Brand RUUD Model UAMC-024JAZ
why do I have:
suction pressure: 42
Head Pressure: 271
Outside temperature 77 F
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
2/3/2016
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Please provide all information I request as it makes it more difficult to troubleshoot something when I'm not there onsite. Essentially, you become my eyes and ears. Thanks for the opportunity to help. At the end of our dialog, you will have a chance to rate my service, but please wait until we are finished and you're satisfied you have all the information you need. Please be patient as many times we work with several customers at once.

Is the A-coil a TXV, cap tube, or orifice metering device?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Subject: heat pump system subcooling requirements for a
subject: heat pump system subcooling requirements for a downflow air handler.I have Rheem 6 ton variable speed split heat pump system. My air handler is installed in downflow position. Air handler is … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I am an HVAC contractor in Southern DE. I have a performance
I am an HVAC contractor in Southern DE. I have a performance issue with a York system that another contractor installed and after going through a few things I believe they mismatched the outside and i… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having trouble getting more that 10 degrees of cooling between the return and the vent. I've adjusted the charge to the spec in the manual for a pi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
If the reversing valve has a internal short like you said is
if the reversing valve has a internal short like you said is that why my suction psi is ;low… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Can you explain me more about expansion valves? What if
Can you explain me more about expansion valves ? What if subcooling is normal ( 10 ) & superheat is high ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a c1030bbd1v condensing unit that the compressor quit
I have a c1030bbd1v condensing unit that the compressor quit work, i replace it with a copeland compressor(the original is tecumseh) the unit head pressure was very high, the liquid line temp was 135F… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
New nordyne a/c 1.5 ton 20 amp breakers 125amp service
new nordyne a/c 1.5 ton 20 amp breakers 125amp service metering device … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I just replaced a heat pump r22 condensing unit. I have a
I just replaced a heat pump r22 condensing unit. I have a high suction pressure, 90psi superheat is 12 degree. Subcooling 10 degree and head pressure 250psi ambient temp 97 degree. Return air temp 77 … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
What are the different BTUs for different evaporator temps
What are the different BTU's for different evaporator temp's for a Copeland CR53KQ-PFV-970 Say 60 degree evap 45 degree evap 37 degree evap… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a ultra 5 tech 80 air handler, an older carrier unit
I have a ultra 5 tech 80 air handler, an older carrier unit outside, guages reading "r-22" 50 deg on the low side and 275lbs on the high side, the condensor line is "cold" on the low side all the way … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
im working on a russell 400 walkin cooler head pressure 250
im working on a russell 400 walkin cooler head pressure 250 and suction 45 psi R22 unit .what s my suction pressure suppose to be and head pressure ? unit supply temp when running is 35 degrees starte… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
straight cool system model # XXXXX; ON START UP HEAD
straight cool system model # XXXXX; ON START UP HEAD PRESSURE SWINGS FROM 250-325psi suc.66-72psi, when head is on the rise, suc.swings down. o.s temp 80, I.S TEMP 77, REGISTER TEMP 60, suc.temp 42*, … read more
drcool299
drcool299
shop owner
Bachelor's Degree
22 satisfied customers
Hello Billy, I have a RUUD UAKA-024JAZ that need a new capacitator.
Hello Billy, I have a RUUD UAKA-024JAZ that need a new capacitator. Can you please advise the brand/model no. of the capacitator I need to purchase? The one that is not working has nothing written on … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
in heat mode i cant get enough heat , 100 degrees.i add more
in heat mode i cant get enough heat , 100 degrees.i add more gas it doesn't change temp but head pressure takes off… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have aRheem RPMC-024JAZ heat pump about 8 years old I checked
I have aRheem RPMC-024JAZ heat pump about 8 years old I checked the suction line temp and its pressure which was 60 degrees and 110 lbs pressure. Outside air temp was 70 degree. The liquid line pressu… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
MY A-COIL IS FREEZING UP ITS NOT LO ON FEON &THE COILS ARE
MY A-COIL IS FREEZING UP ITS NOT LO ON FEON &THE COILS ARE CLEAN & THE BLOWER IS BLOWING GOOD DO YOU THINK IT COULD BE THE TXV THE UNIT IS 1 YEAR OLD… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
just had condensing unit installed,11/2 ton unit everything
just had condensing unit installed,11/2 ton unit everything was fine, until a few days after tech came back and said getting some head press. but no suction press. what ever that means… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I DO NOT GET ENOUGH COOLING IN THE HOUSE . I DID TEST THE
I DO NOT GET ENOUGH COOLING IN THE HOUSE . I DID TEST THE SYSEM OUT AND I OBSERVED TE FOLLOWING - SUCTION PRESSURE 77 PSIG - SUCTION LINE TEMPERATURE 46.5 DEGREES F - LIQUID LINE PRESURE 245 PSIG - LI… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.