We have a Lennox Ch33-36a-2f and it was not working but the fan came on in manual... We figured out from the diagnostic codes light 1 was slow flashing and light 2 solid... We changed the filters. Turned off for 30+ minutes and now no lights and fan does not come on when thermostat set to fan on. What should we try now?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
1/27/2016
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Please provide all information I request as it makes it more difficult to troubleshoot something when I'm not there onsite. Essentially, you become my eyes and ears. Thanks for the opportunity to help. At the end of our dialog, you will have a chance to rate my service, but please wait until we are finished and you're satisfied you have all the information you need. Please be patient as many times we work with several customers at once.

Can I get full furnace model number, please, so I can look up codes? The number you provided, CH33-36A is your coil.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Lennox G40UH (X) series is the number on the manual. Does that work?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Diagnostic light #1 flashing and #2 on solid?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
that's correct.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

This would indicate:

Primary or secondary limit switch open. Limit must close within 3 minutes or unit

goes into 1 hour Watchguard. Check your flame rollout switches to see if they tripped. These would be small disc shaped switches in by the burners. They have a small red reset button in the center.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
should we press the button? This was the condition a while ago.... Now there are now lights on. Should we still go press the red button?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Could also be the pri***** *****mit. Is the fan running continuously?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No it's not running now
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Check your blower. Maybe the blower motor is bad causing it to trip out on the limit.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The blower was running but after we turned the unit off no lights no blower. We turned it off by unplugging it.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Unplugging it?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
it has a plug (grey one) that runs to the furnace and we thought to reset it by unplugging it. I can take a picture and send it.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Hmmm, unusual for a furnace to have a plug in cord.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ours does. I can send a picture if that helps.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Well, lets plug back in and see what happens.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hello?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Well, lets plug back in and see what happens.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Done that and now we have no lights and nothing is working.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Check and make sure power switch is on, blower door on securely. Turn thermostat fan switch to On instead of AUTO, see if blower runs.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

If nothing, check breaker. Maybe it tripped.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Where is the power switch?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Should be right by the unit looks like a light switch

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

You may not have a power switch if you have this plug in cord.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Very unusual for a furnace to have a plug in cord, by the way.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I figuring that... Give me second and I will give you an update
Customer reply replied 2 years ago
No light switch. Our unit is in the attic and is horizontally mounted.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Did you check circuit breaker?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
it's on.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Check the plug in that you are plugging it in at. Make sure it has power.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

If the plug in has power, next check the fuse on the control board. See if it's blown.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Plug has power checking fuse now
Customer reply replied 2 years ago
Fuse is good
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

If fuse seems OK, then the LED's should be slow flashing.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No LEDs are not flashing.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Get a voltmeter, check from C or common on board to R. Should be 24 volts AC. This will be on terminal strip where all the thermostat wires attach.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Make sure blower door switch is pushed in when you do this.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Getting meter now
Customer reply replied 2 years ago
Still working on it
Customer reply replied 2 years ago
No not 24 volts getting 0
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Did you push in blower door switch while taking reading?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok getting 5.2 volts when push in switch. Also getting buzzing noise when push in switch.
Customer reply replied 2 years ago
Pic attached. Where is the limit switch?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Did you see the picture I attached? About the size of a playing card, two wires attached. Sits on the upright portion above the burners.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
saw the pic but it doesn't look like ours. That's why I sent the picture of ours
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Doesn't matter how many burners. The limit will look the same.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Do you have a part number?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

It is a brown flat piece of plastic with two wires attached. About the size of a playing card.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
We found it.
Customer reply replied 2 years ago
It's done power back on. What should happen?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Turn furnace power off, Take the two wire leads off the pri***** *****mit and tape them together, then power back on. The pri***** *****mit can be seen in this picture:

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok did that. Now what?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

See if you now have 24 volts across C to R

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No do not still 5.2
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Not making sense. You must have a burned out transformer, then.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Transformer may look similar to this.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

You do have voltmeter set to volts AC, not DC correct?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Y s set to AC. Is that the part we need? The exact one?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

No, just an example.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

ON board, find the terminals XFMR-H and XFMR-N. Check across these for voltage. Let me know what you have. Make sure blower door switch is pushed in.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok give us a minute
Customer reply replied 2 years ago
Do we keep the limit switch wire disconnected?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Previously you taped the metal ends of the two limit wires together. Leave this way for now.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
125v
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

OK, so we know the transformer has 120 volts on primary side, but only 5.2 volts on secondary side (according to the reading you gave me). So I would replace transformer if board fuse is not blown. I am going to be logging off here for tonight in about 5 minutes.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. Do you do service calls to Azle tx if the transformer doesn't fix it?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

There are many sites that sell Lennox parts. www.cozyparts.com is one of them. No, Just Answer does not do service calls. Sorry! LOL

