I have an American Standard 2 stage furnace model

Customer Question
I have an American...

I have an American Standard 2 stage furnace model AUD800R936K5 and it will light but then go off, it does this several times then the blower comes and and no heat.

Contractor's Assistant: Sometimes HVAC issues that that you think will be really complicated end up being easy to fix. The HVAC Technician I'm going to connect you with knows all the tricks and shortcuts. Tell me a bit more about what's going on so we can help you best.

Could it be the thermostat?

Contractor's Assistant: Is there anything else important you think the HVAC Technician should know?

No, up until this morning it was working fine. I also changed the filter

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
2/14/2016
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,897
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello and thanks for using this service, if you have been waiting do not worry or get upset I am just one of the techs on here and I try to get to as many customers as I can and I just picked up your question now. Please give me time to respond sometimes I get your replies late so there may be a delay in my response.

Remove and clean the flame sensor rod with some fine sand paper or an emery cloth. That is the rod by the burner that has 1 wire attached to it and is typically held in with 1 screw. Just take that out and clean the rod off good and try it.

We are on the honor system for our time, all I ask is please rate my service using the STAR RATING SYSTEM on your page before you leave. If you are not happy with the service please let me know before leaving a negative rating. This is the only way I am paid or credited through the site for my time. This will also allow you to get directly back to me for FREE follow up questions and tips are greatly appreciated! Thanks

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,897
18,897 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trane 2 stage furnace blowing cold air. Diagnostic codes
Trane 2 stage furnace blowing cold air. Diagnostic codes show normal call for heat units starts then blows cold air … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My American Standard FREEDOM 90 works on electric but not on
My American Standard FREEDOM 90 works on electric but not on propane. Red light is a steady blink every second. Gas valve is open air filter is clean, propane tank is full. Have not used the propane s… read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
I have a new trane heat pump installed this summer, we made
I have a new trane heat pump installed this summer, we made modifications to the air handler, did not install the heat strips, instead I took the old core ( forced hot air, water, oil ), and installed… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
No heat - I have a Trane XV 80 gas system with a White Rodgers
No heat - I have a Trane XV 80 gas system with a White Rodgers 50A51-507 controller. Thermostat (Train XT 302C) is calling for heat (System is on heat and little flame is on) but nothing is happening.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an American standard single stage 90. 2 thermostats
I have an American standard single stage 90. 2 thermostats up and down. Down calls for heat shuts down when temp is reached no problem. Upstairs which also controls the ac calls for heat and shuts dow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
American standard freedom 78, model AUD080c936B0- converted
American standard freedom 78, model AUD080c936B0- converted from natural gas to propane. Furnace lights blower comes on runs about 30 secs and goes off, furnace stays lit and continues until it trips … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
My furnace is out. Furnace fan runs when bathroom vent fan
My furnace is out. Furnace fan runs when bathroom vent fan is on. Gas supply valve to unit appears to be on. Replaced furnace filter, used Canned air to dust off thermostat, inside furnace circuit boa… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an Ammna Hi Eff 80 Furnace and an American Standard
I have an Ammna Hi Eff 80 Furnace and an American Standard Heat pump. This AM I heard the Heat Pump Running but noticed that the furnace fan was not operating. I went to the thermostat and kicked the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a year-old 2 stage ruud gas furnace. A bad thermostat
I have a year-old 2 stage ruud gas furnace. A bad thermostat was recently replaced. The new one will not go to stage 2 (no +2 on the indication). Is there anything I can check? I don't want to pay the… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
we have a carrier 2 stage furnace, I intalled a honeywell rth6350
we have a carrier 2 stage furnace, I intalled a honeywell rth6350 thermostat. The A/C worked fine, the heat will not come on sometimes when it is programmed to. If I turn the electric power switch on … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have an American Standard Freedom 90 I cant find a model
I have an American Standard Freedom 90 I can't find a model number are serial number. It is 11 years old. The burner lights but Blower does not come on. I can jumper the blower and it works. Can the f… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have an American Standard 2 stage gas furnace about 5 years
I have an American Standard 2 stage gas furnace about 5 years old Never had a problem till now. Furnace is on electronic pilot works. Furnace blowing cold air. First stage is on second stage starts to… read more
freon
freon
Owner
High School or GED
214 satisfied customers
I have a lennox elite g26q3-75-2, When in heat mode the blower
I have a lennox elite g26q3-75-2, When in heat mode the blower motor does not come on, the burners will ignite and stay on until it overheats and shuts off. but if i select fan on the thermostat contr… read more
John
John
High School or GED
27 satisfied customers
I have American Standard Freedom 80 multi stage gas furnace
I have American Standard Freedom 80 multi stage gas furnace with White Rogers 1F91W-71 thermostat. Occasionally, (about once per week) after a morning startup the fan remains running when furnace stop… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My neighbor has a Model 1200 Braeburn thermostat. He wants
My neighbor has a Model 1200 Braeburn thermostat. He wants the American Standard heat pump he has to go up to 81 degrees, then cool down 6 degrees to 75 degrees before it goes on again. I set D1 to 81… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
what is the difference between a two stage and three stage
what is the difference between a two stage and three stage furnace and how great a difference is there between a 14 SEER and 16 SEER 4 ton AC unit?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a forced hot air, gas fired furnace controlled by an
I have a forced hot air, gas fired furnace controlled by an analog thermostat, like the one posted on your web-page. When I set the temperature above what the room is at expecting the heater to come o… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
American Standard model auy080r9v3 freedom90 2 stage gas furnace
American Standard model auy080r9v3 freedom90 2 stage gas furnace will not switch to 2nd stage. Unit has a cnt 03078 controller. This board was an upgrade installed two years ago which required wiring … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.