HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

Problem … 14 years old - Goodman GMPN Multi-Positional Gas…

Customer Question
Problem … 14 years old...
Problem … 14 years old - Goodman GMPN Multi-Positional Gas Furnace Dependable 92 (GMPN100-4) Starting furnace sequence - Red LED indicator is STEADY - Inducer running great - Igniter glowing hot (20 seconds) But NO gas FLAME !!! - 3 more repeat NO gas FLAME … during cycling’s the LED indicator is STEADY … Furnace locks out, then Red LED indicator blinking slowly constantly every second forever … Primary heat exchanger is in great shape and no rust or cracks and cleaned with low pressure air & vacuum. Secondary heat exchanger cleaned (tubes cleaned also) Pri***** *****mit switch OHM reading 0.1 – Pressure switch 3.2 OHM with manual vacuum – Rollout switches are closed – Gas valve solenoid readings .599 OHM. Any idea what could be the problem?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
1/24/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,178
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

hello,

At any time do you get 24v on the wire to gas valve from roll out switch?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
download furnace - First rollout is connected to Gas Valve. do I have to chech without gas on or off?
Customer reply replied 2 years ago
Just wondering R U there ?
Customer reply replied 2 years ago
Are you around still?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

sorry had to clean sat dish off (snow)

You will put one meter lead to blue wire on valve and other to ground.

See if valve gets 3 seconds of 24v after ignitor glows aprox 20 seconds

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Sorry 4 U im north of Toronto and hardly any snow here !!! - You wrote ... You will put one meter lead to blue wire on valve and other to ground. Q GAS off or On also disconnect wires or not?See if valve gets 3 seconds of 24v after ignitor glows aprox 20 seconds
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

power on, gas valve on

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

leave wires attached

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Volt meter 0.11 V
Customer reply replied 2 years ago
I got 0.1 Volts
Customer reply replied 2 years ago
0.11 not 0.1
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

thank you....this means you have a bad circuit board. It sends al signals except the final 24v to the valve. This is a circuit board defect.

No fix except to replace the circuit board

Billy

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Can i check voltage to the gas valve? Im suspecting valve / solenoid ? Solenoid has 0.599 Ohm only - i belive it has to by arroung 1500 ?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

that is what we were checking at the valve after the ignitor glow.

You have 2 choices:

24v goes to valve for 3 seconds during ignitor glow but no gas = bad gas valve.

NO 24v to gas valve during ignitor glow = bad board.

It is either board or valve.

The 24v test tells us which.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
What if i connect meter to Blue & roll out switch wire (purple) instead Blue & ground, then run the test again?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

you should be testing the wire that goes to valve from roll out...not the wire that goes back to board

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Sorry i don't understand "back to board" ??
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

gas valve has 2 wires..one comes from roll out....the other wire runs back to circuit board...the wire back to board is common and will not read voltage

Ask Your Own HVAC Question
Customer reply replied 2 years ago
You mentioned one meter prong to ground other is to blue wire they all connected to the board aren't they?
Customer reply replied 2 years ago
This is a single not two stage furnace
Customer reply replied 2 years ago
only two wires to GAS VALVE
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

I know....that is why I said test the wire from roll out to gas valve....the other wire (thats 2 all together) goes back to board. The GMPN is a basic single stage gas valve.

You should be able to tell if valve gets 24v no different that how a light bulb gets 120v

Ask Your Own HVAC Question
Customer reply replied 2 years ago
then why i have to meter The Blue wire to Ground - Why not Blue & Roolout wire to test for 24v
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

my schematic shows blue as the 24 in from rollout.

But that is also why I say wire from roll out.

You can also remove both wires and hook one wire to one meter lead and the other wire to remaining meter lead.

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

but they have to be off the valve this way

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Billy - Yes its crazy schematics -- All my roll out switches have people wires! ill try it in 10 min now we getting somewhere .. Looking forward for 24 volt readings get back to you in 10 min
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

this will boil down to the 24v present or not...24v present = bad valve

no 24v = bad board

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Billy i got 0.27 - 0.37 for 2/3 seconds - the numbers i think are great BUT - i just don't understand why . did i set my meter wrong?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

what setting is on your meter or can you post pic?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

set for 200 and test a working outlet. verify 120v....then leave set for 200 and test valve

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have 120 V coming in to furnace
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

yes...I was testing meter...if it reads 120v for a supply voltage...then it should read a full 24-28v for gas valve.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Should i disconnect the Thermostat and JUMP >>> Red &White to call for heat?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

if you are testing while ignitor glows...then r to w is not needed. R to W is is the furnace doesnt start at all...you have exhaust fan, glow etc...so thermostat works.

