First the burners was shutting off and on and not reaching the desired temperature and the heat was not rising to the upper floors. We changed the pump and the relay and the heat came on now for more than 10 minutes and then shut down again.After cleaning burners they do not light. The pilot light is on and

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

We have a Dunkirk 20 year old system and suddenly we were not getting heat to all the floors. The pump was change and the Relay. Once this was installed then the heat came on longer but shut down again. Looking at videos indicated a heating rod may need cleaning. However, this system does not appear to have one. Thereafter, we took the burners apart to clean and re-installed. Now the pilot light comes one and now the burners don't even light....Please help.

Contractor's Assistant: OK got it. Last thing — JustAnswer charges a fee (generally around $18) to post your type of question to HVAC Experts (you only pay if satisfied). There are a couple customers ahead of you. We can help you for less if you're not in a rush. Are you willing to wait a bit?

OK no problem my husband is trying....needs help

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 years ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call. Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 9 hours by:
1/22/2016
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,846
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Sorry for the delay I just saw your question when I logged in this morning. What is the model number of your boiler? does it have a standing pilot (lit all the time) or does it have electronic ignition?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
PVW 150
Customer reply replied 2 years ago
Try to find manual on-line but lucked out.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Give me a few to see what I can find for specs

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Has a standing pilot lit all the time.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Ok, I struck out finding specs for this model. Can you give me pics of the boiler showing the controls, vent connection and an overall shot? you can post pics here by clicking on ADD FILES next to the SEND button

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I am trying
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

No rush, I'm here til ~ 7pm more or less (not including breaks)

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The file is too large to add. Can I forward on an e-mail
Customer reply replied 2 years ago
Pictures only
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

You can get it to me via customer service
http://ww2.justanswer.com/contact-us

It usually takes at least several hours for them to get to it. Have you tried posting the pics one at a time here.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
not working.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Ok, try customer service but it will take a while. You can email them directly to me but there is an additional charge for that.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
File too large, we will call the plubmer
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Ok, but for another $10 you could email them to me. I suspect that would be a lot cheaper than a plumber.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
That's ok...its takes awhile like you said.....however, a friend whose a plumber is coming.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Let me know if you need more help.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Actually the direct email has no wait.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Whats the direct e-mail
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

You can email the pics directly to me without going through customer service but there is an additional $10 fee

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My boiler short cycles about two times before going through
Hello, my boiler short cycles about two times before going through a complete heating cycle. What's causing my propblem?… read more
Rick
Rick
HVAC Supervisor
24,846 satisfied customers
RE: Dunkirk Model PVWB Continuous Pilot Troubleshooting 'no
RE: Dunkirk Model PVWB Continuous Pilot Troubleshooting 'no heat' situation. When thermostat is turned way up, it clicks, pilot light is burning, but flame does not increase. I can hear the circulator… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,978 satisfied customers
Heath Our rheem power vent water heater is in lockout mode.
Hi Heath Our rheem power vent water heater is in lockout mode. We have reset it by turning it off for 10 seconds and then holding down both arrows but the green light does not flash - them we unplugge… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
i have an armstrong ultra sx80 and the blower will come on
i have an armstrong ultra sx80 and the blower will come on and the pilot light is lit but there is no heat coming out of the vents… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Carrier Carrier Weathermaker SXA080. The thermostat
I have a Carrier Carrier Weathermaker SXA080. The thermostat calls for heat. The burner fan comes on, about 10 seconds later the pilot comes on. It used to take at least a minute, sometimes more befor… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
I have a tempstar sp 80 model # ***** At times, especially
I have a tempstar sp 80 model # ***** At times, especially when the programmable thermostat changes maintainence temps, the unit will call for heat but not fire. This seems to be able to to be "fixed"… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox Whisper Heat furnace. The pilot light is lit
I have a Lennox Whisper Heat furnace. The pilot light is lit but the burners won't ignite. The fan runs continually but the thermostat is on Auto. I have changed batteries in the thermostat.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a gas forced air heating system with a heat pump for
I have a gas forced air heating system with a heat pump for AC. Here is the scenario: I set the heat temp up 10 degrees and the heat initiates, however, in about 5 minutes with the heat not quite up 1… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Heath, this is a problem from yesterday. THE GAS SUPPLIED
Heath, this is a problem from yesterday. "THE GAS SUPPLIED TO THE BURNERS SHUT OFF PREMATURELY. IT IS NOT THE PILOT LIGHT BECAUSE I CAN SEE THE PILOT STILL LIT THROUGH THE SMALL OBSERVATION WINDOW WHE… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a 1f80-261 and have lived in this house for 1.5 years.
I have a 1f80-261 and have lived in this house for 1.5 years. Last year everything was fine, this year about a month ago the whole thermostat was blank in the middle of the night. we replaced the batt… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a gas pack heating unit and it suddenly stopped working.
I have a gas pack heating unit and it suddenly stopped working. When I turn on the system, it lights the pilot and the burners start up and the fans start to run, but after 10 - 15 seconds the burners… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
how do I relight a pilot light that appears to have gone out
how do I relight a pilot light that appears to have gone out when the electrician shut off the power in my house?… read more
Rick
Rick
HVAC Supervisor
24,846 satisfied customers
My Lennox HS20 fan is working fine but the air is cold. Where
My Lennox HS20 fan is working fine but the air is cold. Where can i look to see if my pilot light is out? Or how can I troubleshoot my problem? Its snowing so I dont think I can get a tech out here fo… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hello, We have a Burnham Revolution boiler. It will light
Hello, We have a Burnham Revolution boiler. It will light the pilot, but not the burners. If we shut off the power to the boiler, let it reset and then power it up again, it will light properly and he… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
my utica boiler has been shutting down and reset button has
my utica boiler has been shutting down and reset button has had to be used frequently . Had service, all new filters, cleaned firing nozzle, changed burner motor and checked all visible attachments. I… read more
Rick
Rick
HVAC Supervisor
24,846 satisfied customers
HAve a York RTU I fixed last week, hadnt run all winter. now
HAve a York RTU I fixed last week, hadn't run all winter. now when it runs for more than 1/2 min or so, it doesent shut off. cooked the store, and an employee had to shut the power off on unit to shut… read more
Master tech
Master tech
High School or GED
62 satisfied customers
I have a n old rheem split systen. Model #rgdd-06nc-er. The
I have a n old rheem split systen. Model #rgdd-06nc-er. The pilot lights when the thermostat is turned on , but the main burners won't start. What part is bad?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
have a 96 weil McLain CTG-5 boiler. Unit was shut down for
have a 96 weil McLain CTG-5 boiler. Unit was shut down for winter and recently restarted. Unit ran for approx 1hr, then over pressurized and purged through pressure relief valve. This happened several… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.