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thanks for your help. Anyway we can get in touch with you again if we need?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Let me know if you have additional questions. Otherwise, good luck! Thanks for using Just Answer and please don't forget to rate my service as that's how experts get paid (thanks in advance for any bonus left). Otherwise experts work at their own time and expense. Feel free to post back with any additional questions.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Anyway to get in touch with you again?
Customer reply replied 2 years ago
Do we get s case number?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Just bookmark the page.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Bookmark the page and come back to it. As long as you have rated me positively, I will continue to work with you should you need further assistance.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
We have ordered the part and it comes in tomorrow. We are very happy so far and have every intention of rating (fantastically) you once we are done.... Keep tuned!
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Thanks for the update.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Good afternoon. We installed the new transformer and we are still getting the same readings and still I lights. What's next?
Customer reply replied 2 years ago
Still no lights. What's next?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Doesn't make sense. If you are getting 120 volts on PRI1 and PRI2 then you should get 24 volts at SEC1 and SEC 2

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Here's what I want you to do. Check the fuse again on the board. Pull it out and make sure it is not blown. If this looks OK, turn furnace power off, and go to furnace control board. It may be mounted on a bunch of white "stand-offs". Loosen these and CAREFULLY turn it over, examine the back Look for burned marks or signs of overheating.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call. Let me know if you need more information, or send me the service offer(s) so we can proceed.
Customer reply replied 2 years ago
The request for phone call was a mistake my phone was freezing.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Board shows obvious signs of burned marks/overheating. Since we now know transformer is good, the board is the only thing between transformer and R-C reading 24 volts. If you can get me full furnace model number I can get the replacement board part number for you.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

I show part # ***** Found one here. But you may want to check around for better prices.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
One more question. What would make the board burn up. I don't want to replace if it will just burn up again. What can I test or check. Thank you for your help!!
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

It doesn't have to be any one thing. Boards go bad all the time. Remember, this furnace is not exactly new.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Let me know if you have additional questions. Otherwise, good luck! Thanks for using Just Answer and please don't forget to rate my service as that's how experts get paid (thanks in advance for any bonus left). Otherwise experts work at their own time and expense. Feel free to post back with any additional questions.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
3,972 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Hot water quit. Reset circuit breaker. What now? About a
About a week. On occasion water got hot. Sometimes, as now is cold. When I have reset circuit breaker it wasn't tripped, but still the aforementioned happens … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My circuit breaker is popping and i think it may caused by
my circuit breaker is popping and i think it may caused by my intertherm thermostat. can i disconnect the thermostat and would that allow me to reset the circuit breaker? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
This house is missing the circuit breaker for the disconnect
This house is missing the circuit breaker for the disconnect for the outside ac unit. What do I need to get to repair this?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
The compressor trips the circuit breaker in the house, not
the compressor trips the circuit breaker in the house, not immediately, about after 5 minutes. what are my options? can i replace only the compressor? It is a frigidare model FS3BC-042KA … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
Air Handler # NFCX3600C2 what causes the circuit breaker
Air Handler # NFCX3600C2 what causes the circuit breaker panel to fry? I replaced it once and the heat worked OK but when I tryed to run A C the board fryed again … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I, I installed a furnace control Board part # 62-24084-82.
I, I installed a furnace control Board part # 62-24084-82. It cycled once and will will not cycle again. all the controls are ok after checking them. any Ideas? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Turned off circuit breaker while furnace running ... turned
turned off circuit breaker while furnace running ... turned on circuit breaker ... furnace did not come back on ... got message system malfunction outside sensor error on carrier infinity 96. read you… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND IT RESET FOR A TIME THEN DISPLAY CAME BACK UP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Heil CA5536VKD2, circuit breaker trips when it
i have a Heil CA5536VKD2, circuit breaker trips when it turns on compressor runs for like a second then trips bad compressor? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I turned the circuit breaker off to my AC to replace a
I turned the circuit breaker off to my AC to replace a thermostat with a NEST thermostat. When finished, I turned the CB back on. No power. I put the old thermostat back on and still no power at therm… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I woke up this morning to a tripped furnace circuit breaker,
I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My HVAC is not working. The AC circuit breaker trips as soon
my HVAC is not working. The AC circuit breaker trips as soon as the, I guess, the outside unit try to start … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,631 satisfied customers
The circuit breaker keeps shutting off when the Rheem
The circuit breaker keeps shutting off when the Rheem furnance/air conditioner tries to come on. What is our problem? We just had a new capacitor put in about two weeks ago. … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
What size amp circuit breakers needed for lennox heat pump
what size amp circuit breakers needed for lennox heat pump 14hpx-036-230-21 and Lennox air handler cby25uh-036-230-10? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,194 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x