,512 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x