I'm troubleshooting a Rheem heat pump system and I was

Customer Question
experiencing a problem with the...
I'm troubleshooting a Rheem heat pump system and I was experiencing a problem with the 3 amp fuse blowing which inops the system. Found defective thermostat and replaced with Honeywell non-programmable Digital Thermostat Model RTH3100C . With system on there is no heat. The blower is on as well the heat pump. Notice the indoor line going to indoor condenser is cold as if heat pump is in AC mode.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
2/12/2016
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi I'm Brian and I'm here to help!

On Rheem heat pump units, the reversing valve needs to be energized in heating. This means you should not have a connection at O but instead move the wire from O to B. (I'm pretty sure the RHT3100C has BOTH an O and a B terminal). If the thermostat has an O/B terminal then the reversing valve wire should be connected there and the thermostat setup will have to be changed so it energizes the reversing valve in heat instead of cool. That should take care of your problem! (unless of course your reversing valve coil is burnt up and that was the reason the fuse was blowing!)

Let me know if you have further questions on this subject. Otherwise, please remember to rate before leaving (3 stars or higher please!). Bonuses are always appreciated! Thanks for allowing me to help and thanks for using Just Answer!

Thank you,
Brian

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hello again. I removed wire from O terminal to the B terminal. I turned system on and after 5 min delay system turned on and fuse blew. Disconnected wire at air handler which inputs to the defrost board outside which outputs to reverse valve signal and found a short. Disconnected outside at heat pump(defrost board) and confirmed this wire is shorted. Switched to a Different wire (spare). Turned system back on in heat mode and found the condenser was still operating in cool mode. The indoor condenser and piping was cold. I gone to the defrost board and visually confirmed the output signal actually comes out from the defrost board. I gone to the terminals marked reverse valve and found no voltage. Would it be a safe consumption to say the defrost board is bad? I did find one that's available but wanted to make sure if I troubleshooted to the fullest every possible fault.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago

Hello again Al, I'm sorry it took so long to respond. I was away for the weekend.

It sounds like you have a volt meter so let's diagnose the system with that and a few logical steps as well. From your explanation of the symptoms, it sounds like it's either a shorted reversing valve solenoid, a defrost board that's failed or both. It sounds like you have your thermostat wired up right now with the reversing valve wire to B.

I would first disconnect the reversing valve itself from the defrost control board, I'm referring to the 'output' side of the defrost board, not the B wire thermostat connection to the 'input' side of the defrost board. Then ensure you have a good fuse in the air handler and turn power back on. Put the system in heat and measure the voltage at the outdoor unit from C to B at the defrost board. You should have ~24 volts ac. Now measure from C to the 'output' side of the defrost board reversing valve connection, you should have ~24vac there as well. If those checks pass, your defrost board is fine, if the checks don't pass, you have a failed defrost board.

Now with power off to the system and the two reversing valve coil wires disconnected, you should measure the resistance between the two reversing valve wires with your meter set to its lowest resistance scale (Rx200, Rx400 etc..). Let me know what you find. Alternatively, if the defrost board showed failed in the voltage check above, you could bypass the defrost board reversing valve relay by disconnecting the thermostat B connection and connecting it directly to the reversing valve coil wire that was on the output side of the defrost board. The other reversing valve coil wire should be connected to 24 volts common somewhere in the the circuit. If you can give me the model number of the outdoor unit, I can give more specific instructions. When you bypass the defrost board to reversing valve coil, turn all power back on and see if the fuse blows. If it does, you have a shorted reversing valve coil and will need to replace it. If the fuse doesn't blow and the system goes in to heat, you just have a failed defrost board.

Let me know how that goes and we'll go from there.

