#16582 on Dec 31st 2015...
Trane xv90 Replaced inducer and control board with kit #16582 on Dec 31st 2015. Unit stopped running on 1-20-16. Inducer blower would not switch on. Internal error code. Just replaced with another board and inducer. Inducer starts, ramps up and then shuts down before the igniter engages. Error code 3 flashes. Bypassed pressure switches with same results
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have cleaned all the tubes and fittings as well
Answered in 15 minutes by:
1/26/2016
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago
heatncoolrepair
heatncoolrepair, HVAC Technician
Category: HVAC
Satisfied Customers: 75
Experience: 13 Years of Residential Furnace & A/C Repair Experience.
Verified

Hi there, can you tell me what error code 3 means? I believe this is the trane upgrade kit with a new AC inducer and control board? I've replaced a half dozen or so of these.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Draft pressure error.
a. Venting problem
b. Pressure switch problem
c. Inducer problem.Venting is good
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

I don't believe you can just bypass the pressure switches on this furnace and fake the circuit board out. If you are getting a pressure switch fault code, as I have too before on these, I would make sure the inducer is draining. Pull the little 90 degree hose adapter off the bottom of the inducer and see if water drains out. If it does, then the adapter is plugged and needs to be cleaned out with a little pipe brush. That little 90 degree adapter always plugs up.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
There is no water as the unit has not had time to run. The drain is clear.
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

Also make sure to clean out the trap and drain hoses really good too.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Trap and hoses are clear
Customer reply replied 2 years ago
Resistance across both switches is 1 ohm or less
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

if everything is clear, then it is a matter of checking to see if you are getting enough pressure to close the pressure switches. Do you have a manometer and are you familiar with checking pressures?

Ask Your Own HVAC Question
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

Also, is the inducer sealed up in the back or have a gasket?

Ask Your Own HVAC Question
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

Other things you can try are to run it with the exhaust pipe disconnected or the cover off the burner compartment to see if that closes the pressure switches and fires up.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I do not have a manometer.. I have blown into the tube and heard the switches close while the inducer is ramping up, but it still shuts down before the igniter starts
Customer reply replied 2 years ago
I have run it with the burner cover off
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

and it still does not kick on with the burner cover off? Also, have you checked the roll out switches on the burner or the hi-limit?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Sealed inducer with RTV as suggested in install manual
Customer reply replied 2 years ago
Is roll out No or NC. High limit is new
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

sounds like you have done everything correct. roll out should be NC

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I will re-check and get back to you. Have to run out to a Boy Scout meeting. I will get back to you ASAP. Thanks.
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

2" or 3" venting?

Ask Your Own HVAC Question
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

ok, how long before you return?

Ask Your Own HVAC Question
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

If you have a reverse flow switch on this furnace, like on figure 22 of the instructions, check to make sure that is also NC. If all these things check out, I would also check to make sure all the pressure switch hoses are tight on the fittings. If not, snip the ends off each of the hoses and reattach them. Also, blow through them to make sure they are not plugged. If that all checks out, then you need to check what kind of pressure you are getting with a manometer. If the pressures are good, replace the pressure switches, if they are bad, then check your furnace installation manual to make sure your venting is the correct size and length, and make sure there are no obstructions in the piping.

Ask Your Own HVAC Question
HVAC Technician: heatncoolrepair, HVAC Technician replied 2 years ago

I have to go. If you are happy with my service tonight, please don't forget to rate me. Have a good night.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask heatncoolrepair Your Own Question
heatncoolrepair
heatncoolrepair
heatncoolrepair, HVAC Technician
Category: HVAC
Satisfied Customers: 75
75 Satisfied Customers
Experience: 13 Years of Residential Furnace & A/C Repair Experience.

