Customer Question
607c ifm will not shut off
Submitted: 2 years ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 7 minutes by:
2/3/2016
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
Experience: Furnace, A/C and heat pump specialist.
Verified

Problem is going to be a bad fan control board or bad controller built onto end of motor.Do you have a multi meter for troubleshooting?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I changed the defrost control board and the ifm board, this is a Bryant/carrier 2 ton pkg heat pump and yes I have a multimeter the fan still runs when you disconnect the 24vac green wire from the thermostat to the low voltage green wire hookup inside the pkg unit. I looked at the ladder diagram and all the relevant relays are on the circuit boards as far as I can tell. I'm thinking maybe some snap disc for the emergency heat circuit is stuck thinking it has to remove residual heat from the air handler next to the coils and it won't allow the fan to deenergize
Customer reply replied 2 years ago
runs fine in cooling mode, hot gas reversing cycle is fine, defrosts fine , fan just never shuts off
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK looks like the unit has a motor that is high voltage powered but low voltage controlled. Often the contacts in the bell on end of motor will stick.

Locate the low voltage wires from board Brown COM and the wire from LOW terminal on board. Disconnect those 2 wires and see if fan stops.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
This sounds good, I'll try it tomorrow, I went to hvac school but it's been 15 years since I worked in the trade and lots of things got converted to circuit boards from old school relays. motor has common and 4 speed wires coming out so what you're saying is there is a relay in the motor itself powered of the ifm board's 24vac that may be stuck
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Yes there are contacts in the controller on motor itself for speeds controlled by low voltage.

If we disconnect the low voltage com and speed and motor still runs, we know issue is in that controller on motor. If not lets find where we might be getting 24 volts to that LOW terminal on board.Possibly a sequencer or something in heat kit.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
9,367 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have Honeywell stat # RTH 7560E 1001 it won't let me
I have Honeywell stat # RTH 7560E 1001 it won't let me change temp with touch screen tried to replace it but my system has interface module it only uses 3 wires 1 wire to C 1 wire to R 1 wire to termi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Westinghouse Furnace m/n FG7TA 100C-VC. No power to
I have a Westinghouse Furnace m/n FG7TA 100C-VC. No power to igniter. Checked high-limit, roll-out, and bot fan limits on the blower motor housing, checked both pressure switches by jumping them out a… read more
airheatman
airheatman
HVAC Technician
6 years college
9,367 satisfied customers
I have a Nordyne electric furnance my problem started last
Hello I have a Nordyne electric furnance my problem started last week while cooling and all of a sudden I smelled my heat strips so I shut off the unit and upon inspection and a little testing I repla… read more
airheatman
airheatman
HVAC Technician
6 years college
9,367 satisfied customers
After completely disconnecting the thermostat of our HVAC
After completely disconnecting the thermostat for one of our HVAC zones, the AHU blower continues to cycle on and off every 20 seconds or so. What could be causing this?… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Carrier model 48GP-024060321LS gas pack and AC unit.
I have a Carrier model 48GP-024060321LS gas pack and AC unit. The Compressor and the outdoor fan motor both run (start) fine. The indoor fan motor (evaporator blower) will not start. The schematic sho… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a 17 year old Rheem gas 41v50 that is leaking water
I have a 17 year old Rheem gas 41v50 that is leaking water from the top. I'm moving tomorrow and just want to make sure the situation doesn't get worse (this is a condo community). I believe I just wa… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier ac unit model# XXXXX and the blower motor
I have a carrier ac unit model# XXXXX and the blower motor is running forward and backward when the unit comes on. Is the blower motor gone bad? help! gary Crescent City fla.… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
have 2007 payne ph3z Indoor fan motor works fine for a couple
have 2007 payne ph3z Indoor fan motor works fine for a couple of days, and then with no warning outside condenser fan and compressor start, but no indoor fan. Sometimes I can turn unit off and wait 5+… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The IFM runs continuously, regardless of the thermostat setting,
The IFM runs continuously, regardless of the thermostat setting, on my Bryant heat pump. When I set the unit to heating or cooling, the OFM never runs and the compressor never comes online. I believe … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Ive got a Rheem 71-40D B water heater, and Im trying to shut
I've got a Rheem 71-40D B water heater, and I'm trying to shut off the water, drain it and check the heating element. Looking at the picture in the manual, the shut off valve is not where it is suppos… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a RGPH07EAUER that is flashing code two.ive replaced
I have a RGPH07EAUER that is flashing code two.i've replaced the pres.sen. now the IFM will start some times.some times it will run for some time long enough for the burners to come on.most of the tim… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Ok my furnance will not shut off, I have pulled thermostat
Ok my furnance will not shut off, I have pulled thermostat of changed the batteries put temp low and it will not shut off unless I hit the breaker. It won't heat just blows air, I think the problem is… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I am a plumber and I installed a Buderus boiler in my house
I am a plumber and I installed a Buderus boiler in my house 5 years ago. About a month ago I noticed that the pump for the floor heat will not shut off even though the house is not calling for heat. I… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
RUUD Mod. UHLA-HM2417JA------IFM only makes a small back and
RUUD Mod. UHLA-HM2417JA------IFM only makes a small back and forth movement when turned on.-----Motor or control Board? ---------- [email protected]… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
We have a Pulse 212 furnace model G21Q3-40-1. We have $900
We have a Pulse 212 furnace model G21Q3-40-1. We have $900 into repairing it. The first repair in March was for a purge fan which was replaced and replaced air flapper and clean drip leg. Now the prob… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
48TME rooftop, blow the fuses on start up 30Ax3 even after
48TME rooftop, blow the fuses on start up 30Ax3 even after IFM disconnected. I did not find any loose wires, when it is grounded it is usually transformer 575 x 24v but 3 x 30A??? Please advice. Thank… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i just turned off my weil mcclain boiler for the summer --
i just turned off my weil mcclain boiler for the summer -- it is 1 1/2 years old and I have a separate hot water heater... should I turn off the two gas valves too?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Trane EX 80 that the IFM runs all the time there is
I have a Trane EX 80 that the IFM runs all the time there is power to the unit. The W/R fan controller is new. What else can I check?? It also runs with the t-stat wires disconnected from the unit.… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.