HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

I replaced flame sensor and board on g40uh-48b-090-03

Customer Question
furnace and its still short...
I replaced flame sensor and board on g40uh-48b-090-03 furnace and its still short cycling... What else could it be. I've never seen that before after replacing the flame sensor
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 58 minutes by:
1/18/2016
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to help answer your question(s). Please provide all the information I ask for since I'm not onsite. At the end of our dialog you will be asked to rate my service, but please wait until then and all your question(s) have been answered satisfactorily. If you are not satisfied, I'd appreciate it if you'd tell me why before leaving a negative rating and allow me to continue to work with you until we are able to both agree on an outcome to follow. Thanks for your business!

What do you mean by "short cycling"? Is just the burner shutting off, or is entire furnace turning off? Are you getting any LED flash code when it shuts down?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Lennox furnace. M/N G40UH-48B-090-03. Left LED is
I have a Lennox furnace. M/N G40UH-48B-090-03. Left LED is slow flash. Right LED is just on. Diagnostic says Primary/Secondary limit switch open. Blower works but flame is not lighting off. When trying to reset, Both LED's blink quickly for a second then stop after hearing a clicking sound coming from control board..... … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I was asked to look at a Lennox g40uh-36b-090. The call for
I was asked to look at a Lennox g40uh-36b-090. The call for heat starts the inducer, igniter glows, gas valve opens, fires for almost 15 seconds, blower doesn't come on, gas valve shuts off, blower co… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Rheem fun ace new flame sensor won't stay lit 5 to 10 sec.
Rheem fun ace new flame sensor won't stay lit 5 to 10 sec … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I was changing the primary limit switch on my lennox
I was changing the pri***** *****mit switch on my lennox g40uh-48b-090-03 unit. Forgot to turn power off. When unscrewing old limit switch from unit got a spark when srewdriver touched screw head. uni… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Lennox G40uH-48B-090-05 furnace that is give me
Hi, I have a Lennox G40uH-48B-090-05 furnace that is give me some problems. I'm get a code that say that limit switch is open. Leds read left flash's while the right stays on. It says that it could be… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a split system with 2 zone dampers a Lenox Merit Series
I have a split system with 2 zone dampers a Lenox Merit Series G40UH-48B-090-07 the Blower is on in auto but the condensing unit contactor won't pull in. There is no low voltage at the coil (24v) and … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
LENNOX G40UH-48B-090-15 UNIT. BLOWER MOTOR REPLACED JULY 14.
LENNOX G40UH-48B-090-15 UNIT. BLOWER MOTOR REPLACED JULY 14. WHEN HEAT WAS NEEDED WOULDN'T WORK. FOUND THAT THE TECH DID NOT INSTALL SENSOR WIRES FOR HEAT. I PRINTED OUT THE MANUAL WHEN TRYING TO GET … read more
Tim H.
Tim H.
HVAC Professional
3,972 satisfied customers
I have a Lennox G40UH-48B-090-11, 8 years old glow plug ignites
I have a Lennox G40UH-48B-090-11, 8 years old glow plug ignites flame flame stays on for 10-60 seconds. furnace turns off. I suspect the flame thermostat is sending a signal to the controller board to… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
House fan comes on, heater does not light. Code reads red
House fan comes on, heater does not light. Code reads red blinks, green steady. I checked both limit switches. Both closed so ok. Evac fan does not come on unless I disconnect limit switches. No ignit… read more
Expert
Expert
ON MY G40UH-48B-090-3 UNIT I HAD A BAD DRAFT INDUCER FAN. WHILE
ON MY G40UH-48B-090-3 UNIT I HAD A BAD DRAFT INDUCER FAN. WHILE I WAS MESSING WITH IT I CONNECTED AND DISCONNECTED IT A FEW TIMES WHILE IT WAS RUNNING. THE UNIT STARTED FLASHING A CODE FIRST LIGHT ON … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a lennox g-16 hot air furnace, for our house 1140 sq
i have a lennox g-16 hot air furnace, for our house 1140 sq ft, basement is very cold, the g-16 is 22 yrs old. i got a new lennox g40uh-48b-090-11, and want to keep a hot air vent partly open to heat … read more
hvac-technician
hvac-technician
Service Manager
Vocational, Technical or Trade Scho
62 satisfied customers
I have a Ruud Deluxe Drum 90 PlusHSI, model UGED-09ERAJS that
I have a Ruud Deluxe Drum 90 PlusHSI, model UGED-09ERAJS that burns natural gas. The flame won't stay lit. The blower turns on, then the igniter glows. the gas valve turns on (clicks) and allows gas i… read more
Tim H.
Tim H.
HVAC Professional
3,972 satisfied customers
Hi The blower will not start in auto or manual. Neither LED
Hi The blower will not start in auto or manual. Neither LED on the circuit board is lit. The breaker to unit is on. What should I look at? Thank for the help Chuck… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Lenox Merit series M/N G40UH-36B-090-03 that wont
I have a Lenox Merit series M/N G40UH-36B-090-03 that won't fire. I was replacing the filter, removed the covers to inspect inside for dirt/dust replaced covers, and now an hour later I noticed that t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i hava G40UH(X) series model 36B-090-03 , the furnance ignites
i hava G40UH(X) series model 36B-090-03 , the furnance ignites for a few seconds , then goes out...this repeats a few times then the blower and furnace shut down. after i turn the power on and off the… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox HVAC unit which has been breaking down lately. Model
I have a Lennox HVAC unit which has been breaking down lately. Model is g40uh-48b-090-14 what is approx cost of the induction motor and pressure valve for this? I want to double check what mark up I a… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Lennox gas furnace G40UH-48B-090-10 that is stuck
I have a Lennox gas furnace G40UH-48B-090-10 that is stuck in the watch guard mode. The furnace lights but the the flame goes out I would say it stays lite for about 4 to 5 seconds then it starts in s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a Lennox G40UH(X)-24A-045-11 Furnance that will not stay
Have a Lennox G40UH(X)-24A-045-11 Furnance that will not stay lit. I replaced the ignighter and I first cleaned the flame sensor and then replaced it because it still did not work. The ignighter heats… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.