Cannot get a Honeywell 'round' heat only thermostat to

Customer Question
Cannot get a Honeywell...

Cannot get a Honeywell 'round' heat only thermostat to control the furnace. The stat did run this furnace before we shut it down to install a new Propane tank, but since restarting the furnace, I can only get it to run if I remove the stat and jump the R and W wires.

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

I firured the stat was the issue so I changed it. Nothing, same as before. I checked the transformer , it puts out 27 volts. Tried another stat, same thing. In every case, the furnace will run on a jumper, but not on the stat.

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 hours by:
1/30/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

just to confirm....you have wires on R and W in the thermostat?

When touched direct together the furnace runs..but does not through thermostat?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thats right
Customer reply replied 2 years ago
The stat has a three wire terminal for the wires to the transformer, but only the red and white were hooked up when the furnace ran before this problem appeared.
Customer reply replied 2 years ago
The yellow wire from the stat was never hooked up.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

sorry for the delay.

I cannot say if it was related to shut down...but I can say the thermostat has no provision for being field repaired.

These types of thermostats run less than $40 so the most viable option is to replace.

Whether shut down related or not the connection relay in the thermostat is defective now. The thermostat will need to be replaced.

Billy

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Already tried replacing the stat with an exact replacement and with exact same results. This is an older furnace. Rheem model number:RGDA-100C-ER MN3D104 F4290 1877
Customer reply replied 2 years ago
Can there be a problem with the transformer sending too many volts or the correct voltage with wrong cycles per second, or too much amperage?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

if it works by touching wires together and NOT a new thermostat then the only reason can be less than 24v to thermostat. This would be a transformer issue

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I finally got the problem fixed. After trying three (3) thermostats exactly like the original that was installed at the beginning of this odyssey and removing the 'fan control center' and having it tested at a local HVAC shop where it was pronounced "OK", a service tech offered me an old stat of the 'bimetallic spring and mercury tube' type to try. I did and the furnace worked perfectly! It seems that some of the older models will not respond to an electronic type thermostat. Is this something unheard of? After buying three identical stats, dismounting the 'control center' for independent testing, making four or five trips back and forth throughout all this,and asking my questions at this website, on the internet, at HVAC shops, and everyone else I could think of to ask, did it not occur to anyone that the problem might be with the 'type' of stat that was being used? I had mentioned that the furnace was 'old' and given the model number& etc. Would that info. have provided a clue as to what the problem might be?
At the start of my inquiry with you I said that the furnace ran on the originally installed stat before we shut it down to install a regular 500 lb. propane tank, I think I assumed that. It may be that it was never hooked-up to the stat and that the folks just ran it without any thermostat at all. This has been a long ,long process of a job for several people. It is hard to be sure of some things. I have been helping a 'friend' with it, so I was not involved with all the work. The end of it is that I found an older stat with the same shape of the 'spring&tube' construction, installed it and we are good at last.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
23,154 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am replacing a Honeywell T8112D1005 thermostat. The
I am replacing a Honeywell T8112D1005 thermostat. The bettery terminals are corroded and the display stopped working. I tried cleaning up the terminals, but they are eaten through. I found a newT8131C… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Ran out of propane. Trying to fire the goodman hybrid
Ran out of propane. Trying to fire the goodman hybrid furnace back up. Only 32 degrees outside have set t-Stat for 71 in a house that's at 60. Both panels off, looking at lower circuit board, push loc… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I just installed a new lennox SLP98 UHV and have added a wood
I just installed a new lennox SLP98 UHV and have added a wood boiler system. I am trying to figure out how to change the dip switches or whatever is needed to get the furnace to operate without using … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
trying to replace an auomag thermostat that has R W connections with a honeywell wifi th
trying to replace an auomag thermostat that has R W B connections with a honeywell wifi thermostat ; I need a "C" wire and need to which wires to use… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Need assistance with a couple wires and a config option on
Need assistance with a couple wires and a config option on honeywell HZ322 zone controller… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
Greetings, We have a Honeywell RTH9580 WiFi Thermostat It
Greetings, We have a Honeywell RTH9580 WiFi Thermostat It operates the Furnace ok. It operates the 'Fan' in the air handler ok, but the outdoor condenser will not turn on, thus no refrigerated air. Ye… read more
jhvac
jhvac
2 satisfied customers
I recently replaced the furnace in my home with 3year old Lennox
I recently replaced the furnace in my home with 3year old Lennox elite, 44,000 btu in 36,000 out. It was running on Natural gas and I purchased a conversion kit from a Lennox dealer and switched it ov… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
My gas furnace short cycles. I have removed the filter so that
My gas furnace short cycles. I have removed the filter so that is not the problem. The furnace goes through all the proper stages for heating. It just cycles every 5 minutes or so and there are no fla… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
HI, I have a Reem 90 plus RGRA series Furnace. It will not
HI, I have a Reem 90 plus RGRA series Furnace. It will not come on when the tstat calls for heat. If I mess with the tstat I can get it to come on. So I ganged the tstat to a Honeywell Programable but… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a honeywell RTH111 thermostat, I switched from a ritetemp
I have a honeywell RTH111 thermostat, I switched from a ritetemp thermostat. The wires coming out of the furnace are red, white, green, and light blue. I connected the red to rh, the white to W, the g… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Wiring question replacing thermostat written by Tony, June
Wiring question replacing thermostat written by Tony, June 03, 2010 Old one is Honeywell Chronotherm T8082a1171 Williamson oil furnace with A/C. New one is Honeywell VisionPRO TH8000 It appears from t… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I am trying to install a new programmable thermostat ritemp
I am trying to install a new programmable thermostat ritemp #6030 on my Goodman mfg. P030 unit, serial # XXXXX The old (Honeywell) thermostat had 4 wires connected to W, Y, R, and G.and was running ok… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a CR26-48N-F-01 Furnace. We had a power outage for
I have a CR26-48N-F-01 Furnace. We had a power outage for a couple of hours, and the furnace won't restart for some reason.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
If an older gas furnace shows the following symptom, is the
If an older gas furnace shows the following symptom, is the thermocouple a good guess of what may be failing? The stat triggers the furnace to kick on, it trys, fails, then it tries again and fires up… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I replaced my thermostat with a honeywell rth2300. It worked
I replaced my thermostat with a honeywell rth2300. It worked fine for a while, but this morning it stop working. The burners fire up and then shut down. NO heat. But when I manually jump the heating c… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a WellsMclain GCI Boiler. It is short cycling. If
I have a WellsMclain GCI Boiler. It is short cycling. If I put 24 Volts to the pv terminal on the honeywell ignition module it will keep running. Is this the the gas valve or the flame rod?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Hello, I am trying to replace weathertron BAYSTA T240 thermostat
Hello, I am trying to replace weathertron BAYSTA T240 thermostat with HONEYWELL RTH7500D . I tried to replace with Hunter t-stat . Connected wires as shown in book and burned up 24 volt transformer . … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a 3.5 ton trane spilt unit, it will only run the condensing
I have a 3.5 ton trane spilt unit, it will only run the condensing unit for about 15 seconds and then it shuts off. I have bypassed every safety possible. It seems to be losing its 24 volt signal from… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x