If you test the gas valve the entire time the ignitor glows until it goes out...And...

no 24v reading happens = board

24v happens is bad valve

Ask Your Own HVAC Question
Customer reply replied 2 years ago
One more thing .... Let’s say one of the rollout switches out of four are defective? Can it be a defective circuit to run the 24 V test? Reason being for my question is that prior my furnace problem I had to reset one of my rollout switch time to time to run heat. (I never had Flame Rollout) after several days of manually rollout switch resetting my furnace gave up. Then I cleaned Primary & Secondary exchangers 100%. So my question again … What is if one of the rollout switches are defective? Can it be a defective circuit to run the 24 V test to gas valve? Also gas valve solenoid reading is only 599 ohm
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

you are getting a flame fail code..not a roll out or limit code.

BUT....all you would do is work backward following that wire....looking for 24v.

No different than looking for power to an outlet. If not at one point back track to next...or start where you know you have 24v...like the first roll out or limit. The schematic on the blower door shows the path

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

we care about voltage more than ohming coils at this point. find yur 24v...and go from there...

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Billy - thank you for your time trying to help me tonight – doing some additional tests tomorrow. It’s getting late. Can I get back to you tomorrow? Thanks much! Steve :)
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Ready to try some more?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi Billy - im back - had now time to go ahead with my furnace problem. Just for now i have another creation i have before im retiring for the night. Question is after 3 times running furnace with no Gas Flame (i can hear Gas valve or solenoid CLICKING ) Also LED solid ... But after 3 repeat i have Slow blinking LED light for ever on till i shot off the system.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,545
Experience: Furnace, A/C and heat pump specialist.
Verified

Looks like Billy has opened question up for other experts.First of all take a look at this diagram and tell me if wires and colors match what you have .

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi Airheatman - This is Steve - The wires and colors do match. Few weeks ago after cleaning first an secondary heat exchangers i had fast led blinking. Then i checked out the diagram and switched one wire according to the diagram. I have Solid Red LED light at start. I have 27 V at gas valve. Running 3 times - No Flame !!! - Then LED blinking (approx every second) for ever until i shoot it off.
Customer reply replied 2 years ago
Hi Airheatman - This is Steve - The wires and colors do match. Few weeks ago after cleaning first an secondary heat exchangers i had fast led blinking. Then i checked out the diagram and switched one wire according to the diagram. I have Solid Red LED light at start. I have 27 V at gas valve. Running 3 times - No Flame !!! - Then LED blinking (approx every second) for ever until i shoot it off.
NOW What if? … Can I bypass (ONLY temporarily) one rollout switch by disconnecting wires then connect them together to check if rollout switch malfunctioning? I’m suspecting upper middle because all my problems started with that. I had to reset it many – many times manually for few days to have heat. Then furnace stopped working. At that point I CLEANED & checked out Heat exchangers. The look great! No rust or cracks. Also I never experienced any gas/flame rollout before. So what if the rollout switch defective? Can I test the furnace by bypass the rollout switch? I assume if rollout is defective then Gas Valve will not open even if I got 27V.
..
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Good evening Steve. If you are getting 27v at gas valve, either the gas valve is defective or you have a gas pressure issue.To determine which, attach a manometer or gas pressure gauge that reads inches of water column to inlet and out sides of valve.

If you had an open limit the led would blink 4 times pause , 4 times pause until limit is closed.

