I have a carrier ducted air conditioning system 38QPA15-7…

Customer Question
I have a carrier ducted...
I have a carrier ducted air conditioning system 38QPA15-7
After installing a new contactor the system is now displaying error code 59 (Phase fault).
As the system is single phase this error is not correct but I understand this error is showing because the NR-1 board is not set up correctly.
Can you walk me through the steps to set the correct parameters.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 day by:
1/23/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,151
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

I am very sorry your question has not been picked up yet.

I just logged on and found you had not been assisted.

Please let me know if you still need help and I will do my best. Please do not "Rate" as we have not worked toward an answer yet.

If you would like to proceed let me know by replying.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I still need help, error 59 is still there and it is impossible to start or re-set the system while this error persists.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,794
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

If the system is over 5 years old, the odds are high that 59 is a bogus error code (about half of the error codes are not accurate on these systems, the older it is, the more likely the error code is not accurate).

However we can check it out,

First lets try switching Line 1 and Line 2 at the contactor you replaced, that is a bit of long shot but worth a try... and then check for voltage **between** line 1 and Line 2. Tell me what voltage read you get.

Depending on what you discover we can some further testing, and a heat stress test on the printed circuit card, depending on how old it is.,

We can go from there.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,794
9,794 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,794 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
IS IT POSSIBLE THAT A 5TON CARRIER AIR CONDITIONING UNIT TO
IS IT POSSIBLE THAT A 5TON CARRIER AIR CONDITIONING UNIT TO BE SINGLE PHASE … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I recently had a 10-ton emergence rooftop unit (LGH120) with
I recently had a 10-ton emergence rooftop unit (LGH120) with the variable frequency drive MSAV (belt driven). The VFD shuts down with a phase error according to the installer (and shows a frequency pr… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
I have a sinus m variable frequency drive zzo73064 ac 200
i have a sinus m variable frequency drive zzo73064 ac 200 230v 3ph need start up instructions… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a 3.5 ton Carrier 3 phase condenser with Copland scroll
I have a 3.5 ton Carrier 3 phase condenser with Copland scroll compressor. This unit blew very cold until a recent flood and lightening storm tripped the circuit breaker. (I live in Texas. We tried to… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Carrier Weather maker 8000 furnace will run 1 min.
Carrier Weather maker 8000 furnace will run 1 min. then shut off leave a burnt plastic smell. As well my thermostat shows an E2. Can you tell me if their is a sensor bad from this?… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have carrier furnace 58 mvp100-f-17120. the furnace fires
I have carrier furnace 58 mvp100-f-17120. the furnace fires up but the blower won't come on. I have my tech here and we have tested the circuit board. replace motor control module we have also brought… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
on a vlt 6000 hvac, i am getting an alarm 16 which says it
on a vlt 6000 hvac, i am getting an alarm 16 which says it is a short circuit in the output from the drive. i have checked the current on the motor manually and it is normal as per the name plate on t… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
Hello, Is it advisable to install the Carrier Model FY4ANF030
Hello, Is it advisable to install the Carrier Model FY4ANF030 horizontally, if it doesnt fit vertically? Also I have a friend who wants to install it in an attic that is not insulated. He lives in NY … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Good morning,i have a Carrier 30RAP0305KAC0000 SN.4611Q43783
Good morning,i have a Carrier 30RAP0305KAC0000 SN.4611Q43783 chiller.It will run for four or five days and works fine then we get a T196/T197 and A or P 201 and chiller shuts down. My EWT is 60.9,LWT3… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,794 satisfied customers
I have a Carrier Infinity ICS, 58mvc100 with the Inifinity
I have a Carrier Infinity ICS, 58mvc100 with the Inifinity themostat. I have experienced 55 fault 33s since installation in Nov. 2009. My observations when these occurred were the following: - Large s… read more
heatncoolrepair
heatncoolrepair
Former HVAC Service Technician
Vocational, Technical or Trade Scho
75 satisfied customers
I have a commercial roof top unit, Carrier model 48TJE006---601GA
I have a commercial roof top unit, Carrier model 48TJE006---601GA S/N 4693G01396. I am having problems with the squirrel cage motor that pushes the air into the building. When i turn the power on the … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
I have a Carrier high wall duct free split system model #38GXM
I have a Carrier high wall duct free split system model #38GXM /40GXM. the fan inside is running but not cooling it has a red light flashing 7 times and H7 is displayed as an error code… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
I have a 7 1/2 ton carrier 38AUZA08 that intermittenly trips
I have a 7 1/2 ton carrier 38AUZA08 that intermittenly trips comfort alert , the compressor has been changed once fault code flashes 6 . I have checked power at disconnect by unit all 3 legs of voltag… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,794 satisfied customers
Error code-American Strandard freedom 80single stage gas
Error flash code, 4 flashes indicates open temp limit control. What components affect this condition? American Strandard freedom 80 single stage gas fired model add100c945f3 8 yrs old.… read more
spivco
spivco
153 satisfied customers
I have a Carrier heat pump that is displaying a system malfunction.
I have a Carrier heat pump that is displaying a system malfunction. the error codes are as follows: 81-thermal lockout in low stage 4 hours 85-low contactor open. The filter was extremely dirty, but e… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
trouble with my furnace I have a Carrier gas fired model 58CVA070---1
trouble with my furnace I have a Carrier gas fired model 58CVA070---1 / using Infinity Control / keypad shows system malfunction call technician. I have already shut power off and gas and then turned … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,151 satisfied customers
we have recently installed (April 2010) a LGB72 ducted reverse
we have recently installed (April 2010) a LGB72 ducted reverse cycle air conditioning system. Has been working fine but we were away for the weekend and when we returned turning on the unit the contro… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a white rodgers 90 series model # 1F95-1271 programmable
I have a white rodgers 90 series model # XXXXX programmable thermostat. My problem is it won't let the heat pump come on. It runs on the strip heat only. If I switch to the air conditioner it still wo… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x