My furnace will not get hotter than 66 degrees. I have a…

Customer Question
Hi my furnace will...

Hi my furnace will not get hotter than 66 degrees. I have a bayweb intenet thermostat and their tech says that the thermostat is calling for heat but the furnace shuts off.

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

The temperature stays in the range of 64-66 even if I have the therostat set to 72 degrees. This has happened since yesterday morning. I have the temperature set to 66 at night and 70 after 7 am

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
2/1/2016
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,363
Experience: Furnace, A/C and heat pump specialist.
Verified

Can you do some hands on troubleshooting? Also give me model on furnace you are having problems with.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

If you can provide model on furnace I will pull a manual on furnace and help you with tep by step troubleshooting.The website does offer phone call service for an additional fee of 18.00.If you select the additional service offer, you may get a different technician.Accepting the offer automatically charges you for the question as well as the additional 18.00 phone call fee. We can work here until finished at no additional fee.If you do want a phone call and don't mind the extra fees let me know ,otherwise we will continue here

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I can The model number is ***** 58MXA100-16
Customer reply replied 2 years ago
ANYONE THERE
Customer reply replied 2 years ago
Hello
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK The 58MXA has a control board mounted in blower compartment with an error light on board.If furnace shuts down while thermostat is still calling for heat, we should get an error code indicating what is failing by flash pattern.For example if a limit opens we will get one short flash followed by 3 long flashes. When it shuts off and should be running. look on the board and give me the flash code.That will tell us where to concentrate .

Ask Your Own HVAC Question
Customer reply replied 2 years ago
are you there airheatman, Phil has broken in and I cannot contact you
Customer reply replied 2 years ago
Phil wants $28.00 more What gives
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Yes I am here. Can you tell me if we get a flash code on board when furnace fails and should be on?The website does offer phone call service for an additional fee of 18.00.If you select the additional service offer, you may get a different technician.Accepting the offer automatically charges you for the question as well as the additional 18.00 phone call fee. We can work here until finished at no additional fee.If you do want a phone call and don't mind the extra fees let me know ,otherwise we will continue here

Ask Your Own HVAC Question
Customer reply replied 2 years ago
hello
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Yes I am here. Can you tell me if we get a flash code on board when furnace fails and should be on

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I had a zoned heat & air heat pump installed in my house.
I had a zoned heat & air heat pump installed in my house. One thermostat is upstairs, the other is downstairs. There is only one return in the house in the bedroom upstairs so that I can't shut off th… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My thermostat is set at 72 and its says inside is 72 but
My thermostat is set at 72 and its says inside is 72 but heat says on on the thermostat but system is not running… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a 2009 Luxaire Acclimate Modulating gas furnace...it
I have a 2009 Luxaire Acclimate Modulating gas furnace...it is turning on at correct programmed time, but not to desired temperature. Thermostat has been replaced. It is supposed to come on at 6am and… read more
airheatman
airheatman
HVAC Technician
9,363 satisfied customers
I have a Trane heating system that is split into 2 zones, one
I have a Trane heating system that is split into 2 zones, one downstairs and one upstairs. This morning we noticed that upstairs stayed warm, at 72 degrees but downstairs dropped to 59, although the t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I just got a new Trane furnace and air conditioner and new
I just got a new Trane furnace and air conditioner and new thermostat. Furnace is XC95m and air conditioner is XV20i variable speed. The thermostat is ComfortLink II XL950 Control. Although I have the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
yesterday morning about 6 am, the heat pump fan was running
yesterday morning about 6 am, the heat pump fan was running blowing cool air and the indoor temp was 68 degrees and the thermostat was set at 71 and the outdoor temp was about 36 degrees. We cut the p… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell 4000 series programmed to turn the heat
I have a Honeywell 4000 series programmed to turn the heat up from 66 to 69 degrees at 7:00am. The past 2 mornings when I get up the thermostat reads around 64 and it is clear the furnace is not givin… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
i have a heat pump and in the real cold weather (3 this morning)
i have a heat pump and in the real cold weather (3 this morning) it will not go above 64. it is sent on 72. it is not iced up and is on auxiliary full time. is this normal… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My ptac unit must have a thermostat problem the fan will
My ptac unit must have a thermostat problem the fan will work but the ac will not cool. Last summer the desired temperature had to be set progressively lower to get the unit to cool now this year it w… read more
airheatman
airheatman
HVAC Technician
9,363 satisfied customers
i have problems with my a/c model lwhd1209r s/n 902tayv14362 i
i have problems with my a/c model lwhd1209r s/n 902tayv14362 i turn on my a/c them put my temperature con trol on 70 after that i i turn on my timer for 7 hours and after my room get the temperature a… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
At a set point of 72 degrees my Honeywell VisionPro 1AQ wont
At a set point of 72 degrees my Honeywell VisionPro 1AQ won't shut off. If I set it down to 71 degrees or below it will shut off. Problem started just today and it has been installed and working for a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Honeywell thermostat model RTH6400D1000 date 0929.
I have a Honeywell thermostat model RTH6400D1000 date 0929. When I set the heating temperature at 68 the house will only heat to 66 degrees. Can the thermostat temperature be adjuisted so that the roo… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My Thermostat does not appear to be working, The night-time
My Thermostat does not appear to be working, The night-time program is set at 70. The temperature is reading 72 and the furnace is still running. I changed the batteries this morning and it appeared t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello, I recently purchased and installed a TL8230 Line
Hello, I recently purchased and installed a TL8230 Line voltage programmable thermostat. The first morning, I had it set to go to period 1 (default 70 degrees) at 6am - thinking this would have the ro… read more
Al-Moderator
Al-Moderator
High School or GED
I have a braeburn 2000 thermostat. How do I manually override
I have a braeburn 2000 thermostat. How do I manually override the programmed temperatures? when I follow the directions printed on the box, this is what happens: I hit the "up" button, the display fla… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Gas Furnace SA Series 80+ High Efficiency Upflow/Horizontal. The
I have a Gas Furnace SA Series 80+ High Efficiency Upflow/Horizontal. The furnace was installed during the summer and I don't know if they tested anything more than the furnace kicking on. I have redu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have my heat set on 70 and recently is has started to run without cutting off.
My home is all electric and recently my heat has started to run all day and night without stopping. I have the thermostat set on auto but it will not cut off. Please let me know the problem. Thanks.… read more
Expert
Expert
my new maytag furnace will not warm my condo from 66 degrees
my new maytag furnace will not warm my condo from 66 degrees at night to 72 degrees in the morning within a three or four hour time period. The furnace fires up and then cycles down numerous times war… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x