HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,897
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello and thanks for using this service, if you have been waiting do not worry or get upset I am just one of the techs on here and I try to get to as many customers as I can and I just picked up your question now. Please give me time to respond sometimes I get your replies late so there may be a delay in my response.

Does the ignitor glow and gas valve kick on?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
To give you a little more insight to the problem: 1) We have a Bryant 1-stage, hybrid system. 2) It is set, per installer, to utilize heat pump, until outside temperature drops below 35 degrees, & the heat pump can no longer bring home to desired temp. 3) at that point, the propane burning portion of the unit should kick in, i.e., the propane is set to function as E-heat. 4) If the propane portion does not kick in, after 3 attempts or so, the unit shuts off. If the outside temperature comes up above 35 degrees, you can reset the outside breaker for the unit & the heat pump will function, again, until temp drops. The installer/repair person has been out several times over the past several weeks, and can "somehow" force the propane unit to light & work short term; however, when the unit goes (due to increased outside temp) back to heat pump, the cycle described above repeats itself with propane not kicking in, when temp once again drops, as it should. THINGS THE HVAC PERSON HAS TRIED THUS FAR: 1) cleaned the unit twice & restarted each time, (& he reported according to code readings he did the following): replaced the burners, the orifices and the exchanger; each time, he restarted the unit & pronounced it fixed. His most recent visit, today, he advised he thought we should contact the propane company, since he suspected we had moisture in our tank. I called our supplier, Southern States, & explained the serviceman's thoughts. Southern states advised they put additive in each & every tanker of fuel they received & this would alleviate any problems related to moisture in any individual tank. The HVAC serviceman seems to be at a loss at this point & meantime, we are spending mega dollars trying to heat with kerosene space heater & small electric heaters. Where should we go from here?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,542
Experience: Furnace, A/C and heat pump specialist.
Verified

Let me know if you still need help with this.If so check the following and let me know.

1.Will the furnace work in emergency mode"?

2.When the propane should take over does furnace attempt the sequence below:

Inducer vent motor comes on

Pressure switch closes

Igniter lights

Burners ignite

Main circulating blower comes on

If furnaces fails anywhere in the sequence we should get an error code by blinking lights on the control board. Turn power off and back on, then call for heat.tell me how far in that sequence it goes and what error code is on first failure We will go from here.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am trying to troubleshoot a brand new system from 2017.
I am trying to troubleshoot a brand new system from 2017. System is by Carrier and is a heat pump system. Ever since install the furnace fan will not shut off. Runs constantly. Only shuts off if turn … read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
My 13-year-old PerfectHumidity 574BNW042090AB just died
Hi Richard, my 13-year-old Bryant PerfectHumidity 574BNW042090AB just died (Lots of rusty parts nearly fell out when he opened it--Needs a heat exchanger, a collector plate, and an inducer motor, for … read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
I have a York Affinity YZH03611CA 3 ton Heat pump with auxiliary
I have a York Affinity YZH03611CA 3 ton Heat pump with auxiliary propane back up. (YPC80 variable speed furnace) This has happened 3 times when the temperature was between 36 and 40 degrees. Heat pump… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
what would cause my honeywell thermostat to loose the option
what would cause my honeywell thermostat to loose the option to select heat mode with my lennox furnace/heat pump, and how do I fix it. One day the options were: Cool, Off, Heat, Em Heat. The next day… read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
I have a Bryant through the wall heat pump installed in my
I have a Bryant through the wall heat pump installed in my condo, (circa very early 90's). I am replacing the current thermostat with a new Lutron HVAC controller. The old thermostat had the following… read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
Hi We are replacingvour old CAC system. I had several people
Hi We are replacingvour old CAC system. I had several people come in for quotes and opinions. Have it narowed down to two but i am confused. Both offer verybdifferent systems. System 1: rheem 4 ton mo… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,897 satisfied customers
What A/C unit and coil is best to match with a single stage
I live in Los Angeles. I currently have a single stage Carrier 58MCB100---11120 furnaces. I will be redoing all the ductwork with R-8. I am trying to figure out which A/C unit and coil to match it wit… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
Hi, Can a Lux TX500E thermostat replace a Bryant HH07AT187?
Hi, Can a Lux TX500E thermostat replace a Bryant HH07AT187? If so, how does the wiring transfer over? Bryant has terminals Y-G-R-O-E-L-C-W2 and Lux has RH-RC-Y-W-G-O-B... the RH and RC came with a jum… read more
airheatman
airheatman
HVAC Technician
9,542 satisfied customers
My Carrier heat pump unit does not shut off when its cold outside
I have a carrier heat pump unit, electric furnace, and a TP-PRH-A thermostat. There is an outdoor sensor that seems to be fairly accurate when compared to other thermometers. Anyway on to problem. Whe… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Im replcing a heat pump thermostat with a Honeywell VisionPro
I'm replcing a heat pump thermostat with a Honeywell VisionPro TH8000. The old Thermostat (Bryant System - I think a White Rogers stat) used the W1 and W2 contacts, and the new thermostat doesn't have… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox 10hpb series unit, back in July we were hit
I have a Lennox 10hpb series unit, back in July we were hit by lightening, not the pump just the thermostat in the house, we were told we didn't have to use a lennox thermostat but a honeywell was com… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Trane XL80+heat pump with Honeywell Pro2000 (TH2210D) tstat
I have a Trane XL80 (2 stage) + heat pump with a thermostat wiring terminal labeled: W2 W1 R G B/CY The Honeywell Pro2000 thermostat (TH2210D) is a 2H/1C model with terminals labeled: R C Y G O/B Aux/… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I think my furnace is using way to much propane. I have burned
I think my furnace is using way to much propane. I have burned 100 gallons of propane in the last 25 days. We keep the thermostat on 68-70 at night and turn it down to 65 during the day. I have a new … read more
Gary Brufach
Gary Brufach
Owner Operator
Vocational, Technical or Trade Scho
12 satisfied customers
Bryant Model Number FY4ANF030 - I replaced the standard thermostat
Bryant Model Number FY4ANF030 - I replaced the standard thermostat control with a hunter programmable thermostat. What is the standard wiring configuration for the bryant system? Should the fan come o… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
i have a bryant thermostat bryant BBBHP01-B and there were
i have a bryant thermostat bryant BBBHP01-B and there were 6 cables colors white, Orange, Green, red, blue and Yellow. How do I hook it up to a Lux with a G, RH, RC (with bridge between), Y, O B, C… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
We have a 3 year old Bryant 350 Single Stage Furnace. Just
We have a 3 year old Bryant 350 Single Stage Furnace. Just this week after running several heat cycles the furnace begins to make a buzzing noise on start up before the blower fan begins...never heard… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I am attempting to hook up a thermostat to my HVAC system,
Hi, I am attempting to hook up a thermostat to my HVAC system, the thermostat was wired with colors that are nonstandard to the unit according to the diagram. I am attempting to replace a goodman ther… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
what is a good temperature to set the furnace lockout at
what is a good temperature to set the furnace lockout at? I have my heat pump lockout set to 35 degrees. Should it be 35 degrees or X degrees more than I set the heat pump?… read more
BOILERMAN856
BOILERMAN856
Owner/ HVAC Technician
Vocational, Technical or Trade Sch
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x