Domestic hotwater is the priority zone but does not maintain…

Customer Question
Domestic hotwater is the priority...
Domestic hotwater is the priority zone but does not maintain the hotwater temp when heating goes down at night or is not called for. Takes several cycles of running hotwater to raise temperature. Weil McClain Gold plus 30 tank. Aguastat has been replaced & drywell is good.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 28 minutes by:
2/15/2016
HVAC Technician: Daniel Plourde, HVAC Technician replied 2 years ago
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 464
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified

Hi I am dan I can help you with this. The priority means that if the tank zone calls for heat then it will turn off the heating zones until the tank is satisfied. Are you having problems with the domestic water heating up or the boiler water?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Domestic hotwater temp is not maintained when heating is not called, overnight or when zones are not calling for heat. Takes several cycles of running domestic hot water to raise temp. New aquastat on W.M Gold plus30 has been installed.
Customer reply replied 2 years ago
System was fine until a few months ago.
Customer reply replied 2 years ago
Circulator s are fine
HVAC Technician: Daniel Plourde, HVAC Technician replied 2 years ago

When the heat is calling is the temp fine? Is it just a problem when the heat is off? How old is the tank?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Sorry for the delay we lost our internet connection. Temperature is fine when one of the other zones are calling for heat. The tank is about ten years old. Drywell is fine, no moisture and thermostat was just replaced. Priority switch is on.
HVAC Technician: Daniel Plourde, HVAC Technician replied 2 years ago

ok was the aquastat changed after the problem or did the problem start after the aquastat was replaced. Also what is the model number of the aquastat.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Was changed after the problem but did not fix the problem.
HVAC Technician: Daniel Plourde, HVAC Technician replied 2 years ago

ok what is the model of the aquastat and the zone pannel?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Zone panel is aTaco E20B the boiler aguastat is a Honeywell dual aquastat type L4081B, the thermostat on the hot water tank is is a T100 30°C 70°C
HVAC Technician: Daniel Plourde, HVAC Technician replied 2 years ago

ok the next thing i would look at is the zone panel. first thing i would try is switching the tank wires to one of the other zones and see if that helps the problem or if you get a problem with the zone you switch to the priority zone

Ask Your Own HVAC Question
Customer reply replied 2 years ago
That is going to take some time. Does it matter how fast I get back to you?
HVAC Technician: Daniel Plourde, HVAC Technician replied 2 years ago

no i relize it will take some time to test that out. just reply back when you can. what we are testing is the zone board may be bad or maybey intermitent where is does not always bring the boiler on when the water heater calls but turns on the circulator

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a series 2 and think it needs to be reset. The
I have a series 2 and think it needs to be reset. The problem is its making hot water but will not pump through the house. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a weil-mclean boiler and a Taco 404 zone valve controller.
I have a weil-mclean boiler and a Taco 404 zone valve controller. 3 heating zones plus a side-arm hot water heater is the 4th zone. The hot water zone is the Priority zone. about once a week the boile… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have three zone gas boiler heat. I am currently only using
I have three zone gas boiler heat. I am currently only using 2 zones - zone 3 is a priority for tankless hotwater and zone 1 is for the downstaris. right now, the zone 3 is wokring fine , but zone 1 w… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil-Mc Lain Gas Fired Boiler in my house. Model
I have a Weil-Mc Lain Gas Fired Boiler in my house. Model CG7 SPDN (series 12) input BTU 210,000. The heating system has - Two zones for radiant heat. - One Zone for hot water tank. - Four zones for b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
baxiht380 short cycles in heat mode does not maintain constant
baxiht380 short cycles in heat mode does not maintain constant temp flame does not modulate heat ex must max out then it shuts down heat zones continue to run dont think its internal pump it wouldnt e… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Weil-Mclain Ultra gas fired boiler and a Weil-Mclain
I have a Weil-Mclain Ultra gas fired boiler and a Weil-Mclain holding tank. The water is scalding hot at the tap. The factory setting is 140 degrees. Do I simply lower the factory setting to adjust th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a weil-mcclain propane fired boiler-we have gone through
I have a weil-mcclain propane fired boiler-we have gone through nearly 1/2 of a 500 gallon tank of propane since oct. 1, and had the thing turned off most of that time. When it is running, it runs all… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
The problem is with a Weil-McLain high efficiency furnace with
The problem is with a Weil-McLain high efficiency furnace with hotwater heater. The furnace was in lockout mode when I woke up. After resetting the lockout with message "high temp", the furnace indica… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello, I have a Weil-McClain CG PFG-5 home boiler. When it
Hello, I have a Weil-McClain CG PFG-5 home boiler. When it was installed (5 years ago) the installer set the water termperature to 220. The Unit has been relatively trouble free. We had a technician i… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Our CG Series 12 Weil-McClain gas boiler is making a howling
Our CG Series 12 Weil-McClain gas boiler is making a howling sound periodically which seems to happen shortly after it kicks on. The Weil-McClain service man we hired to look at it is stumped. He says… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I am not getting hot water, it is warm, though. I have a Superstor
I am not getting hot water, it is warm, though. I have a Superstor SSU-45 with the temp set to 140 degrees. I have a Weil McClain (sp) gold series with a Honeywell Aquastat relay L8148a set to 200 deg… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
At what settings should the Hi and Lo limit switches be set
At what settings should the Hi and Lo limit switches be set to? I have a Weil - McClain boiler without the hot water coil installed. I have a Amtrol 41 gallon boilermate connected for hot water. I am … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
7124 Aquastat It was installed (back when ) with the LO
7124 Aquastat: It was installed (back when??) with the LO on "disable" and HI set at 190. Very tight and well insulated older two story house with modern DPane windows etc. it holds heat beautifully. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am going to list the items used in this application 1.
I am going to list the items used in this application: 1. Weil-McLain Ultra 155 with PHD technology (Gas fired) 2. Weil-Mclain Plus-Line 80 Indirect fired water heater 3. 8-Taco 007 circulators for zo… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
We have a Weil Mcclain gas boiler, model GV Gold. The technician
We have a Weil Mcclain gas boiler, model GV Gold. The technician was here the past two days, but the unit still does not remain on. The unit is about 10 years old. Here is what I understand: 1)All the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I just purchased this house, it has hot water baseboard heat.
I just purchased this house, it has hot water baseboard heat. It does not have seperate water heater. This heats the upstairs (raised ranch)downstairs has elec heat and elec water heater just for down… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I just installed a L8148 Aquastat relay to replace a 22 year
I just installed a L8148 Aquastat relay to replace a 22 year old relay that had mechanical failure. My furnace supplies forced hot water heat as well as hot water (no separate hot water heater). My he… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
what brand of brand of boiler would you recommend to replace
what brand of brand of boiler would you recommend to replace this heating system with a burnham rs109 tankless hot water?? not looking a boiler with all "bells and whistle" controls,,, a high efficien… read more
macleaner
macleaner
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x