Jason I attempted to connect...
Jason I attempted to connect based on your input and I am blowing the circuit board fuse
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
1/30/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,039
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello, my name is Billy.

I hate to give conflicting info but it is NOT recommended to wire the humidifier into the gas valve circuit.

Also we will need to know humidifier maodel number as some Aprilaire units use their own built in transformer which would conflict with HUM terminal.

So, what model humidifier?

What wiring was used before to humidifier?

And yes you are correct...we should not need a current sense relay.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Aprilaire 400M
Customer reply replied 2 years ago
I previously used a current sensing relay and worked fine but the humidifier no longer works. I want to make sure I have the wiring correct before I replace a possible bad solenoid valve.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Ok, you have a basic flow through with a simple 24v solenoid.

Now there are various ways to wire. The most common is HUM and C..

The hum goes to humidistat

out of other humidistat terminal to solenoid and from remaining solenoid wire back to C.

As a test..turn power off..

Run a wire from R and C..

Attach R to one solenoid wire and C to to other...the solenoid should react as it will have 24v constant.

Then we can go from there

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Unfortunately I don't have the chance to do this now.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

no problem...just wait until you can attempt and then respond.

Keep this on your end as any response from you forces a response from me.

Billy

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi Billy, if I wire using the HUM connection will the humidifier only run during HEAT mode? Is this not the same as connecting to the W terminal?jim
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Hum = operation in heat mode.

We do not want W terminal as that puts it in the same circuit as the gas valve. Basically this adds another "load" in the gas valve circuit.

The HUM is dedicated circuit for humidifier. To wire in the W (gas valve circuit) would work but is strongly frowned on as it can affect the heat circuit.

Ask anything you need to know...

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Billy, I am just now getting to try this. I wired it as you stated and I am blowing the fuse on the board when the humidifier kicks on.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

please post pic of the humidifier here with front off.

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago
Jason Whatley
Jason Whatley, HVAC Technician
Category: HVAC
Satisfied Customers: 60
Experience: HVAC/R Supervisor at DOJ
Verified

Hello, Billy has opted out of the question so now I can help you again. Have you tried the original diagram that I sent you? ( Sorry you are getting conflicting information here - Aprilaire specifically gives you the option to use the w terminal because the solenoid has a very low volt amp rating)

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

If you are blowing a fuse when the humidifier is turning on, you have a short in the humidifier circuit. Recheck all of the wiring and make sure there are no nicks in the wire jacketing too.

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

IF all wiring is good - when Billy had you run a pair of wires from r and c to the humidifier, the fuse blows then the solenoid valve itself is suspect of the source of the short.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i just replaced my humidifier with a new one thinking the solenoid valve was bad.
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

And the new one is blowing the fuse?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
hold on I'm going to rewire based on using the W terminal
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Okay. Did you run all new wiring to the new humidifier? If any piece of the wiring is skinned or touching the ductwork or both wires touch each other it will ground out and short. It's most common to find a short in the wiring from a bare spot touching metal

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

I see the picture you sent of the furnace circuit board, is this a Bryant/Carrier/Payne furnace? Also a picture of the humidifier and the humidistat would be really helpful.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
just blew another FUSE and now i am out of fuses!!! this is awful
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

can you send me a picture of the humidistat with the cover off and a picture of the humidifier with the cover off?

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

I know these shorts are trying, but we will get it straightened out

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

The diagram you followed is correct for a conventional humidifier and humidistat like the Aprilaire 400m with dial humidistat. We need to be certain there are no shorts in the wires themselves.

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Okay got the pictures. Can you send a picture of where the wires splice into each other? ( I see the humidistat is wall mounted and has a red and white wire to it, and the solenoid has two white wires to it)

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I had to go to store to get fuses and they only have two. I can't afford to blow any more since its going to be double digits. Can we do this by phone?
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Unfortunately I'm not set up for phone right now. If you want to wait until you can get more fuses that's fine with me. Just so you're not out of heat for the night

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I should have them in about 20 minutes
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

No problem

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Okay, so the white wire goes straight to the solenoid valve, and the red goes up to the humidistat and back from the humidistat to the solenoid valve?

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Do you have a volt meter available?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
no volt meter
Customer reply replied 2 years ago
Yellow wire from solenoid valve is wired to 24V common on furnace board, W from furnace board is going out to HSTAT, other HSTAT wire is going to other solenoid connection
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

That's exactly how it should be. Try this one more time - turn off power and disconnect humidifier wiring from solenoid valve and circuit board. Run one wire from c terminal to one leg of solenoid valve. Run one wire from r terminal to the other leg of solenoid valve. Restore power and listen for the solenoid to click. This will verify the solenoid valve is not shorted (I know it's new but I've seen it before)

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i did that and the solenoid didn't click on.
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

did it blow the fuse?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
no it did not blow the fuse
Customer reply replied 2 years ago
crap hold on I didn't replace the fuse. Let me test again.
Customer reply replied 2 years ago
OK! the solenoid clicked on
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Okay, that verifies that the solenoid is good. Now, that also tells us there's a short in the wiring somewhere.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I checked all the wires and they look good, nothing has changed since I installed the first unit last year.
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Okay let's try this... Turn off the power, Replace the wires as they were, disconnect the wires from the humidistat on the wall. Take those wires at the humidistat and tie them together. Restore power and see if fuse is good when the runs (solenoid will click then too when heat comes on if the fuse doesn't blow). This will tell us if the humidistat is causing a problem.

