HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,075
Experience: Furnace, A/C and heat pump specialist.
Verified

Lets check the flame roll out limits first.They will be above and/or beside burners.Little button in center will push in to reset. http://i.imgur.com/CGkB9sa.jpg

If the flame rollout switches are ok, we will go to the main limit switch.It will be one of a couple of different types,usually located right in the front panel of the fire box.One is a credit card sized plate with 2 terminals exposed with wires connecting and the other is an oval snap disc type.See links below.

http://i.imgur.com/LNCrUvz.jpg

http://i.imgur.com/jQqQYN7.jpg

To check limits, if you have a test meter that checks continuity we can unplug the limits and test between the terminals for continuity (closed circuit)If you do not have a test meter we can do the following.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Removing front panel, I see a circuit board....Did not see any buttons to push
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Look just above burners, Can you attach me a picture with panels removed?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

If you have a paper clip icon on your page you can attach using that link.Or

You can upload the pictures using the tiny pic site .

Here is a link to the site.

http://tinypic.com/

Click on Browse , select the file from your folder.then click UPLOAD NOW.

They will give you a quote to enter in the box to verify you are a human.Enter the quote and click UPLOAD NOW

You will see your picture on right side of screen.

Then copy the link URL for email & IM

Paste that link here on the site.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
OK
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Did you locate them?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
OK, here are a few pics, with BOTh front panels removed.
IMAG0305.jpgIMAG0305.jpgIMAG0306.jpgIMAG0306.jpgIMAG0307.jpgIMAG0307.jpgIMAG0308.jpgIMAG0308.jpgIMAG0309.jpgIMAG0309.jpg
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Waiting for pics

Ask Your Own HVAC Question
Customer reply replied 2 years ago
sent them, see attached.
Customer reply replied 2 years ago
Rollouts ?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

The resettable rollout limts

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

What are first 3 numbers in model?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
XV95
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

That is a series containing several models.Look inside for a number that starts with TUD,TDE,TDD etc.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

I have to leave at midnight which is a few minutes from now so I am going to open this to other experts so you do not have to wait.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
TUH
Customer reply replied 2 years ago
Looks like TUH2B080A9V3VAC
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,344
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Check limit switches on burner box and by stack and see if they need to be reset. Small button should be in middle of switch, Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a UAPC-024JAZ, getting 25AC signal from upstairs,
Have a UAPC-024JAZ, getting 25AC signal from upstairs, change relay and start cap. TS, 26AC getting through the switch attached to compressor, but not through the switch that has a coiled tube attache… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
My Rodgers thermostat will not bring down the temp. The
My White Rodgers thermostat will not bring down the temp. The Cooling icon keeps flashing … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
I replaced the capacitor and fan motor, but now the
I replaced the capacitor and fan motor, but now the capacitor won't turn on. What should I look at now? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Rheem gas furnace air handler will run for 1-2 mi. then
My Rheem gas furnace air handler will run for 1-2 mi. then stop. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have an old RUUD UHQA-1310s. It doesn't blow cold air. Can
I have an old RUUD UHQA-1310s. It doesn't blow cold air. Can I recharge it with freon? … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Can I get the circuit board for a Kelvinator 2.7kw reverse
Can I get the circuit board for a Kelvinator 2.7kw reverse cycle window unit? … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
My AC unit is not turning on. It has been super hot ant it
My AC unit is not turning on. It has been super hot ant it failed lsat nite … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have an American Standard Condensing Unit 4TTB3018-060. I
I have an American Standard Condensing Unit 4TTB3018-060. I have never messed with this unit before but I cannot afford someone to clean it this year. So I went out removed all the screws pulled off o… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
My york ac is on and off from cooling though the compressor
my york ac is on and off from cooling though the compressor is on in the central unit … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I just replace a Honeywell PC8900 with an Honeywell RTH6360.
Hi, I just replace a Honeywell PC8900 with an Honeywell RTH6360. But the system become not working even with the fan. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
MY WHIRLPOOL WATER HEATER MODEL# IS L40S62-403 PURCHED 7/13
MY WHIRLPOOL WATER HEATER MODEL# ***** ***** PURCHED 7/13 WILL NOT LICHT. I HAVE DONE WHAT THE BOOK SAYS DO AND GET NO SPARK FROM THE IGNITER. I TRIED LIGHTING THE PILOT ( HOLDING THE PILOT BUTTON) WI… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a bathroom faucet #0749746. The hot water will not
I have a bathroom faucet #0749746. The hot water will not turn off. I have taken it apart and can't see any problem, nothing broken. I have to keep the water turned off under the sink. Please help! … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
An elderly neighbor asked me to replace her Thermalstat
An elderly neighbor asked me to replace her Thermalstat because it was so complicated she could not use it. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a furnace I believe model number 305318-201 rev A I
I have a furnace I believe model number 305318-201 rev A I need the wiring diagram for it. I cant find it and my A/C guy says he needs it to get the job done. something to do with the relay … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Billy. You were a great help a couple of months ago with my
Hi Billy.You were a great help a couple of months ago with my thermostat install. I am a newfie owner too!Installing another thermo that needs a common wire. It's a gas heat/ac combo commercial unit. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I live in ohio and have home built in 1992 with HVAC. i use
i live in ohio and have home built in 1992 with HVAC. i use a programable thermostat since nobody is home during day and have temp set at 75 during the day and drop it to 72 at 6pm. it takes about 3 h… read more
airheatman
airheatman
HVAC Technician
9,075 satisfied customers
My water heater will go through a cycle and then turn off
My water heater will go through a cycle and then turn off the entire system. Is this caused by a bad thermocouple? … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a blank screen. Less than 12 hours. Haha. Anything
Haha. Anything more than being told to push a button or 2 would be way out of my class. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x