I have a furnace that has Ultrazone EWC-ST-2E control panel.

Customer Question
I have a furnace...

I have a furnace that has Ultrazone EWC-ST-2E control panel. The furnace does not start when heat is required. It starts when I pull the relay out and put it back. What could be the problem?

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

It works fine for cooling and also when heating is not required frequently. That is when it is not too cold outside

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 hours by:
1/23/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

I am very sorry your question has not been picked up yet.

I just logged on and found you had not been assisted.

Please let me know if you still need help and I will do my best. Please do not "Rate" as we have not worked toward an answer yet.

If you would like to proceed let me know by replying.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I still need help
Customer reply replied 2 years ago
Where is my answer?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

the relay you are pulling out....is it in the panel or the unit and what relay is it?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Out side the control panel. It is line electric coil CRH102C - 24 VAC
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Ok that is breaking the 24v circuit and restarting...does turning thermostat off/on do the same thing?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Turning off and on the thermostat did restart the furnace same as the relay switch
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Thank you, ***** ***** it is a 2 zone panel...does the other thermostat react same same way or just the master?

Or does second zonenot work until master off/on?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The second zone did not start until the master thermostat off and on
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
23,151 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Pearl ... I put a new Nest 3D generation thermostat on the
Pearl ... good afternoon. I put a new Nest 3D generation thermostat on the upper zone of my house but there is no power to the RH wire. I checked the fuse and it looked good. Is there a reset on my HV… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
I'm trying to update my old Ultra Zone: EWC-ST-2D controller
I'm trying to update my old Ultra Zone: EWC-ST-2D controller to a new EWC NCM-300. My wiring is as follows using a heat pump and Oil Burner as well as Air con feeding 2 zones in the house: 1. R, ???? 2. RH/Blue wire Heating Transformer 3. RC/orange O/B (energize reversing valve on call for cool) cooling Transformer 4. G>>Fan relay, 5. Yellow>>Y1 compressor relay 6. White>> W1 Heat Control … read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
How to hook up my Honeywell Wi-Fi thermostat instead of
Trying to hook up a Honeywell wifi thermostat to replace my Luxpro standard thermostat/ System is Gas forced hot air. Current wires are G Y W RH B O RC Honeywell is K Y2 W2 G W C Y R RC I have traced … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I would like to wire a Honeywell RTH6500wf wifi thermostat
I would like to wire a Honeywell RTH6500wf wifi thermostat to a EWC-ST-2E/EWC-ST-3E series ULTRA-Zone Control Panel.… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
New furnace , when power turned on blower motor starts imm
New furnace , when power turned on blower motor starts immediately It is a williamson low boy model club 140 dd r st. Furnace burner started at first then shut down but blower stayed on now it runs as… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
can you use a Honeywell TH6220D programmable thermostat on
can you use a Honeywell TH6220D programmable thermostat on an EWC-ST-2D HVAC - not heat pump If yes - I need a wiring diagram to show where the B and O wires are connected. 6 wires available.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Need instructions for wiring my outside wood furnace.
I have installed an outside wood furnace, all left is the 24v wire. I have a York 9.v &EWC BMplus 3000 . I would like some instruction on how to wire it, so 1stage will be wood & 2stage gas, then if I… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
We have a ca 2001 Rheem furnace in our attic here in North
We have a ca 2001 Rheem furnace in our attic here in North Florida. For 10 years we have battled with the furnace and our HVAC contractor over the following. During the day or during moderately cold w… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a C33-60D-2F-1 Furnace and 10ACC-060-230-02 A/C unit
I have a C33-60D-2F-1 Furnace and 10ACC-060-230-02 A/C unit that both stopped working during the night. Thermostats sound like they're kicking in correctly. Tried to run FAN just by itself, but no luc… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Im trying to replace white-rogers thermostat with honeywell
I'm trying to replace white-rogers thermostat with honeywell rth7500, but matching up the wires are a challenge. Any suggestions on keeping this simple would be appreciated.… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Comfortmaker furnace. 2 weeks ago our power went
I have a Comfortmaker furnace. 2 weeks ago our power went out. It didn't go out fully. there was enough power to run certain appliances, but I am afraid the low voltage has damaged our air conditionin… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I am hooking up a HW RTH7600 thermostat to a gas FHA system
I am hooking up a HW RTH7600 thermostat to a gas FHA system with A/C. My old thermostat has 6 wires and goes to an EWC-ST-3E ultra zone control panel. Wires hook up as follows on the Zone-1 T'STAT in … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, my natural gas furnace cycles very frequently. Especially
Hi, my natural gas furnace cycles very frequently. Especially when its cold outside. It often cycles 2x per minute. This even occurs when its 65 in the apartment, and I set the digital thermostat to 8… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have an A/C unit (Furnace) that heats ok so long as the temperature
I have an A/C unit (Furnace) that heats ok so long as the temperature isn't too cold. Otherwise it doesn't work with it is too cold (i.e. 35 degrees outside or less). The problem is puzzling but I can… read more
Bill
Bill
High School or GED
318 satisfied customers
Hi. I have a 2006 carrier infinity system with 4 zones. All
Hi. I have a 2006 carrier infinity system with 4 zones. All carrier equipment. The keypads were blank yesterday. I replaced the 3a fuse. everything was fine. This evening, when I got home from work, t… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,151 satisfied customers
Im trying to update my thermostats with some touchscreen models.
I'm trying to update my thermostats with some touchscreen models. I currently have honeywell digital programmable thermostats that are about 14 years old. I just bought new Honeywell TH8110U1003's and… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
hi,I have a furnace no-start problem. !st off, the ac works
hi,I have a furnace no-start problem. !st off, the ac works fine but when I try to start the furnace I get a click,a buzz but the draft inducer will not start.A friend told me how to jump-test thermos… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing a honeywell rth7600 series. I currently
I am installing a honeywell rth7600 series. I currently have an ewc with r,y, w, g, o and b wires. It is two zones and does not have a heat pump. What do I do with the o and b wires. the system is not… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x