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Very doubtful but this is the only way to troubleshoot without a volt meter

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Can you send a picture of the humidifier without the filter panel in? Do you have those white wires that the diagram shows?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i just did that wiring you suggested and as soon as i turned on the power the fuse blew
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

So it's not the humidistat. And you have it wires exactly like the diagram shows with the white wires? (That is an overflow switch in the bottom of the unit)

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Try taking the white wires out of the sequence.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i'm down to 2 fuses and need at least one. I don't know what bypassing the white wires will do?
Customer reply replied 2 years ago
i give up
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Just to verify the overflow switch isn't causing the issue (doubtful again). I'm definitley positive there's a short in the wiring - we've proved that. What I would suggest is running new wiring from the furnace to the humidistat and back from the humidistat to the humidifier. There is a short, somewhere

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Its very hard to tell without a volt meter to check continuity with

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I cant to anymore tonight. I am going to have to call a contractor
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Try the wiring before calling for someone to come in. I'm confident that will save you $$$!

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

When you have time of course. I'll be hear waiting to hear if you got it! :)

Ask Your Own HVAC Question
Customer reply replied 2 years ago
son of a bitch. i used the spare thermostat that came with the new unit and wired it up and now it works. somehow there's a short in the line!!!!
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Awesome, I knew there had to be somewhere

Ask Your Own HVAC Question
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

Probably a small pinch that you can hardly see

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thanks for sticking with it
HVAC Technician: Jason Whatley, HVAC Technician replied 2 years ago

For sure! That's what I'm here for

Ask Your Own HVAC Question
Was this answer helpful?
Ask Jason Whatley Your Own Question
Jason Whatley
Jason Whatley
Jason Whatley, HVAC Technician
Category: HVAC
Satisfied Customers: 60
60 Satisfied Customers
Experience: HVAC/R Supervisor at DOJ

Jason Whatley is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How do I operate a humidistat. How to operates humidistat. I
I simply turned humidistat on and turned to the current area humidity and assumed the a/cwould come on Nothing happened. HELP … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Carrier furnace is blinking 2 fast then 4 slow and the
carrier furnace is blinking 2 fast then 4 slow and the blower will not turn on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a carrier furnace, the pilot light is on. The burners
Hi, have a carrier furnace, the pilot light is on. The burners used to come on & off on their own (not in response to the Thermostat). Then they stopped responding all together. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Carrier furnace igniter doesn't spark. It was working but
It was working but today the electronic igniter doesn't spark … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My carrier furnace model 395baw036060. There is a clicking
there is a clicking sound and the flame comes on but goes off and it keeps clicking… read more
Bill
Bill
Service Mgr
100 satisfied customers
I just replaced a 10 year old Carrier Furnace with a Lennox.
I just replaced a 10 year old Carrier Furnace with a Lennox. It is a 2 zone system (Carrier again). At the install we had to change out the zone control board and thermostats to be compatible with Len… read more
Bill
Bill
Service Mgr
100 satisfied customers
I have a Carrier furnace funace, and it's not blowing warm
Hi I have a Carrier furnace funace, and it's not blowing warm air … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace that is having issues. The t-stat
I have a Carrier furnace that is having issues. The t-stat calls for heat, inducer motor runs, for approx 30-60 seconds, then the surface igniter heats up and gas ignites. Then sometimes the last few … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier Steam Humidifier - HUMXXSTM3134. The red
I have a Carrier Steam Humidifier - HUMXXSTM3134. The red light was blinking, so technician replaced canister. Red like is STILL blinking. red light … read more
Bill
Bill
Service Mgr
100 satisfied customers
Carrier furnace. Igniter comes on, but no flame. There was
Carrier furnace. Igniter comes on, but no flame. There was an electrical issue earlier today on the electric company's side of the meter. It has been repaired. Furnace was OK prior to that. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace rated at 1865 cfm was recently installed in
carrier furnace rated at 1865 cfm was recently installed in Jan 2018. Total cfm for all vents is 1056 cfm. heat distrbution for 16 vents ranges from 69 to 95 cfm. what could be the problem? Please adv… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,039 satisfied customers
I have a Carrier furnace model 58CTA090-12114 that was
I have a Carrier furnace model 58CTA090-12114 that was installed in 2005,I am currently having an issue with it when it is called upon for heat, it will start the burner sequence with the ignitor glow… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier furnace is not turning on. Thermidistat is blank.
My carrier furnace is not turning on. Thermidistat is blank. Error codes is 33. … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,039 satisfied customers
My carrier furnace is not igniting, no error code. Last
My carrier furnace is not igniting, no error code. Last night it was glowing like it was trying to ignit, but it's not glowing anymore. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 1983 Carrier furnace 294gaw00100. There is not
I have a 1983 Carrier furnace 294gaw00100. There is not pilot ignition. I've checked blower, theromstat, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Getting a code 33 on my carrier furnace intermittently. And
getting a code 33 on my carrier furnace intermittently … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier pad needs to be changed. Is that something easy to do? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,800 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x