I have a AC/ natural gas furnace combination unit all

Customer Question
enclosed in one big unit...
I have a AC/ natural gas furnace combination unit all enclosed in one big unit that sits outside our house. We got a lot of snow overnight and now the heat won't work. The fan is still running but its just circulating cold air. Any ideas on how to get the furnace running again? Thanks
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
1/23/2016
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,024
Experience: Furnace, A/C and heat pump specialist.
Verified

Let's start by making sure the vent on side of unit is not blocked rt filled with snow.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
we've completely cleared all snow on and around the unit.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

1. Give me complete model on unit

2. Tell me exactly what if anything happens on call for heat

Ask Your Own HVAC Question
Customer reply replied 2 years ago
It's model 48GS-042090301 serial 3501G13220.The fan is running and circulating cool air but the heat is kicking on at all
Customer reply replied 2 years ago
It's blinking 7 times
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Sorry had to reboot computer.let me get my manual opened back up.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
It's saying that means a rollout switch fault
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Thanks for your patience. The 7 flash code indicates a flame rollout switch is tripped. Look just above burners for small rollout switches with 2 wires attached and small red button in between wires, Push those buttons and lets see if they will reset.

http://i.imgur.com/CGkB9sa.jpg

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I don't immediately see the burners. Any idea where they might be located in relation to the red flashing light?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Looks like someone may have replaced with wrong switch.These should have a reset button as shown earlier.Also looks like one may already be bypassed .Picture gets a bit blurry when I enlarge so I cant really tell on it.

For a test to see if code will o awy and burners light, unplug and connect the blue wires to this switch.

http://i.imgur.com/WqmGzzO.png

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am replacing a Honeywell S86F intermittent pilot on a 1983
I am replacing a Honeywell S86F intermittent pilot on a 1983 Heil natural gas furnace. I am installing a S8610U3009 but the manual is confuing on how the wires should be connected from the old to the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Luxaire furnace - high efficiency - wont start
I have a Luxaire 90+ high efficeny furnace that will not produce heat or light, the exhaust fan does run when I turn the thermostat on. The blower does not run or blow air through the returns. It is a… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I need to replace a Honeywell natural gas furnace main valve
I need to replace a Honeywell natural gas furnace main valve V804 24V60hz-0.2A class 2 transe what valve will replace this valve… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I own a Lennox Conservator III G16 natural gas furnace/home
I own a Lennox Conservator III G16 natural gas furnace/home heater. It has a problem which I trying to troubleshoot and repair myself. With the thermostat turned all the way down (no heat commanded), … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Ducane natural gas furnace. It quit working today.
I have a Ducane natural gas furnace. It quit working today. The pilot doesn't always light and if it does, the burners go out right after they ignite. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gibson KG7SC090D35C 92% afue upflow natural gas furnace.
Gibson KG7SC090D35C 92% afue upflow natural gas furnace. Furnace running normal heat cycle. Flame in burner goes out, fan runs constantly. Temporary solution reset flame roll out switch. Then furnace … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HVAC, 30 year old natural gas furnace, blower starts and
HVAC, 30 year old natural gas furnace, blower starts and heater relay on circuit board immediately clicks off. Does not trip circuit breaker. Thinking bad relay or over amp load condition, maybe dead … read more
Bill
Bill
Service Mgr
99 satisfied customers
I have a new Rheem 95P single stage natural gas furnace and
I have a new Rheem 95P single stage natural gas furnace and I'm getting a code 56, not listed in the manual. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a ruud ultra series natural gas furnace. it will not
i have a ruud ultra series natural gas furnace. it will not light the burner when it tries. it is flashing code 45. what it wrong … read more
airheatman
airheatman
HVAC Technician
9,024 satisfied customers
I have a Rheem classic 90 plus natural gas furnace that is
Hi, I have a Rheem classic 90 plus natural gas furnace that is not properly igniting. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Have Ruud natural gas furnace and the gas valve opens after
Have Ruud natural gas furnace and the gas valve opens after the purge does its thing and only stays on for approx 3-5 seconds. Then goes off. The flame rod sensor light never comes on. Changed the rod… read more
airheatman
airheatman
HVAC Technician
9,024 satisfied customers
I have a Payne Forced air Natural gas furnace with a
I have a Payne Forced air Natural gas furnace with a condenser pumo on the side. the pump will not shut off. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a tempstar natural gas furnace model nug5075bfb1 with
I have a tempstar natural gas furnace model nug5075bfb1 with a S8600M ignition module that is giving me trouble. The furnace operates correctly most of the time but occasionally requires multiple trie… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an Nordyne M1M series heater for manufactured home.
I have an Nordyne M1M series heater for manufactured home. The red LED light is flashing 4 flashes. Error code is "lockout due to failed ignition". Is there something I can do to fix this?… read more
airheatman
airheatman
HVAC Technician
9,024 satisfied customers
I have a Luxaire Model PBLU-LD08N040A natural gas furnace that
I have a Luxaire Model PBLU-LD08N040A natural gas furnace that when main burners light, is delayed - lights rough. I've tried repositioning the HSI and also checked gas pressure. What else could I try… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
My Nordyne natural gas furnace , has a yellow blinking light,
My Nordyne natural gas furnace , has a yellow blinking light, means weak flame. what can i do to fix this… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have an old sunbeam/american standard natural gas furnace.
I have an old sunbeam/american standard natural gas furnace. It has a button to press to crank it up. Makes all the burners light up. It usually stays depressed after I press it in, lighting it for th… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
my bryant plus 80 natural gas furnace has a intermittent problem,
my bryant plus 80 natural gas furnace has a intermittent problem, it in turn sets a code 14 which is ignition lockout and then says refer to code 34 which leads me to believe that there is a problem w… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x