I'm not sure if I was on here already We are in Allentown PA and in the blizzard we live in a newer home with a Lennox G43UF-48C-090-08 are you familiar?

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

We had the thermostat set to 71 but it was freezing this morning and it was only 55 in our house. we called the gas company and they said to make sure the intake pvc was clear of snow I cleared it then I changed batteries in the thermostat. turned it down to 40 and went down to furnace and turned off main switch for 5 minutes I turned it back on and put thermostat back to 73 it says hold and no heat cold air is blowing

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 23 minutes by:
1/23/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

hello sorry for delay. Are you ready to proceed?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Ok, I understand you are unfortunate enough to be in the blizzard?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
but if we could figure out how to send a heat signal in our furnace so that the heat starts would be good
Customer reply replied 2 years ago
The fans are blowing properly the thermostat is responding to the drop in temperature and also turning on the fans when we turn the heat on but there is nothing that's making heat start down at the furnace
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Your furnace has 2 pipes attached. One out the side higher than the other. This pipe is the intake you have heard about...but first, in the furnace bottom section is a circuit board with blinking lights...can you tell me the pattern?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
How do i decipher the pattern? There is a green light and a red light. The red light is a slow pattern the green light is on steady
Customer reply replied 2 years ago
The red light be fat heartbeat pace the green light is solid no blinking
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

refer to them as led 1 (left) and Led 2 (right)

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Sorry for the typo I meant the led 1 blinks at a heartbeat pace and led 2 stays lit no blink
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Ok, by chance is the filter plugged or was when this happened?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
What do you mean by filter the screen that's next to the furnace or the intake that is outside
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

filter by furnace

Ask Your Own HVAC Question
Customer reply replied 2 years ago
That is a new filter in there
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

This is an overheat code of a tripped limit.

Do you mind a bit of hands on checking?

On the front wall of the furnace is a credit card sized flat plate with 2 wires do you see this?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Do I need to turn the fans off in the switch before I open the panel?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

turn power switch off

remove upper door

locate switch

let me know when ready

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

switch means the flat credit card sized plate

Ask Your Own HVAC Question
Customer reply replied 2 years ago
There is a light switch looking power switch on the right side of the furnace I turn that off is that okay? So the fan won't be running
Customer reply replied 2 years ago
Okay and I am in the upper door and I see a on off switch with two wires
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Against the back wall of the upper section...flat on the wall...the credit card sized plate..2 wires...does not say on or off...just a flat plate 2 wires

Ask Your Own HVAC Question
Customer reply replied 2 years ago
it looks like it's like a burgundy color the wires are two on the left purple blue one on the right blue
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

ok tap that flat plate a couple times....then turn power back on and tell me what code does on the lights

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Same led 1 heart beat blink led 2 solid lit no blink
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

thank you,

now follow the wires to that switch. One leads direct back to circuit board...the other goes to another switch...can you follow for me and tell me result of what the other wire leads to?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The connection on the left has two wires -a purple and blue.... the blue one goes to the circuit board and the purple one goes to a smaller round black gadget about 2.5 inch round. The connection on the right is a solitary blue wite that goes to a bigger round gadget about 9 to 10 inches round
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

ok the can you post a pic of this? Thre were several different versions of this model and I would like to be certain

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I sent you a photo and a video please let me know if they came through
Customer reply replied 2 years ago
Okay I was just told that the video is too large so you won't be getting that
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

did you use the attach files link?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I just sent you another photo
Customer reply replied 2 years ago
I use the Add Files link and took 2 or 3 photos that you should have
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

havent seen photos pop up yet...see page 8 HERE

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I received the file you sent to me. Why are you sending that to me I have no idea how to read these parts that's why I contacted you
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

I wanted you to see if the any of the parts matched what you were trying to show me