Thanks,

Brian

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
1,024 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Where can I purchase 2-#-1773es-03 Honeywell thermostats? I
Where can I purchase 2-#69-1773es-03 Honeywell thermostats? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
JUST INSTALLED HONEYWELL THERMOSTAT RTH3100C. AC WILL NOT
JUST INSTALLED HONEYWELL THERMOSTAT RTH3100C. AC WILL NOT COME ON. THE WIRING IS, Y R G AND W. DOES THE W WIRE GO INTO THE AUX? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier split heat pump system that failed. Outdoor
I have a Carrier split heat pump system that failed. Outdoor unit 38YCC060 with and in-door unit FA4BNF060 tied to a non-programmable carrier thermostat model no. TSTATCCNHP01-B set to the auto mode. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I just installed a new rth3100c non programmable heat pump
I just installed a new rth3100c non programmable heat pump thermostat replacing a thermostat that was not for a heat pump. The non heat pump thermostat had been on the wall from the builder, I suppose… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I set the temperature at 76 degrees in summer and wake up
i set the temperature at 76 degrees in summer and wake up the house is at 70 degrees AC is blasting with a honeywell ultrastat whats wrong i do not want to go below 76 degrees… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Replaced Honeywell non-programmable thermostat with a
replaced Honeywell non-programmable thermostat with a Honeywell programmable thermostat. System blowing hot air when on cold setting (heatpump setup)… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell thermostadt RTH74001008. I came to vacation
I have a Honeywell thermostadt RTH74001008. I came to vacation house & it was set at 55F. I set to 70F. Temp was climbing & then stopped. I noticed no LED readout on front of thermostat. I replaced ba… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Non-Programmable Digital Thermostat RTH3100C, have heat pump
Non-Programmable Digital Thermostat RTH3100C, have heat pump with gas heat as emergency as back up. Name and type of old thermostat not none. It has the following wires connected Y, M, R, VR, V and F.… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have a McQuay Enfinity Vertical Water Source Heat Pump
I have a McQuay Enfinity Vertical Water Source Heat Pump that I recently replace the thermostat on. The original thermostat was a McQuay P/N XXXXXXXXX Single Circuit electronic thermostat. I am switch… read more
V12Tech
V12Tech
252 satisfied customers
Heat not coming on, replaced thermo with Honeywell RTH3100C
Heat not coming on, replaced thermo with Honeywell RTH3100C does heat and cool fan in auto. Old unit not wired properly, no tags. I can get ignition of gas furnace but still blowing AC, no heat. Wires… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem air handler RHLA HM4821JA at night and early morning
Rheem air handler RHLA HM4821JA at night and early morning air handler comes on without condensing unit (inside set at 78)for about five seconds and inside temp below 78 many times///noon and as outsi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an asha10a heat pump system with a new honeywell rth3100c
I have an asha10a heat pump system with a new honeywell rth3100c thermostat. In emergency heat mode, the blower does not shut off. will putting a jumper from E to Aux on the thermostat correct this?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im attempting to replace my original thermostat with a Honeywell
I'm attempting to replace my original thermostat with a Honeywell RTH2300. System is a Rheem AC & heat strip system. Non heat pump. Original stat has 6 wires marked B, Y, R, G, W2, & E. New stat wirin… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I currently have a White-Rodgers mercury thermostat on my Carrier
I currently have a White-Rodgers mercury thermostat on my Carrier Heat pump system; which has heat, auxillary & emergency heat along with cool on it. What is the best thermostat with which to replace … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hello Carrier Service, I replace the Pcb last summer, The
Hello Carrier Service, I replace the Pcb last summer, The cold system work ok, but when the winter come the heat system no working, no heat, the 5 a fuse in PCB keep blow out . What is the problem? My… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I would like to update my heil (model # haxcoo4tw01, 2 stage
I would like to update my heil (model # XXXXX 2 stage heat & 1 cool) thermostat to a honeywell digital RTH3100C thermostat, but the wiring colors don't match. What do you suggest?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I just replaced a merc controlled thermostat with a rth3100c
I just replaced a merc controlled thermostat with a rth3100c honeywell non-programmable digital one ( a heat pump ). all the wires matched the new one except the old one did not have a L wire coming f… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Rheem/Ruud Achiever 14 Heat Pump/Air Handler. When
I have a Rheem/Ruud Achiever 14 Heat Pump/Air Handler. When heating the blower runs fine, when cooling the blower is no go. Oddly, when I turn my Evap Cooler on too, it blows Ice cold air out of the i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x