Ran across a 2010 Trane unit with a TCONT803AS32DAA Trane thermostat. The customer would put it in heat mode, the unit would come on and almost immediately go into auxillary heat and the temp would fall. The condensor was tryng to run but would cycle on and off. Checked the charge, caps and verified it had high voltage. I am leaning toward a control board in the condensor.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
2/14/2016
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,335
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

How long would it run before it cycled off. You checked charge was pressures ok in the heat mode. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I was charged 28 dollars for this response?? So far, not satisfied at all.
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Trying to respond to you. When it was running in heat what were pressures on the unit. Suction and head pressure. If the thermostat is set 3 to 4 degrees below set point the Aux heat will come on. I am a Trane dealer for 27 years I work on these everyday. Did you check true suction to see what suction pressure was doing. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

I have to ask you questions to get info for troubleshooting. Thanks

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Looks like you posted question twice. Taconite803 is the same as the Honeywell Vision Pro 8000D. Be glad to continue with you. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
In heat mode the head pressure was above 100 at about 65 degrees ambient. In cool the pressures were 84/211 (410A). The unit came on in heat and ran about 3 minutes and cycled off. It tried to cycle back on in heat but kept shutting off (this is at the condensor). In auxillary heat the air handler ran but the temp at the plenum never got above 73 degrees.In cool the condensor never came on, had to manually energize the contactor in order to get those pressures. The problem is at the condensor but also concerned about the low temp in auxillary heat.
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Seems low on gas to me. What model condenser and air handler are they using. Did you take an amp draw on electric heat. What KW is electric heat. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

If this is a Trane or American standard you can take left side panel off and check true suction and head pressure there. If head is running 100 psi in heat need to know what the suction is doing. Good info. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Its a Trane, checked pressure at ports behind panel at condensor, suction pressure in heat was about the same. Never checked amps at heater which is a 10 kw. I actually added gas to it but did not want to overcharge.
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

10 KW should be putting out more heat unless its on a 4 ton unit. Should be a charging chart inside cover for charging in heating. Just cross inside dry bulb with outside dry bulb and that will get you close. Sounds low on refrigerant. Russ

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Inside uint blowing but outside condenser not coming on.
inside uint blowing but outside condenser not coming on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I'm replacing a old trane thermostat (baysenso19c) with a
I'm replacing a old trane thermostat (baysenso19c) with a Honeywell (th831r1001) the old trane has numbers instead of letters so I don't know where to plug the wires into the new honeywell … read more
Bill
Bill
Service Mgr
100 satisfied customers
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE ERROR CODE I AM GETTING SAYS "EE" =compressor relay contacts welded … read more
Bill
Bill
Service Mgr
100 satisfied customers
The condensate pump on my xe90 is cycling on and off. 1st
the condensate pump on my xe90 is cycling on and off … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
HVAC question I have a Carrier condenser unit that was
HVAC question I have a Carrier condenser unit that was running this morning when the heat was on in the house. The thermostat was set for heat? Model number 38TGO30300. I through the outside breaker b… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Looking to buy replac ement condenser to model nac036akc3
Looking to buy replac ement condenser to model nac036akc3 serial e040516483 … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
My Trane Thermostat has a screen and is unresponsive....
My Trane Thermostat has a white screen and is unresponsive.... common problem or something more?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My trane thermostat is blowing hot air when the system say
my trane thermostat is blowing hot air when the system say cool … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a three zone Trane thermostat system with a Hyperion
I have a three zone Trane thermostat system with a Hyperion air handler and a Goodman heat pump. Two of the three zone work okay but the third zone does not work. This was done by the builder. Should … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,335 satisfied customers
I have a Trane thermostat xl824 and the screen is flashing.
I have a Trane thermostat xl824 and the screen is flashing. I can't turn the heat on. No problem with the fuse box any ideas? This morning I started to change the thermostat and stoped. Replaced all t… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
452 satisfied customers
Ihave a 15 year old trane thermostat I am replacing.I
ihave a 15 year old trane thermostat I am replacing.I purchased a Honeywell rth111 to replace it with.I am not sure about the wiring of the new one.Can you help … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a trane heat pump with an old trane thermostat. I'm
I have a trane heat pump with an old trane thermostat. I'm wiring in my nest but my black wire was in x2 on old. I don't have an x2 on nest … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a a trane thermostat that I want to replace with a
I have a a trane thermostat that I want to replace with a radio thermostat thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,796 satisfied customers
Our trane thermostat was blank this morning and we can't get
Our trane thermostat was blank this morning and we can't get it to go back on. Yesterday, although we had a display, the ac wasn't working properly. The unit was running, but even set at 65, the insid… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x