I HAVE A UNIT PURCHASED IN 2014 THAT NEVER PROPERELY RAN RIGHT. TOOK IT BACK TO THE DEALER AND HE PUT IT ON A HOSE AND IT RAN FINE. WE TOOK IT BACK RE-INSTALLED IT AND THE UNIT KEEPS GOING INTO RED LIGHT INDICATOR MODE AND NOT OPERATING
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 28 minutes by:
2/15/2016
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Sounds like it is going out on head pressure not enough water flow thru condenser. does this system have a pump that pump water thru from a well or a loop system. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
It's a loop system comes right out of the water coming into the building and then drains right back out but there are no pressure valves attached just a 3/4" water line going in 3/4" water line goong out when we turn on power to the unit the green indicator light on the unit stays lit foe about 30 seconds and then turns red the unit. Never turns on
Customer reply replied 2 years ago
I understand that probably is the cause but what can be done to rectify the issue
Customer reply replied 2 years ago
it has a full 3/4" water line coming in to the building not on a well. could it be that it is draining the water to quickly and pressure does not have time to build up?
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

To make proper diagnosis gages would have to used on unit to see what the refrigerant pressures are running. I need to know what the high side pressure is doing when unit starts up. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the unit never actually starts up
Customer reply replied 2 years ago
what if I closed off the drain and let the water fill up in the unit and then try to turn it on with that create an unsafe condition or a back pressure
Customer reply replied 2 years ago
What does it have to be circulating in order for the unit unit to kick on
Customer reply replied 2 years ago
I'm a licensed master electrician and I have been installing wiring to AC units for 30 years this is the first water cooling unit I've worked on
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

If you can get a set of gages I can walk thru the procedure for checking pressures. Really need to know what the head pressure is doing. Does not sound like it is getting enough water flow. Can you see where the water comes out of the unit. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the water outlet is connected to a hose its dumping water at the same rate that it is inputting it . this unit belongs to my cousin and I am 2000 miles away right now the last time I was there which was last month I tried to help him troubleshoot the issue. I will be going back in a few weeks. I will get a set of gages and then get back with you for guidance. do you mean a triple set of gauges with red yellow and blue hoses?
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Yes You will know as soon as you install gages and start unit if it is water flow problem. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My ac unit turns off after approx 1 hr of operation. A red
My ac unit turns off after approx 1 hr of operation. A red light on the front comes on. I have had the unit almost a year with a lot of operating time. Never had a problem. While gone a week. There we… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Have a Rheem furnace model# RGRA-10AJS. No heat problem. Two
Have a Rheem furnace model# ***** No heat problem. Two days ago deraft inducer fan would not run, had voltage. If you spun squirrel cage to get started it would run but would not start on its own. Rep… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Honeywell vision pro8000 connected to heat pump.
I have a Honeywell vision pro8000 connected to heat pump. In the upper right hand corner, (not on the screen) but on the frame is a red light that on occasion will be on. What does this red light indi… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 1991 Bryant furnaceProblem started with the
I have a 1991 Bryant furnace Problem started with the thermostat, not sending 24v signal to the furnace control board. While this was being changed the service man cleaned the unit, pulling the burner… read more
Expert
Expert
my goodman furnace is blowing cold air, went up to attic and
my goodman furnace is blowing cold air, went up to attic and I hear water moving in the pvc pipes (vent to roof) and it will not ignite.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a York h/p with vp8000 stat. Unit runs continuously
I have a York h/p with vp8000 stat. Unit runs continuously and red light on stat flashes 3 times, continuously. Room keeps temp as well. What is light telling me?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
hello we have a new trane TAM7 and all LEDs show proper operation.
hello we have a new trane TAM7 and all LEDs show proper operation. fan runs fine in cooling and heating mode. however can't get dan to come on for fan only /circulation mode. using a nest thermostat w… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
In August of this year, I purchased a Bryant High Efficiency
In August of this year, I purchased a Bryant High Efficiency Furnace, Model 987MA66100V21. A little over two weeks ago, the furnace came on in the morning (6 AM, Saturday) according to the programmed … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
my Trane 4 ton 16 year old gas pack does not ignite about half
my Trane 4 ton 16 year old gas pack does not ignite about half the time. Everyone I get to check it out says they can't diagnose or fix when it is working fine when they come. I need to know what the … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
hello We've just moved in to a new apartment, (recently built) Aircon has acted up,
hello We've just moved in to a new apartment, (recently built) Aircon has acted up, no matter what we do the TIMER light just keeps flashing. Best we can do is getting it going for a min, then timer l… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Category-Gas Furnace--Installed new Day&nite N8MSL furnace
Category-Gas Furnace--Installed new Day&nite N8MSL furnace replacement. Recently, I replaced the thermostat without knowing the total problem. My renter reports that the furnace lights up, blows cool … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Two years ago I purchased a 5 ton York Affinity 2 stage compressor/variable
Two years ago I purchased a 5 ton York Affinity 2 stage compressor/variable speed blower Heat pump and AC unit. Heat strips were also installed to defrost the coils in cold weather. Since then I have … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
have a baxi bermuda 51/5 back boiler and the indicator light
have a baxi bermuda 51/5 back boiler and the indicator light is frequently turning red and we are having to re light the boiler every time this happens the ciciut board was replaced about two years ag… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
3 satisfied customers
Our trane XR80 furnace red light was flashing continously calling
Our trane XR80 furnace red light was flashing continously calling for heat but nothing happened. Called our energy company who came out and determined we needed a new thermostat. We purchased a new ho… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York heat pump, built in the 80s that worked fine
I have a York heat pump, built in the 80's that worked fine in A/C mode all summer. In the winter heating season the outside unit was covered in ice and the thermostat in the house had a blinking red … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,358 satisfied customers
I have a Heil 5 ton roof top mounted condensor and the air
I have a Heil 5 ton roof top mounted condensor and the air handler is about 45 feet away on the first floor. the unit is freezing up and is not cooling. The unt will not take adequate refrigerant and … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
had a 5 ton ruud installed with a seer raqting of 11.2 and
had a 5 ton ruud installed with a seer raqting of 11.2 and it ran fine for 12 years. i replaced it with another 5 ton ruud with a seer rating of 13. at the same time i replaced the evaporator with a n… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
No heat service call on Luxaire M/N TG9S080B12MP11A S/N WOH8185394.
No heat service call on Luxaire M/N TG9S080B12MP11A S/N WOH8185394. Diagnostic light indicates 9 flashes, which is ground or polarity fault. Checked all wiring from panel to furnace and all is well. A… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x