Burnham boiler Series 2A P205A WNM 17270999, 24 volt,

Customer Question
millivolt, 130,000 BTU boliler has no...
Burnham boiler Series 2A P205A WNM 17270999, 24 volt, millivolt, 130,000 BTU
boliler has no vent damper, no electronic ignition, is gas pilot, Control Center R82B5D, Honeywell R822U relay, Tranformer 40VA, heating system forced hot water 2 zone, one switch relay RA32A 1066 for both circulators:
Can you please show me how to put another switch so there is a switch for each
circulator?
Can you, please tell me how to diagnose if the 40VA transformer is at fault, if I need to.
Can you please tell me how I can diagnose Honey Well limit switch L4080 is at fault if I need to. Please let me know if you can help me, if so how I can pay you with pay pal and
how much.
Thank you, ***** ***** "*****@******.*** Tel(###) ###-####xtn.5301 Thank you
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
2/17/2016
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,593
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

What do you plan to use for the second relay?

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

I assume you meant your existing relay is an RA832A. Will you use another one?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
another RA832A 1066
Customer reply replied 2 years ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call. Let me know if you need more information, or send me the service offer(s) so we can proceed.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Ok, you connect your second pump hot lead to the relay terminal 3 pump neutral to 2 or any other neutral. Thermostat leads for that zone to T & T then X & X to the thermostat terminals on the boiler. These are usually R & G on the transformer relay but you mention millivolt which sounds out of place. That transformer relay is usually only used with 24 volt gas valves. The XX from the existing RA832A should connect to R & G now. The wrinkle here is that you're describing a very old 2 series. So if what I'm suggesting doesn't match up to what you see I need to know.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call. Let me know if you need more information, or send me the service offer(s) so we can proceed. Gas valve is
VS82OC1373 I do not understand what the service offer is, does this mean more money, I do not want the free trial.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Please direct any payment or subscription questions to customer service. I don't now anything about the promotions they run or subscription issues. You can contact them at

http://ww2.justanswer.com/contact-us

I only answer plumbing & heating questions. Do you have any more questions about this wiring? If you want a phone call that is an additional charge. We can continue here if you like

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call. Let me know if you need more information, or send me the service offer(s) so we can proceed. Gas valve is
VS82OC1373 I do not understand what the service offer is, does this mean more money, I do not want the free trial.
No, thank you, ***** ***** not want to continue., Please do not charge my Pay pal
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,593
24,593 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I need a steam boiler for 5000 sq ft house 2 pipe system gas
I need a steam boiler for 5000 sq ft house 2 pipe system gas a burn ham 7 section boiler was recommended to me. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I need your help. Great umm burnham model V-14AT do you have
ok great umm burnham model V-14AT do you have stock? … read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
Replacing a Gas/Steam Boiler (cracked). House is 4 stories,
Replacing a Gas/Steam Boiler (cracked). House is 4 stories, 4390 SF with Steam Radiators (standing and baseboard) and some vents. Built in 1895, has relatively poor insulation. HomeServe cane and meas… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
The transformer blew on a armstrong air handler ( when fan wheel was stuck) I bought a hon
The transformer blew on a armstrong air handler ( when fan wheel was stuck) I bought a honey well tru zone hz322 with transformer I have a at140a transformer do i hook up the white common to the black… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Burnham residential boiler that's about 8 yrs. old
I have a Burnham residential boiler that's about 8 yrs. old and the circulator pump doesn't seem to be running. I checked for power at the circulator connections in the aquastat relay and Im not getti… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
The power light is on on Burnham Revolution Gas Burner SR503,
The power light is on on Burnham Revolution Gas Burner SR503, the red zoning lights are on, but no heat is generated. If you turn the switch off and then turn it on, the boiler starts to generate heat… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
our lilehammer stove is having and issue. Pilot lights. stays
our lilehammer stove is having and issue. Pilot lights. stays lit. no oder of gas. tern stove on with switch or thermostat and the flame lights up, not fully and the flame pulses and a gas oder occurs… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have installed a heat exchanger to heat my pool, how do I wire it?
I have installed a heat exchanger to heat my pool off my boiler. All the plumbing is done. a new circulator has been installed dedicated to the pool. I need some help wiring an aquastat, flow valve, s… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
I own a Burnham Holiday Gas boiler No. 6-70. Series #1 Input
I own a Burnham Holiday Gas boiler No. 6-70. Series #1 Input BTU 375,000 Output 300,000, natural gas. The gas control valve is not working and needs replaced. Is there a replacement and how can I get … read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
I have a Burnham HE gas boiler. The circulating pump continues
I have a Burnham HE gas boiler. The circulating pump continues to run when the thermostat temperature is reached and the boiler is not heating. Is this correct or should the circulating pump turn off?… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
Looking to replace our oil-fired hot water Delco furnace that
Looking to replace our oil-fired hot water Delco furnace that was installed in 1953 with a new gas-fired boiler. Our house is approximately 5,000 sq. feet - stone - built back in 1783. Any recommendat… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
I am looking to wire up a new boiler I have the following components.
I am looking to wire up a new boiler I have the following components. My plumber is installing a new Biazi B10-4 boiler with a 40 gallon indirect water heater but he does not wire up the electrical. 2… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My oil fired Peerless MODEL EC 04 WV CAST IRON boiler is curently
My oil fired Peerless MODEL EC 04 WV CAST IRON boiler is curently fitted with a L4080B1261 Honeywell aquastat (3/4 Short 123870A} that doesnt have an adjustable high low limit, and because the boiler … read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
My 1 year old pvg5 shuts down (no power, no codes) intermittently
My 1 year old Burnham pvg5 shuts down (no power, no codes) intermittently when called for heat. Runs fine when heating only hot water. Can be reset by turning power off then on.(4zones, 3heat+1hw) Whe… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
I have a 3 zone hydronic heat system. Im using V8043E1012
I have a 3 zone hydronic heat system. I'm using V8043E1012 motorized valves with each thermostat. I am not familiar with control systems, but I've been reading alot. I needed a transformer for the act… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
I want to hear two apartments off one GWA boiler. I have wired
I want to hear two apartments off one GWA boiler. I have wired the two Honeywell 24 VAC Zones. Hower I read in the boiler's information manual that I cannot you the load off the boiler's 24 VAC tracfo… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
Hey! I have an older Burnham Series 2A gas boiler. Were
Hey! I have an older Burnham Series 2A gas boiler. We're way up in the mountains of NM so we're on propane. I do all of my repairs myself given our location and my desire to avoid the pain of having a… read more
Rick
Rick
HVAC Supervisor
24,593 satisfied customers
i need to install a transformer to a furnace for operation
i need to install a transformer to a furnace for operation of the furnace and the air conditioner. I believe there are 6 wires that need to be connected on the transformer. Where exactly do i need to … read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x