I'm troubleshooting a Rheem heat pump system and I was

Customer Question
experiencing a problem with the...
I'm troubleshooting a Rheem heat pump system and I was experiencing a problem with the 3 amp fuse blowing which inops the system. Found defective thermostat and replaced with Honeywell non-programmable Digital Thermostat Model RTH3100C . With system on there is no heat. The blower is on as well the heat pump. Notice the indoor line going to indoor condenser is cold as if heat pump is in AC mode.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
2/12/2016
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 1 year ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi I'm Brian and I'm here to help!

On Rheem heat pump units, the reversing valve needs to be energized in heating. This means you should not have a connection at O but instead move the wire from O to B. (I'm pretty sure the RHT3100C has BOTH an O and a B terminal). If the thermostat has an O/B terminal then the reversing valve wire should be connected there and the thermostat setup will have to be changed so it energizes the reversing valve in heat instead of cool. That should take care of your problem! (unless of course your reversing valve coil is burnt up and that was the reason the fuse was blowing!)

Let me know if you have further questions on this subject. Otherwise, please remember to rate before leaving (3 stars or higher please!). Bonuses are always appreciated! Thanks for allowing me to help and thanks for using Just Answer!

Thank you,
Brian

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Hello again. I removed wire from O terminal to the B terminal. I turned system on and after 5 min delay system turned on and fuse blew. Disconnected wire at air handler which inputs to the defrost board outside which outputs to reverse valve signal and found a short. Disconnected outside at heat pump(defrost board) and confirmed this wire is shorted. Switched to a Different wire (spare). Turned system back on in heat mode and found the condenser was still operating in cool mode. The indoor condenser and piping was cold. I gone to the defrost board and visually confirmed the output signal actually comes out from the defrost board. I gone to the terminals marked reverse valve and found no voltage. Would it be a safe consumption to say the defrost board is bad? I did find one that's available but wanted to make sure if I troubleshooted to the fullest every possible fault.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 1 year ago

Hello again Al, I'm sorry it took so long to respond. I was away for the weekend.

It sounds like you have a volt meter so let's diagnose the system with that and a few logical steps as well. From your explanation of the symptoms, it sounds like it's either a shorted reversing valve solenoid, a defrost board that's failed or both. It sounds like you have your thermostat wired up right now with the reversing valve wire to B.

I would first disconnect the reversing valve itself from the defrost control board, I'm referring to the 'output' side of the defrost board, not the B wire thermostat connection to the 'input' side of the defrost board. Then ensure you have a good fuse in the air handler and turn power back on. Put the system in heat and measure the voltage at the outdoor unit from C to B at the defrost board. You should have ~24 volts ac. Now measure from C to the 'output' side of the defrost board reversing valve connection, you should have ~24vac there as well. If those checks pass, your defrost board is fine, if the checks don't pass, you have a failed defrost board.

Now with power off to the system and the two reversing valve coil wires disconnected, you should measure the resistance between the two reversing valve wires with your meter set to its lowest resistance scale (Rx200, Rx400 etc..). Let me know what you find. Alternatively, if the defrost board showed failed in the voltage check above, you could bypass the defrost board reversing valve relay by disconnecting the thermostat B connection and connecting it directly to the reversing valve coil wire that was on the output side of the defrost board. The other reversing valve coil wire should be connected to 24 volts common somewhere in the the circuit. If you can give me the model number of the outdoor unit, I can give more specific instructions. When you bypass the defrost board to reversing valve coil, turn all power back on and see if the fuse blows. If it does, you have a shorted reversing valve coil and will need to replace it. If the fuse doesn't blow and the system goes in to heat, you just have a failed defrost board.

Let me know how that goes and we'll go from there.

Thanks,

Brian

Ask Your Own HVAC Question
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 953
953 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a condensing furnace, MN G51MP- 48C- 090 -06 this
Hi , i have a condensing furnace, MN G51MP- 48C- 090 -06 this furnace gives trouble every year at some point. flash code says condensation is backed up or not enough combustion air or pressure switch … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
78 satisfied customers
We have a 7-day programmable digital thermostat and lost the
We have a 7-day programmable digital thermostat and lost the instructions. I messed up trying to program it, and now it won't come on at all. It is getting very cold and we need the heat. How can I ge… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier unit in attic/digital thermostat/nothing is
i have a carrier unit in attic/digital thermostat/nothing is turning on-even in fan mode,all breakers are goood … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Ritetemp digital thermostat not working: Displays Heat 2.
My Ritetemp thermostat says 'Heat 2'; the furnace will kick on for a minute but then shuts off. It does not get to the desired temp. Filter is not dirty.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need assistance in programing honeywell digital thermostat.
need assistance in programing honeywell digital thermostat … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
AC condenser outside the house keeps running after inside
AC condenser outside the house keeps running after inside temp reaches set point. Only way to turn it off is pull the breaker. I changed the contactor today but didn't fix the issue. I have 24 volts g… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell digital thermostat. the back light was
I have a Honeywell digital thermostat. the back light was out. it said the battery needed replacing. forgetting you can tip out the battery pack to do the replacement, I just pulled the unit off the m… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Batteries died in heat pump digital thermostat. Change
Batteries died in heat pump digital thermostat. Change batteries (3 AAA) replaced unit now no AC or fan?… read more
Michael Ferryman
Michael Ferryman
82 satisfied customers
Trying to install a new digital thermostat. The AC red and
Trying to install a new digital thermostat. The AC red and white wires were spliced into the wires going from the furnace to the old thermostat. So I thought, "These should just be installed directly … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
346 satisfied customers
I have an Emerson digital thermostat. The display is not
I have an Emerson digital thermostat. The display is not showing "system on" even though it should be calling for AC. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 1F80-361 programmable digital thermostat which,
I have a 1F80-361 programmable digital thermostat which, after 10 years, is giving me problems. Upon returning from an extended vacation, the thermostat is reading 79 degrees (HOLD mode) and the outdo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I installed a Honeywell Rth 6340/50 digital thermostat a
I installed a Honeywell Rth 6340/50 digital thermostat a couple of weeks ago and I have had nothing but problems ever since. When I called Honeywell they helped me set up the programming but I'm still… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
Connected humidistat to Honeywell digital thermostat. I
Connected humidistat to Honeywell digital thermostat. I cannot bring the fan on when set on auto when the humidistat calls for cooling, air runs but fan does not. This is a mobile home in florida whic… read more
Ricky Main
Ricky Main
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x