heatncoolrepair is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a luxaire furnace. Installed a new pressure switch
I have a luxaire furnace. Installed a new pressure switch but it still flashes pressure switch open. Blower comes on and line is clear. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
I have two identical Olsen gas furnaces - installed about 20
Hi - I have two identical Olsen gas furnaces - installed about 20 years ago - Model # HHS-90T - also noticed that I think the ignition control module is a "white - Rodgers" Model # 50A50-216. The issu… read more
Michael Ferryman
Michael Ferryman
97 satisfied customers
I had a dayton gas furnace installed by a friend, all looks
I had a dayton gas furnace installed by a friend, all looks good except that there is no draft diverter in the flue, and the blocked vent swiitch trips. Otherwise, the flue is unblocked. Do I need to … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
We have a Lennox furnace installed 2011. My husband went
We have a Lennox furnace installed 2011. My husband went downstairs and took (what he thought was the filter) to see if we could replace it, now we can't put it together and need somebody to help us, … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We had furnace installed 2 years ago. There is excessive
We had furnace installed 2 years ago. There is excessive rust on bottom of furnace. No leaks anywhere. Furnance is on cement slab with no moisture in basement. What could be causing this … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I am having a new furnace installed. I just had a Kelvinator
I am having a new furnace installed. I just had a Kelvinator model kg7sa furnace delivered. Is this an upflow or downflow furnace? … read more
Rick
Rick
Supervisor
24,042 satisfied customers
We just had a new furnace installed with the Hydrostat 3250
Hi Pearl. We just had a new furnace installed with the Hydrostat 3250 plus. We do not have a separate water tank. We have three zones and our upstairs zone is working correctly. The Honeywell reads 68… read more
Rick
Rick
Supervisor
24,042 satisfied customers
Our new Amana Furnace (installed earlier this year) won't
Hi Pearl, our new Amana Furnace (installed earlier this year) won't seem to heat up past 60-66 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
Sure. I have a Goodman gas-fired furnace installed around
Sure. I have a Goodman gas-fired furnace installed around 2005. Not working. When last checked, there were three red flashes indicating pressure switch circuit not closed. Changed thermostat batteries… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We recently had a brand new furnace installed. The
We recently had a brand new furnace installed. The technician said it was going to be highly efficient compared to the older model we had. After the installation, we noticed that the furnace is runnin… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Furnace install, permit and license requirements? I have a
Furnace install, permit and license requirements? I have a friend that works full time for an hvac company. He can help me install a furnace on the side but the license is through his company and they… read more
Rick
Rick
Supervisor
24,042 satisfied customers
I have a payne furnace.. installed this summer..it's not
I have a payne furnace.. installed this summer..it's not coming on when it should. Thermostat shows unit is on but temp keeps dropping … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 311aav furnace installed 6/2016 by Reliable Furnace
i have a 311aav furnace installed 6/2016 by Reliable Furnace c0. San jose CA. it has never worked properly. it cycles 9 minutes. error code 13 shows about 4.5 miniutes into the cycle. Reliable techs h… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have computerized luxaire furnace installed 2009, I cannot
I have computerized luxaire furnace installed 2009 , I cannot turn on heat , … read more
hvacdave84
hvacdave84
53 satisfied customers
My furnace was replaced in 2014 and the furnace installer
My furnace was replaced in 2014 and the furnace installer also put in a new Honeywell thermostat without charge. I assume it is the least expensive thermostat Honeywell makes. No identity code is on o… read more
Rick
Rick
Supervisor
24,042 satisfied customers
I have a ARCOAIRE RPJ II furnaced installed 10+ years ago. A
I have a ARCOAIRE RPJ II furnaced installed 10+ years ago. A change of tenant required local gas co to to turn service back on. Inspector refused because the existing (plastic) pipe had been recalled … read more
Rick
Rick
Supervisor
24,042 satisfied customers
I had a Rheem furnace installed R95PA0601317M and the
I had a Rheem furnace installed R95PA0601317M and the installer did not leave an owners' manual. I have contacted them several times with no result. Can I get an owners' manual directly from Rheem? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently had an Airhandler and furnace installed at my
I recently had an Airhandler and furnace installed at my home. It continually trips the breaker. I have a video of the airhandler fan shutting off and turning back on. It happens 7 times in the 2 minu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x