I have a Scotsman Prodigy. The ice is getting hung up in the…

Customer Question
I have a Scotsman Prodigy...
I have a Scotsman Prodigy. The ice is getting hung up in the harvest mode and it seems to me that the left side of the ice grid is not melting enough to brake free and fall. We had a tech out and he replaced the ice thickness sensor and the harvest assist solonoid. When that didn't work he said that we would have to replace the entire "grid" as he called it referring to the evaporator for around $2500. I have spent a great deal of time watching it and resetting it to see where it gets stalled.
It seems to me that the left side of the evaporator is not melting enough as the hot gas runs through the serpantine and holds up the entire sheet of ice cube. Is it possible to do it my self and replace the hot gas solonoid? Just guessing at this point hoping not to spend $2500.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 hours by:
1/19/2016
HVAC Technician: shaithus1,
 replied 2 years ago
shaithus1
Category: HVAC
Satisfied Customers: 94
Verified

Hi.. let me see if I can help...

It sounds like the grid itself may have a blockage...

When the hot gas solenoid opens, it sends hot gas through the grid to melt the ice and harvest.

When the technic***** *****ged out the solenoid valve, did he change the whole valve or just the coil?

Did he place it under a vacuum? Did he purge the system?

His guages should have indicated that there was a blockage when harvest started because pressures would have increased from no gas flow...

It pretty obvious if you can see the ice sheet move up to a certain point.... but... let me be clear... if the blockage is there, you would see a freeze line on the grid. If hot gas wont flow neither should the cold, unless the blockage is partial and metering is occuring.

Unless you are a trained and licensed refrigeration tech, you should no attempt to repair the refrigeration portion of the machine.

Is the company you used an authorized agent of Scotsman? I know our techs are and Scotsman provides us training and technical support on their equipment.

The evaporators can be very expensive to change out and depending on the age of the ice machine, replacement may be the better option.

The ice thickness sensor would not effect only part of the grid.... the ice thickness sensor tells the machine to harvest at a set thickness.... the fact that the ice is not coming away from the grid evenly, indicates an issue in the grid...not the sensor.

Ask Your Own HVAC Question
HVAC Technician: shaithus1,
 replied 2 years ago

Can you give me a model number so I can pull up a schematic and verify any other potential issues.

Phillip

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Please review my earlier comment. The technician did not replace the solenoid or valve (hot gas). It is my conclusion after watching, that the cubes are not melting enough to free themselves in the harvest cycle. Can I send u pictures?
Customer reply replied 2 years ago
Co 330MA -1A
HVAC Technician: shaithus1,
 replied 2 years ago

. I'm sorry... he did replace the harvest assist solenoid...

I wont get any pictures...

Ok.. per the manual....

When the harvest cycle begins, the controller shuts off the fan motor, switches on the hot gas valve, and through a parallel circuit, the harvest assist solenoid. After a few seconds the purge valve opens and water is drained from the reservoir. Based on either the automatic purge or manual purge setting, the pump and purge valve will be switched off at a time determined to have drained enough water for that setting. The inlet water valve will open to fill the reservoir anytime the mid length probe is uncovered, which occurs during the reservoir drain cycle. Harvest continues as the hot discharge gas flows into the evaporator serpentine, heating up the evaporator. At the same time the harvest assist solenoid is pushing against the back of the ice slab. When the ice releases from the evaporator, it harvests as a unit, and the harvest assist probe provides some additional force to push it off. When the ice falls off it will force the curtain(s) open. An open curtain during the harvest cycle signals the controller that the evaporator has released its ice. If this is a single evaporator machine the controller will terminate harvest. If it is a two evaporator machine, the controller will continue harvest until both curtains have opened. If one curtain remains open, the controller will shut the machine down on bin full. Anytime harvest is complete the hot gas valve and harvest assist are shut off. The harvest assist pin returns to its normal position by spring pressure.
If the curtain(s) re-close after harvest, the freeze cycle will restart.

So... if he changed the harvest assist the problem may be in the hot gas valve itself.... you might be seeing only the harvest assist working...

You will need an EPA licensed technician to come back out and check the operation of the hot gas valve...

