I have a Coleman Evcon, CGH07512E. The fan timer is Honeywell ST9120C 2010 and the gas valve/ignition control is Honeywell SV9501. My problem is on call for heat, the inducer fan comes on, the pilot lights and burns for about 2 seconds and then the ignition control clicks, the flame goes out and the cycle repeats over and over. I measured the voltage at the timer board of the EFT output (blue wire) connected between the board and the SV9501. When the power is turned on I read about 195 mV. When the igniter comes on the power jumps to about 280 mV and then returns to 195 when the pilot goes out. I have no idea if this is the correct voltage or if this might even be a problem and I do not know how to test the flame sensor. I am assuming the problem is that the gas valve is not opening due to a failure in the ignition sequence somewhere after the flame sensor else the valve is faulty. Can someone please tell me how to proceed and if I am even on the right track?
Thanks very much for your help,
***** *****
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
2/1/2016
HVAC Technician: Brian Horton,
 replied 2 years ago
Brian Horton
Category: HVAC
Satisfied Customers: 3
Experience: Service Technician II at Hobart Corporation
Verified

That pilot is heating a thermopile right? If so your thermopile is bad. Most thermopiles are closer to 400-600mv when fully heated which opens the MV part of the gas valve. The flame sense rod would only come into question when the burner actually lights and then quits.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Brian,
This furnace has a hot surface igniter and a flame sensor. According to the manual for the timer and gas valve, the pilot flame is detected by the flame sensing rod. When the pilot flame is sensed, the main gas valve opens. I do not see any kind of thermopile device on the burner assembly, nor do I see any mention of one in any documentation that I can find. The voltage readings I mentioned were measured at the timer circuit board on a wire that connects to the SV9501 at the terminal labeled "EFT Output". I am under the impression that voltage itself doesn't directly open the valve, but I am not sure and that is where I am stuck. As I mentioned in my request, I don't know how to test the flame detector which I believe is the logical next step, so that I can proceed with troubleshooting. If I am completely off base, can you provide a diagram or part number for the thermopile generator please?Many thanks for your help,
David
HVAC Technician: Brian Horton,
 replied 2 years ago

Have you checked to see that you have 24 volts to the flame sense rod? Is the flame sense rod heated by the the actual pilot flame?

Ask Your Own HVAC Question
HVAC Technician: Brian Horton,
 replied 2 years ago

Im not real familiar with this unit. But usually a flame sense rod is in direct contact with the burner flame. Not the pilot. Does the rod that the pilot is heating have wires coming out of it or just a cappilary line?

Ask Your Own HVAC Question
HVAC Technician: Brian Horton,
 replied 2 years ago

It would really help also if you could attach a couple of pictures of the pilot, igniter and flame sense rod.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Brian,
My problem has been solved. Thanks for your help.David
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian Horton Your Own Question
Brian Horton
Brian Horton
Brian Horton
Category: HVAC
Satisfied Customers: 3
3 Satisfied Customers
Experience: Service Technician II at Hobart Corporation

Brian Horton is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The blower on my furnace while using AC randomly will stop
Hello! The blower on my furnace while using AC randomly will stop and try to start up again while making a distinct noise. I have the audio file to help. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
Does not cool that well in hot weather. Have only owned the
have only owned the house for a year but the past week has been steady 90 degree temps and system stays 75 to 78. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
Goodman model ARUF182416CA LEAKING WATER. condensation is
goodman model ARUF182416CA LEAKING WATER. condensation is being blown outside drain tray along the outside of the unit. Drain tray is not overflowing. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
No power to rc wire detected what do i do. It just recieved
it just recieved this msg about 10 min. ago never has happen before unit wont work … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We just purchase a Honeywell Lyric T5 WiFi Thermostat and
Hi We just purchase a Honeywell Lyric T5 WiFi Thermostat and have it hook up and we do not have any showing up on the screen … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a GE Weathertron For Bay28x138 or Bay 28x140 with 8
I have a GE Weathertron For Bay28x138 or Bay 28x140 with 8 wires landed O= orange R= red T= brown G= green Y= yellow X2= black B= blue W= white It appears that there is a jumper to U from W. Can I use… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My thermostat said low battery this morning and I changed
Hi. My thermostat said low battery this morning and I changed the batteries. The led screen showed the temp. and all. I came home a little while a go to find the ac not working and the thermostat scre… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
I have a Honeywell FocusPRO 5000 that is less than 3 years
I have a Honeywell FocusPRO 5000 that is less than 3 years old. It started by the A/C unit not shutting off, and now the unit is not cooling at all. Is this a thermostat problem? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 1F85-275 thermostat that is locked and don't know
I have a 1F85-275 thermostat that is locked and don't know the code to reset. Is there a factory unlock code? … read more
Bill
Bill
Service Mgr
104 satisfied customers
My honeywell thermostat is not showing any readings of the
My honeywell thermostat is not showing any readings of the temperature. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Having a problem with lennox AC. It run good until it
having a problem with lennox AC . It run good until it reaches temp then turn off. will nit start again until it is reset. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I'm trying to figure out how to access the power cord on a
i'm trying to figure out how to access the power cord on a frigidaire FFRH2522R20 through the wall air conditioner. I have the replacement cord, but I cannot find anything that tells me how to actuall… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a model number EJC 2 200 under sink water heater and
Have a model number EJC 2 200 under sink water heater and the pressure has gotten very low in the past few months? Any way to correct this problem? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Wiring up a new Honeywell Lyric T5 thermostat. Thermostat
Wiring up a new Honeywell Lyric T5 thermostat JA: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat? Customer: Thermostat specific JA: Do you plan on… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE M847D1004 ZONE ACTUATOR THAT NEEDS REPLACING. NOT
I HAVE M847D1004 ZONE ACTUATOR THAT NEEDS REPLACING. NOT SURE IF ITS A NORMALLY OPEN OR CLOSED DEVICE. REPLACEMENT PART IVE FOUND IS M847D-ZONE. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Ihave TH9320WF5003 thermostat that allows the inside fan
Ihave TH9320WF5003 thermostat that allows the inside fan unit to continuously operate even when the thermostat is set for higher temp or turned off completely. The fan is set for automatic. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm replacing a Trane Weathertron thermostat with a
I'm replacing a Trane Weathertron thermostat with a Honeywell RTH5160. The Trane thermostat has 7 wires one of which is a "T" wire (color appears brown) connection. Also I have an "X2" (white) connect… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to find floater switch on carrier 9200 to see if
Trying to find floater switch on carrier 9200 to see if tripped the thermostat from having no power … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x