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The diagram is too flat and complicated it doesn't really specify what I'm looking at . Sorry my phone jammed and I had to restart Can you tell me what this code meansPrimary or secondary limit switch open. Limit must close within 3 minutes or unit goes into 1 hour watchguard.
Customer reply replied 2 years ago
I just have to sit and wait now and hope that somebody gets back to me soon and maybe 24 hours in a blizzard? What kind of service is this? I turned my phone off to restart it while were in the middle of assessing the situation and the tech disappears
Customer reply replied 2 years ago
The add files to send you photos feature is not working
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a lennox G43UF-36B-070-08 furnace and the fan is
I have a lennox G43UF-36B-070-08 furnace and the fan is constantly running but it is not blowing any heat … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am a new owner of a Lennox boiler (Model# ML 193UH). Last
I am a new owner of a Lennox boiler (Model# ***** 193UH). Last week during the blizzard the pilot went out and came to realize that the intake and exhaust pipes were covered over by snow. When they bu… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a lennox el296uhe series furnace. We are having a
I have a lennox el296uhe series furnace. We are having a blizzard in Pennsylvania and my furnace is not working. I am getting a error message e223 and e270 Can you help me?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a 9200 weathermaker and it's not working. We are in
We have a 9200 weathermaker and it's not working. We are in a blizzard and think we just found and cleared snow from the intake vents. What do we do next?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Furnace keeps shutting off prematurely name is ***** *****
Customer: furnace keeps shutting off prematurely name is ***** ***** … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a EL296UHE - the furnace only comes on a minute at a
I have a EL296UHE - the furnace only comes on for about a minute at a time and then shuts off - it's dropped to 55 degrees in the house… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My Lennox furnace will only cycle once an hour--I have had
My Lennox furnace will only cycle once an hour--I have had this problem for over 2 months. A new thermostat and integrated control board have been installed, but the problem remains. What can fix it??… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My G26q3-50-1 furnace is turning on but there is no pilot light.
My G26q3-50-1 furnace is turning on but there is no pilot light. We turned the thermostate low and let it sit for 15 minutes then tried again. Can you suggest something else?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We have a 2008 Bryant Evolution 90i furnace and it is 15 degrees
We have a 2008 Bryant Evolution 90i furnace and it is 15 degrees outside... furnace quit heating....thermostat controls show no problems. Just cleared snow away from our intake and exhaust air. Powere… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
lennox furnace model number c33-43c-2f-3 stops before reaching
lennox furnace model number c33-43c-2f-3 stops before reaching temp. diagnostic lights are red and green flashing simultaneously or red off and green flashing slow.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox G61MPV-60C-110 furnace. 3 PVC pipes are
I have a Lennox G61MPV-60C-110 furnace. 3" PVC pipes are used for the intake and exhuast vents. The pipes exit my house about 12" above the grade. A Elbow fitting is attached to each pipe facing 90 de… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
I can hear my heater turn on, but its not working properly.
I can hear my heater turn on, but it's not working properly. There is a blizzard here, can that affect it?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
We are in the middle a blizzard in Milwaukee with high winds
We are in the middle a blizzard in Milwaukee with high winds with gusts of 50 miles per hour. I cleard the intake and exhaust tubes on the side of the house. After I turn the toggle switch on the outs… read more
Electrifier
Electrifier
Owner - Contractor
Bachelor's Degree
147 satisfied customers
Hi, I have a Lennox G43UF furnace that is only intermittently
Hi, I have a Lennox G43UF furnace that is only intermittently working. It's keeping the house at around 66, with the thermostat set at 69. The LED indicator lights are alternating slowly. The cycle se… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Were in the middle of a Chicago blizzard and I woke up to
We're in the middle of a Chicago blizzard and I woke up to take care of the baby and the heat wasn't working. The LED light was blinking 7 times and online it said that on a Diamond 80 York that meant… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Ruud achiever super save 80 gas furnace in a house
I have a Ruud achiever super save 80 gas furnace in a house I bought this summer. We are under a blizzard warning and the temp is going down to minus three tonight and the furnace has quit working. Th… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
I have a 4 year old furnace with a lennox 78m4701 circuit
I have a 4 year old furnace with a lennox 78m4701 circuit board. The heater will start up and run for about 5 minutes (fast blinking red and green then red goes out and the green fast flashes) then tu… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My G14 Lennox Pulse furnace quickly starts and stops about
My G14 Lennox Pulse furnace quickly starts and stops about three times, then dos not start again. I have had a problem with the fresh air intake pipe clogging with snow. When I cleaned it out, the fur… read more
Bill
Bill
High School or GED
318 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x