If limit was open we would not get igniter.If rollout switches were open we would not get the 27v to valve.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi - I have gas oven and no problem. I don't have manometer. I have solid LED. Igniter is glowing/working.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK with ignitor glowing do we get the 24 to 28 v to gas valve?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
27 V
Customer reply replied 2 years ago
27 v and i can hear Valve clicking
Customer reply replied 2 years ago
Forgot to tell you i bypassed Termostat by connectin R & V wires
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK if all other gas appliances are working, most likely a bad gas valve.If we are getting 27v to valve there are no limits,pressure switch or rollouts that are not doing what they should.If any of these were an issue, the board would not send 27v to valve. The solenoid sounds like it is clicking but gas valve not opening.Replace valve and this should solve your problem

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

At this point of furnace sequence valve should be open.To question any other component such as a limit or a pressure switch would be like a car engine not starting and wondering if low tire could be the issue.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok ill order gad valve next couple of days - Can i get back to you after its replaced?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Absolutely.You can wait until we are finished to rate answer.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thank and have a nice evening!
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

forward to hearing back.You have a great evening too.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,545
9,545 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Lennox G51MP that is flaking (no ignition). It just
Hi Pearl. I have a Lennox G51MP that is flaking (no ignition). It just ran through a purge cycle (again) and then shut down. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a Amana hvac pgd42c0902e that the heat is not coming
I have a Amana hvac pgd42c0902e that the heat is not coming on. Both blowers just stay running. The main control board has a red LED that flashes 4 times. I checked both of the limit switch's the one … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My furnace is not heating. The diag is saying primary limit
My furnace is not heating. The diag is saying pri***** *****mit open … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
My carrier furnace, model 58PAV070-12 does not come when the
My carrier furnace, model 58PAV070-12 does not come when the thermostat calls for heat, but if I cycle the power coming into the unit, it comes on and lights. Any suggestions? … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a rude achiever series super quiet 80 which was
I have a rude achiever series super quiet 80 which was cycling off after the the burners kicked on for a few seconds, I cleaned the flame sensor and now the blower comes on, the light labeled “ok” bli… read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a Centurion 2 not working with the flashing indicator
I have a Centurion 2 not working with the green flashing indicator 4 time. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
The Furnace stopped working but the fan keeps going. I don't
The Furnace stopped working but the fan keeps going. I don't know where the pilot light is supposed to be. On the motherboard the red light flashes 11 times. I changed the ? it turns to a steady green… read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have carrier furnace model CK5BXA048021AAAA that is not
I have carrier furnace model CK5BXA048021AAAA that is not heating up. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a lennoxG43UF-36B-70-09 furnace. Fan running but no
I have a lennoxG43UF-36B-70-09 furnace. Fan running but no heat. Filter clean. Message lights indicate"a)primary … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a Frigidaire furnace model g6ra096-16 and the blower
I have a Frigidaire furnace model g6ra096-16 and the blower fan motor won t stop running evenwhen thermastac is off and no heat coming on whats the problem?… read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
Unit will not heat... Unit will not turn off through
Unit will not heat... Unit will not turn off through honeywell FocusPro 6000 … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have an infinity touch thermostat from carrier. On the
I have an infinity touch thermostat from carrier. On the screen, it says system fault, and under it, it says 33-limit fault. There currently is no heat in the house. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I am receiving a 3/3 code on my furnace and I checked the
I am receiving a 3/3 code on my bryant furnace and I checked the filter and it stops in mid operation and started humming?Please send my answers to***@******.*** instead of***@******.***, thank You.… read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a Ruud Achiever 90 Plus furnace and the burner will
I have a Ruud Achiever 90 Plus furnace and the burner will not ignite … read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
GMPN Multi-Positional Gas Furnace Dependable 92 (GMPN100-4)
GMPN Multi-Positional Gas Furnace Dependable 92 (GMPN100-4) Starting furnace - Red LED indicator steady - Inducer running great - Igniter turning on – NO FLAME … Inducer still running - After 3-4 repe… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have I carrier AC heater and its flashing 33 error code.
I have I carrier AC heater and its flashing 33 error code. It won't even try to start it does nothing.… read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
I have a Lennox G60UHV, the furnace will light and run for
I have a Lennox G60UHV, the furnace will light and run for a short time and kick off. It gives the fault Primary/secondary limit switch open Primary secondary or rollout switch open. Any help would be… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a RHEEM furnace/air combo, natural gas furnace, no action
I have a RHEEM furnace/air combo, natural gas furnace, no action when turn on just hear a blower come on, no sparks from elect ignitor and no flames from 4 burners, error LED five blinks what does thi… read more
airheatman
airheatman
HVAC Technician
6 years college
9,545 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x