Customer Question
Klimaire unit fan won't blow...
Klimaire unit fan won't blow in heat , heat pump is running
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
1/19/2016
HVAC Technician: hvacexpertjoe, HVAC Technician replied 2 years ago
hvacexpertjoe
hvacexpertjoe, HVAC Technician
Category: HVAC
Satisfied Customers: 183
Experience: I have owned and operated 2 HVAC companies in KY an WV. My background is electrical engineering.
Verified

So the fan will not blow no matter what you set the fan to on the remote? Low ,medium or hi?

Ask Your Own HVAC Question
HVAC Technician: hvacexpertjoe, HVAC Technician replied 2 years ago

Also it is possible that the unit is in defrost mode. The outside unit will run but the inside unit will not. Defrost mode should only last 10 minutes though.

Ask Your Own HVAC Question
HVAC Technician: hvacexpertjoe, HVAC Technician replied 2 years ago

There is a digital display tube in outdoor PCB.

  • In standby , The LED displays “”,

  • In compressor operation, the LED display the frequency,

  • In defrosting mode, The LED displays the frequency or “dF” each other for 2

    seconds,

  • In compressor pre-heating, The LED displays “”

  • In protection or malfunction, the LED displays error code or protection code.

    7.4 Outdoor unit point check function

    There is a check switch in outdoor PCB.
    Push the switch SW1 to check the states of unit when the unit is running. The digital display tube will display the follow procedure when push SW1 each time:

Display

Remark

1

Indoor unit capacity demand code

2

Outdoor unit running mode code

Off:0, Cooling:1, Heating:2

3

Amendatory capacity demand code

4

Outdoor unit fan motor state

Off:0, Low speed:1, High speed:2

5

Evaporator outlet temp. for 1# ***** unit

Actual data

6

Evaporator outlet temp. for 2# ***** unit

Actual data

7

Evaporator outlet temp. for 3# ***** unit

Actual data

8

Evaporator outlet temp. for 4# ***** unit

Actual data

9

Condenser pipe temp.

Actual data

10

Ambient temp.

Actual data

11

Compressor discharge temp.

Actual data

12

Inverter current

Actual data

13

EXV open angle for 1# ***** unit

Actual data×8

14

EXV open angle for 2# ***** unit

Actual data×8

15

EXV open angle for 3# ***** unit

Actual data×8

16

EXV open angle for 4# ***** unit

Actual data×8

17

Outdoor unit DC Voltage

AD *472/255=Actual Voltage

18

Indoor unit number

The indoor unit can communicate with outdoor unit well.

19

The last error or protection code

00 means no malfunction

20

The Compressor’s running frequency

29

――

Check point over

Ask Your Own HVAC Question
HVAC Technician: hvacexpertjoe, HVAC Technician replied 2 years ago

I will opt out for another expert to help here.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trane XR90 is leaking water out of the bottom of the unit.
Trane XR90 is leaking water out of the bottom of the unit. I pulled off the condenser trap on the right side, cleaned and tested - works fine. There are two pvc drains going to it - one from the upper… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I need to diagnose a pressure switch lockout issue on a heatpump.
I need to diagnose a pressure switch lockout issue on a heatpump. For the last 2 seasons during summer I got the issue sporadic (3-4 times during the season). But now it is also happening during heati… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a Trane XE 1100 heat pump that is 15 years old and used
I have a Trane XE 1100 heat pump that is 15 years old and used year round. It just started tripping the breaker in the breaker box as soon as it turns on. The technician says the compressor has a dead… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I am replacing a evaporator on a refrigerator and I have a
I am replacing a evaporator on a refrigerator and I have a FB12 flame barrier. It has two sides and aluminum and fiberglass. There's a little sticker on the aluminum side saying do not use the side to… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My upstairs HVAC has the evaporator located in the attic.
My upstairs HVAC has the evaporator located in the attic. There are two drain lines running inside the wall to ground, one on the evaporator and one on the drip pan under the evaporator, the drip pan … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
61 satisfied customers
What would make evaporator fan motor stop and the unit to
what would make evaporator fan motor stop and the unit to freeze up … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I need the BTU rating for a Heatcraft Evaporator Model
I need the BTU rating for a Heatcraft Evaporator Model ADT56AWGJ … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Today, evaporator coil froze over and i heard the outside
Today, evaporator coil froze over and i heard the outside condensor area making a louder noise. i shut the ac off when noticing this and the coil melted and the fan blows air now. i looked at the evap… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,808 satisfied customers
I replaced a jazz bored today along with evaporator fan
I replaced a jazz bored today along with evaporator fan motor and I can only get the motor running if I use the ground wire to one terminal on the motor and one of the wires that has 120 V I replaced … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
What is the cost of a Goodman evaporator coil replacement?
What is the cost of a Goodman evaporator, for the part and for the part installed with the usual amount of freon (R22) in a two-section (upstairs) Trane XL 1500? The unit is leaking badly and the tech… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Why is my suction line freezing up?
Why is my suction line freezing up?… read more
R G
R G
44 satisfied customers
my cooling fins need to be replaced......is this possible
my cooling fins need to be replaced......is this possible???… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Is it possible to charge a heat pump system while in heat
Is it possible to charge a heat pump system while in heat mode?… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I want to install a new 3 ton 16 seer AC condenser. The lineset
I want to install a new 3 ton 16 seer AC condenser. The lineset install already is 3/8" OD liquid and 7/8" OD suction. The run is 90 feet from the unit and there needs to be 6 90 degree elbows to make… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello Phil i have an ice machine . It leaks water at the bottom
Hello Phil i have an ice machine . It leaks water at the bottom From center to back . Can you help me?… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x