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Im working on a Crystal tips ice maker and could use a
Im working on a Crystal tips ice maker and could use a service manual for a system overview. Can you help? … read more
Ricky Main
Ricky Main
8 satisfied customers
I have a manitow Qd0323w ice maker that the harvest light
I have a manitow Qd0323w ice maker that the harvest light blink randomly when on ice mode, went it harvest ,the light went solid , it tried to harvest( hot gas mode) but no ice fall off. I can feel so… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a model C0330SA-1A Prodigy ice maker and it will make
Hello, I have a model C0330SA-1A Prodigy ice maker and it will make ice for several hours say 6 to 8 hours and then defaults to a flashing 2 which is max harvest retry. I can shut the unit down let it… read more
shaithus1
shaithus1
94 satisfied customers
i turned my Scotsmann DCE33A ice machine off to clean. When
i turned my Scotsmann DCE33A ice machine off to clean. When i turned it back on the water run but does not freeze.… read more
shaithus1
shaithus1
94 satisfied customers
got a c1448 scottsmanice machine worked fine the weekd
got a c1448 scottsmanice machine worked fine the weekd gave a code 2 said longharvest cleaned it all the sensors it still doest drop ice water runs on the cube coil get cold but doesnt make ice all sy… read more
shaithus1
shaithus1
94 satisfied customers
Rheem Seer 10 Heat Pump Model RCBA - 3670AS17. I have replaced,
Rheem Seer 10 Heat Pump Model RCBA - 3670AS17. I have replaced, Defrost Control Board. Contactor and Furnace Transformer. (I blew that when failing to shut off the Furnace Breaker prior to replacing t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an AC46 scotsman icemachine. is it possible that the
I have an AC46 scotsman icemachine. is it possible that the 1. electronic thermostat 2. defrost timer 3. evaporation coil can all break at once to cause malfunction.? .… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
My Manitowoc Ice Machine says the exhaust fell below 85 degrees
My Manitowoc Ice Machine says the exhaust fell below 85 degrees for three cycles. What do I need to do?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Hello Phil. I have a Scotsman Ice machine Model: CME500AE-1A.
Hello Phil. I have a Scotsman Ice machine Model: CME500AE-1A It doesnt produce enough ice. Only half of normal." I through gages on high and low. I have 40 PSI on the low side. I have 250 PSI On the H… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
q130 manitowoc ice maker---it will harvest 3 batches and then
q130 manitowoc ice maker---it will harvest 3 batches and then stop--if i turn it off then back on it will make 3 more batches and then stop again--help… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
Model EC300FAB A third of the ice on the left side of the
Model EC300FAB A third of the ice on the left side of the evap doesn't not fall durning harvest but some of that third then falls when the water comes over it when machine goes back into freeze mode.… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have a Scotsman CO322 ice machine (CO322MA-1A) that will
I have a Scotsman CO322 ice machine (CO322MA-1A) that will make 5 - 10 harvests then quit with a error code 1 or 2 indicating a max freeze or max harvest time. The failure is not consistant. I have ch… read more
shaithus1
shaithus1
94 satisfied customers
My Scotsman DCE33 icemaker is not filling the bin with ice.
My Scotsman DCE33 icemaker is not filling the bin with ice. It is making 8 perfect ice cubes every 20 to 30 minutes, but it melts in the bin as fast as it is made. I regularly run cleaner through the … read more
shaithus1
shaithus1
94 satisfied customers
I have scotsman ice machine CME5061 Sometimes the contol
I have scotsman ice machine CME506 1 Sometimes the contol panel saw me by bliking led the bin is foul but the bin is empty 2 After start working again Drop some ice ant stop by bliking the red led on … read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
just purchased a scotsman ice machine and it has sat up for
just purchased a scotsman ice machine and it has sat up for 2 years now when i run it it makes some ice thn freezes up and makes 4 huge peaces of ice. what can i do. also it runs the cycle for harvest… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have a CME506 and it will come on for a second and then go
I have a scotsman ice machine CME506 and it will come on for a second and then go off. The freeze light blinks but i cannot get any of the other buttons to work. I cannot reset the machine.… read more
hopetohelp
hopetohelp
manager/HVAC contractor
Associate Degree
2 satisfied customers
I am working on a QD1472C and I believe the cool vapor defrost
I am working on a QD1472C and I believe the cool vapor defrost valve is leaking. The liquid line is hot and the water gets hot instead of freezing. The pressures were 225PSI and 30 PSI. Am I correct i… read more
hopetohelp
hopetohelp
manager/HVAC contractor
Associate Degree
2 satisfied customers
we have two 5 ton split ac units in stalled and one of them
we have two 5 ton split ac units in stalled and one of them is icing up. we replaced the TX valve and it seems to have made it worse. The charge is correct, what should I look for to solve this proble… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x