Loud banking noise-temp of up down- is there away to bleed

Customer Question
the lines?...
loud banking noise-temp of up down- is there away to bleed the lines?
Submitted: 2 years ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 2 minutes by:
1/9/2016
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,064
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Here are instructions to purge a typical system with copper baseboard.

A purge station is typically a shut off with a hose fitting above it. There can be 1 piece purge stations where both the shut off and hose fitting are combined in one piece. Or it can be a separate valve(shutoff) with a hose type "faucet" (we call it a boiler drain) above it. They are usually at the boiler on the pipe above the circulator pump. You need to determine which one goes to your problem area. I have seen purge stations in old systems some distance from the boiler on the heating line (pipe). