I have a nordyne g7. It will start, the flames ignite, it…

Customer Question
I have a nordyne g7...
I have a nordyne g7. It will start, the flames ignite, it runs for 5-10 minutes then I get an open limit switch fault. The blower continues to run for 3 minutes, the green light stops flashing and red and green go solid and the process repeats.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
2/12/2016
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi Luke, I'm Brian, an HVAC expert here at Just Answer and I'm here to help!

The fact that the furnace runs for so long before shutting down on high limit usually indicates either a weak high limit switch, or diminished airflow because of a dirty air filter (the most common reason for this), dirty blower wheel or dirty air conditioning a-coil. I would check for the airflow conditions first and if all is clean then I would replace the limit switch with a new one with the same ratings. I would also check the temperature rise of the furnace and compare it to the data plate on the furnace. The plate should have a 'Max Temp Rise' or the like. That is the temperature difference from entering to leaving air on the furnace. If the furnace is running at or near the max, then there is some kind of diminished airflow problem.

Let me know if you have further questions on this subject. Otherwise, please remember to rate before leaving (3 stars or higher please!). Bonuses are always appreciated! Thanks for allowing me to help and thanks for using Just Answer!

Thank you,
Brian

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Air flow is not restricted. Fan blades are clean. The limit that is tripping is on the heat exchange. The ambient temperature yesterday was 10℉, today it is 25℉. The thermostat is set at 68℉. Today the problem is gone.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago

Ok, it sounds like the high limit switch may be getting weak and tripping lower than it should. The way to double check that is to check the temperature rise by measuring temperature of the return air and the supply air and subtracting. Compare that to the "Max Temp Rise" on the furnace's data plate. If the temp rise is well under the max temp rise, then you most likely have a weak limit switch.

-Brian

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
1,024 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Upflow Furnace model G6RA120C-16 and the gas is
Good evening...I have a Miller Upflow Furnace model G6RA120C-16 and the gas is igniting intermittently. For example, temp is 64 and I set thermo to 76....heat kick on for about 2 mind and then shut of… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our Lennox ml193uh is not blowing. Have reset the breaker
our Lennox ml193uh is not blowing. Have reset the breaker and the reset on the side of the furnace, but it continues to blink quickly the red and green lights simultaneously.… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a nordyne furnace and I have already changed a few
i have a nordyne furnace and I have already changed a few parts. Originally i was told that the limit switch was bad so i changed that red light was flashing once. i have changed the pressure switch, … read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
My coleman heater shuts off after about 10 minutes. The
My coleman heater shuts off after about 10 minutes. The igniter will come on but it won't light and the green light flashes once. I can shut it off and after an hour it will do the same thing but it h… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi. I have an Intertherm/Nordyne M7RL furnace. The fan starts immediately, but no heat is
Hi. I have an Intertherm/Nordyne M7RL furnace. The fan starts immediately, but no heat is pushed, only cold air. When I look at the control board, I see a solid Red and solid Green light on, but the y… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
have a nordyne gl1ra090c-16b vent fan comes on, burner comes,
have a nordyne gl1ra090c-16b vent fan comes on, burner comes, when blower come s on burner turns off ????… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have had snow freezing temps in colorado the past 2 days
We have had snow freezing temps in colorado the past 2 days (-1 this am) woke to thermostat reading 44. Checked furnace and black circle thing was rotating very slowly. I went through process of dropp… read more
Joe Chappell
Joe Chappell
Building Engineer
7 satisfied customers
I have a Gibson KG6RC080C-16B furnace that is not heating... It
I have a Gibson KG6RC080C-16B furnace that is not heating... It uses Nordyne 624631-a control board and a 904081 gas valve. I am getting a constant flash from the red led on the control board. After r… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello there I have a York 80 furnace, P2MP. Thermostat calls
Hello there I have a York 80 furnace, P2MP. Thermostat calls for heat, inducer motor starts, ignition comes on, gas comes on, flames start, blower motor starts. 5-10 minutes later flames stop, inducer… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My 3 y old York furnace, the fan spools up but wont stay on.
My 3 y old York furnace, the fan spools up but won't stay on. The heat in the house is dropping.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Blower starts then immediatly shuts down. Repeats this numerous
Blower starts then immediatly shuts down. Repeats this numerous times (10-15) before finally goes to the ignition mode and then burner flame begins. Goes through this false start problem 1 to 5 times … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a york gas furnace FG8 125000 BTUH The air circulating
I have a york gas furnace FG8 125000 BTUH The air circulating blower was running continuous. The furnace started normally, but had 1 yellow 5 second flash diagnostic, (indicating false flame sense)? T… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an amana 80 sse furnace with a white rogers 50a50-298
I have an amana 80 sse furnace with a white rogers 50a50-298 control unit. On initial start up the unit works fine. vaccum fan then ignitor then flame and blower for about 5 minutes. After the initial… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
intermittent Carrier Weathermaker 9200 displays a continuous
intermittent Carrier Weathermaker 9200 displays a continuous red led light. What does this mean? How do I know if it is red light 1 or red light 2? Thanks!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
No heat. Nordyne G7 fault, Open limit switch Fault. 1. When
No heat. Nordyne G7 fault, Open limit switch Fault. 1. When unit is off, both red/green leds lit (normal), 2. once thermostat temp is raised, fan starts, aux fan on exhaust starts, Green LED flashes, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Janitrol model (GMP075-3). There seem to be a problem
I have a Janitrol model (GMP075-3). There seem to be a problem with the burner. It won't stay lite. When the unit is first turned on both the burner and the blower is working, but seconds later the bu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Ducane Gas heater - about 10 Years old. The model
I have a Ducane Gas heater - about 10 Years old. The model number is XXXXX We used programmable Thermostat (Honeywell). Currently, the heater is signal error code as follow : 4 flash stop for 2 second… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Nordyne FG6RA 072C 12A Scenario 1.Thermostat activates
Nordyne FG6RA 072C 12A Scenario: 1.Thermostat activates 2.Inducer starts 3.igniter lights 4.Gas valve opens 5.Flame 6.Gas Valve shuts off in 3-4 minutes (thermostat not satisfied)Cycle begins again...… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x