My Rheem 90 classic is not blowing heat. I see a blinking…

Customer Question
My Rheem 90 classic...

My Rheem 90 classic is not blowing heat. I see a green blinking light for the ok,solid green for power and no ***** ***** light on

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

It uses gas for the heat the gas knob is turned to the on position

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Not sure why the gas burner is not starting and the blower is not kicking on.
Answered in 16 minutes by:
1/23/2016
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,835
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

I need the model number of your furnace. You can find it on the rating tag inside the blower compartment

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I was able to get it to work, but the gas will not stay lit. It is a Rheem Classic 90
Customer reply replied 2 years ago
I take off the panel and manually light it, but just a few seconds after I close the panel the gas goes out
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

That's the series not the model number. I need the model number on the rating tag.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I did go outside and remove the 2 foot of snow that had drifted around the gas pipe that goes into the house
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Snow around the gas pipe makes no difference. Snow around the exhaust does. I can't help you until you give me the actual model number

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rheem Classic 90 Plus, sounds like it will start to
Hello - I have a Rheem Classic 90 Plus, sounds like it will start to kick on, then stops before the blowers power up. Two Green lights I can see, one on the right is solid, left is blinking steadily.… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have a furnance in my mobile home. Model DGAA077BDTA and
I have a coleman furnance in my mobile home. Model DGAA077BDTA and we have a steady green light and one blinking red light which indicates a ignitor issue. Can someone assist?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem gas furnace blower stays on after temp is reached,
Rheem gas furnace blower stays on after temp is reached, blows out cool air, turn up thermostat, igniter does not kick in. is that a motherboard or ignitor problem?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox wisper heat gas furnace and it only blows cold
I have a Lennox wisper heat gas furnace and it only blows cold air. It looks like the burners won't ignite.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have RUUD Silhouette heater, Model # ***** 10NBRJR When
I have RUUD Silhouette heater, Model # ***** 10NBRJR When I turn the heater on the inducer motor starts running. After a few seconds the fan starts but the ignitor never glows, the gas doesn't come on… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a gmt power vented multi-position gas furnace, it started
I have a gmt power vented multi-position gas furnace, it started only blowing cold air, i checked and the flame is out. it won't come back on. what to do.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We have had snow freezing temps in colorado the past 2 days
We have had snow freezing temps in colorado the past 2 days (-1 this am) woke to thermostat reading 44. Checked furnace and black circle thing was rotating very slowly. I went through process of dropp… read more
Joe Chappell
Joe Chappell
Building Engineer
7 satisfied customers
Same unit rheem classic 90 plus. When I restart the furnace
Same unit rheem classic 90 plus. When I restart the furnace it goes thru start up fine including the ignition but when the blower kicks in the flame goes out and the ok light blinks.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
hi I have a rheem classic super quiet 80 furnace. stopped
hi I have a rheem classic super quiet 80 furnace. stopped heating last night. on bottom panel the power and status light are solid green (no blinking) the red light does not come on. I don't hear it t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Matthew, I have a Rudd Achiever Super Quiet 80 that will
Matthew, I have a Rudd Achiever Super Quiet 80 that will not light when the temp goes below the thermostat settings. When the thermostat is turned off and then back on, everything seems to be ok. Is t… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Rheem Classic 90 Plus Furnace Blower kicks on. Burner is
Rheem Classic 90 Plus Furnace Blower kicks on. Burner is ignited. Runs for a minute then kicks off. Blower kicks back on but flame on burner is no longer appearing. Turn it off then on again. I have a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a RHEEM furnace/air combo, natural gas furnace, no action
I have a RHEEM furnace/air combo, natural gas furnace, no action when turn on just hear a blower come on, no sparks from elect ignitor and no flames from 4 burners, error LED five blinks what does thi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Rheem classic quiet 80. The pilot wont come on and
I have a Rheem classic quiet 80. The pilot won't come on and the instructions are not legible. How do I light the pilot?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Rheem Classic 90 Plus and the furnace will not stay
I have a Rheem Classic 90 Plus and the furnace will not stay on. It will go on if I turn the thermostat heat button off and on but it only stays on for about three minutes.… read more
Paul
Paul
Vocational, Technical or Trade Scho
108 satisfied customers
We have a Rheem Classic 90 Plus, model RCBA 3765GGZ1XI. There
We have a Rheem Classic 90 Plus, model RCBA 3765GGZ1XI. There is a green light on, the air is coming through the vents, it sounds like it's on, but only cold air is coming out. It's getting colder and… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a new home about 1 year old with 3 lennox central air/heat
I have a new home about 1 year old with 3 lennox central air/heat units. The A frames in the atic are all gas for heat. Now one unit comes on but just blows cold air. I checked and the gas jets are ne… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Rheem Classic 90 plus furnace/air not working this morning
Rheem Classic 90 plus furnace/air not working this morning - no heat. Thermostat seems ok (24vac at both red and white wire. After pushing in the filter interlock switch, on the control board the pwr … read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have a rheem classic 90 plus, it is 3 years old. It is a
I have a rheem classic 90 plus, it is 3 years old. It is a gas furnnse. It is turning off and on, sometimes it does not fire up, and just blows cold air. Othertimes it runs like a champ.… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.