Customer Question
I took off the required...
I took off the required panels to access the boilers for cleaning. I also made sure that there was clear passage between the boiler section to the burners. I still get fame roll out.
James French
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
2/19/2016
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello and thanks for using this service, if you have been waiting do not worry or get upset I am just one of the techs on here and I try to get to as many customers as I can and I just picked up your question now.

It cuts off on one of the rollouts? Have you replaced the rollouts sometimes they do go bad.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
rollout next to burners replaced.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Can you see the flame when it lights up?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I see the flame. Its blue and spills out of the fire box
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Are you sure the exhaust motor is blowing good and strong and clear if so something has to be blocking the manifold or it has a crack in it. Nothing else would really cause that issue.

We are on the honor system for our time, all I ask is please rate my service using the STAR RATING SYSTEM on your page before you leave. If you are not happy with the service please let me know before leaving a negative rating. This is the only way I am paid or credited through the site for my time. This will also allow you to get directly back to me for FREE follow up questions and tips are greatly appreciated! Thanks

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
18,747 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Dunkirk PSB-4D steam boiler. The burner burn with a
I have a Dunkirk PSB-4D steam boiler. The burner burn with a 4in yellow flame and lots of soot. I have cleaned between the boiler section and resealed the draft diverter . None of this seems to affect… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Vaillant boiler model GA92-140 that set of the CO
I have a Vaillant boiler model GA92-140 that set of the CO detector. The boiler is about 23 years old and was full of soot. I cleaned the boiler and it still sets off the CO alarm. The flue is clear a… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Weil-Mclain HE-4 gas water boiler, with induced draft, shuts
Weil-Mclain HE-4 gas water boiler, with induced draft, shuts offs by Fuse Thermo rollout switch. What is wrong with it? Boiler got new control unit, vacuum switch, new blower motor. Works good for sev… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Flames roll out from under the boiler. we've tried to clean
flames roll out from under the boiler. we've tried to clean it and reduce the gas going to the boiler.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Not sure what is causing the flame roll out switch to burn
Not sure what is causing the flame roll out switch to burn out. I repalced it 2 weeks ago. It was working until yesterday afternoon. I had to bypass it in order to get the boiler working.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi I have an old Hydortherm HI 125- I suspect that the absorption
Hi I have an old Hydortherm HI 125-B I suspect that the absorption units need cleaning. I can clean the top one by removing the dome and vaccuming out the soot. How do I clean the other absorption ele… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Dear *****, Boiler info is as follows: Munchkin model 140
Dear *****, Boiler info is as follows: Munchkin model 140 M R-2 S/N H30N42221 Mfg Date 8-30-2007 installed Jan 2008 Flue passages are clear, Heat exchanger has been cleaned, Condensate flushed and cle… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Amana air command 95 furnace Its at least 15 years
I have a Amana air command 95 furnace It's at least 15 years old. I've noticed that when the burners light, there is a slight flame rollback. It is the same whether the blower motor is running or not.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a 1979 Burnham gas boiler which stop coming on, unless
I have a 1979 Burnham gas boiler which stop coming on, unless the access panel is removed (which broke off). also how can I tell if this is a 4 or 5 section burner, so I can replace the access panel.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a mod. no. P-568V furnace/boiler that I believe needs
I have a mod. no. P-568V furnace/boiler that I believe needs soot removal. Where is the acess port for this job? I know I can do this but don't want to proceed blindly. Can you explain the step by ste… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a gas hot water boiler that just recently started giving
I have a gas hot water boiler that just recently started giving off a foul odor. The chimney is clear, I was able to look up the flue pipe all the way to the roof. My hot water heater (also connected … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
lp unit new yorker water boiler was inop found flame rollover
lp unit new yorker water boiler was inop found flame rollover wires melted switch open ,removed burners cleaned scale for good open passages reinstall.(temporarily by pass one time flame switch as it … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a burnham series 2 gas boiler. When the heat is turned
I have a burnham series 2 gas boiler. When the heat is turned on the , the flame from the main burner over flows out of the chamber.… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
carrier 58 sxa 080 101 jg furnace smells real rich out side.
carrier 58 sxa 080 101 jg furnace smells real rich out side. gas pressure @ 3.5 W/C burners blue no yellow tips.it smells bad 30 foot away.from the vent. changed gas valve a while back it leaked a sma… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Have Trand Diamond 90 and it shuts off. A reset of the top
Have Trand Diamond 90 and it shuts off. A reset of the top limit switch corrects it. Looking through the site window the top burner flame is rolling up towards the limit switch. Had the system cleaned… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hi I was looking at a 1966 hillside ranch in a surb of Bufffalo,ny
hi I was looking at a 1966 hillside ranch in a surb of Bufffalo,ny with a building inspector thinking of buying. it is 1468 sq feet with a walk out basement. the boiler in on 3 zones, baseboard heat. … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
old Wards boiler ... 1930s soot backing up all over basement gas
old Wards boiler ... 1930's soot backing up all over basement gas fired cleaned the burners....they are burning yellow and not blue. should i take the entire top off and take out the insulation (black… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have a old Well &Mclain gas boiler 30 years old. The problem
Have a old Well &Mclain gas boiler 30 years old. The problem is the first initial start, It has a hard time igniteing, end result has a very abrubt start, sometimes shakes the house. The pilot is ther… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.