Issue is regarding a lennox g50uh (x), i keep getting a Blocked inlet/exhaust; condensate line blocked; or pressure switch closed prior to activation of combustion air inducer

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

Exhaust fan comes on, gives the two fast blinking lights that everything is ok. then goes to the DS2 light slow blinking, and doesn't do much of anything than that and shut off

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 22 minutes by:
1/31/2016
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,625
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.
This error is either a draft problem or a clogged condensate drain problem. You need to remove all the hose on the unit an make sure the water is draining freely. Also check the small vac tubing connected to the draft pressure switch ( see attached pic for typical). The tubing should have no water in it and where it connects to the furnace should be open. You can poke a paper clip into that port but not the one on the switch.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
As far as hoses are concerned, the only one is the vacuum tubing connected to the draft pressure switch (unless i require it to be disassembled further, but most of the wiring and it seems all the circuit boards are visible) , and that vacuum hose goes to the exhaust fan. The hose is clear, the exhaust fan side, i am able to blow through. and the switch side i am able to blow and suck and cause it to make a clicking noise. Exhaust pipe did have a couple mud dobber nests in it, but i have cleared it out and it is clear now. The only "hose" for draining condensation is on the upper part of the unit and is PVC and drains down from there to be pumped. it seems to work because it drains my AC just fine. So from here, i dont know what to do, which is why i am seeking the advise of an expert such as you.Thanks Dan
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Ok, blowing/sucking on the hose to the switch doesn't indicate anything if it clicks. The vacuum that the switch responds to is far lower than what your lungs can create. So since you're sure the tubing and the port the tubing connects to is clear then you either have a bad switch, a weak draft inducer fan or your vent us still partially blocked. The only way to determine which is the likely culprit is to put a manometer on the exhaust and measure the draft pressure. Since you probably don't have a manometer replacing the switch would be the next thing to try.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,625
24,625 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Lennox ML 193UH will not turn on heat. I have tried
Please help! Lennox ML 193UH will not turn on heat. … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
My name is ***** ***** and I am having a problem with my
Hi - my name is ***** ***** and I am having a problem with my Lennox HVAC unit - seems as though when there is a demand for heating, the ignitor is not lighting and it is not producing heat … read more
Rick
Rick
HVAC Supervisor
24,625 satisfied customers
I have Lenox C33-44C-2F gas furnace. When heat is called,
I have Lenox C33-44C-2F gas furnace. When heat is called, one of two diagnostics light goes off. 2nd diagnostic light flashes slowly. Here are the LED flashing codes: A: Pressure switch open; B: Block… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace is a Lennox ML193. It stopped working and would give a slow green flashing light,
Furnace is a Lennox ML193. It stopped working and would give a slow green flashing light, red light out completely. Panel shows this indicates: A) Pressure switch open or, B) Blocked inlet/exhaust ven… read more
type2technician
type2technician
253 satisfied customers
I have a 5-6 year old Lennox g61mpv 2 stage funnace. It has
I have a 5-6 year old Lennox g61mpv 2 stage funnace. It has been cycling for over a year and I can not figure out why. The error code on LED lights is DS1 off and DS2 flashing slow. The manuel shows e… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
i have a lennox furnace wont turn on and blinking only the
i have a lennox furnace wont turn on and blinking only the green light slowly model c50uh-48b-090-12, the induced motor is keep spinning and wont stop even its not calling for heat… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
my furnace, ML193UH, has been working very well, no longer
My furnace, ML193UH, has been working very well. This morning I awoke to an unusually cool house and checked the diagnostic lights and sure enough, the green light was blinking slowly. When I checked … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox G40UH gas furnace. The combustion air inducer
I have a Lennox G40UH gas furnace. The combustion air inducer turns on but the ignitor won't energize. The LED #1(red) goes off and the LED #2(green) shows a slow flash. The diagnostic code chart says… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox model C33-48c-2f-2 & run into situations that
I have a Lennox model C33-48c-2f-2 & run into situations that the furnace will not kick on when the thermostat indicates it should. The furnace sounds like it's running, but the burners are not lit & … read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
Have G51MP Series. Using SureLight Troubleshooting - T-stat
Have G51MP Series. Using SureLight Troubleshooting - T-stat calls for heat DS1 and DS2 Fast Flash for about 2min 30sec then Blower shuts off then DS1 OFF DS2 Slow Flash ??? Any suggestions? Thank you.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Lennox G40UH(x) furnace. The diagnostic code states
I have a Lennox G40UH(x) furnace. The diagnostic code states the error could be: (A) Pressure switch open or, (B) Blocked inlet/exhaust vent or, (C) Condensate line blocked or (D) Pressure switch clos… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox surelight elite series surelight status/diagnostic
I have a lennox surelight elite series surelight status/diagnostic codes diag no 1 off diag no 2 slow flash - pressure switch open or has opened 5 times during a single call for heat or blocked inlet/… read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
My Lennox system will purge but not fire.. Problem has been
My Lennox system will purge but not fire.. Problem has been worked 6 times but is still occurring. Service Company is Ace Heating and Air Cond. in Fairfax VA. Model number is XXXXX 61MPZ36C090.. I'm c… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
i have a lennox elite series furnace, first of all the thermostat
i have a lennox elite series furnace, first of all the thermostat is an older round twist mercury type, the furnace is not turning on unless i move the thermostat around a few times, but once the furn… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
my heater doesnt turn on.. if i set the Fan to ON, the blower
my heater doesn't turn on.. if i set the Fan to ON, the blower turns on, but if I set the Fan to AUTO and the system to HEAT with the desired temp at least 5 degrees above ambient, nothing happens FIX… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Turned the heat on the first time today and it wont run. The
Turned the heat on the first time today and it won't run. The fan works when set to on. Model is lennox c33-43c-2f-3. Troubleshooting lights are red - off and green blinking.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Just turned the heat on for the season-- Blower motor comes
Just turned the heat on for the season-- Blower motor comes on but no heat- Can't hear burners coming on first--Just blower which shouldn't come on till after burners heat up-- Changed batteries in Th… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Lennox 90ugf, was shutting down due to condensate collecting.
problem solved. Had to suck on hose leading to pressure switch to get ride of a bit of water that had collected in there. Lennox 90ugf, was shutting down due to condensate collecting. Removed boot and… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.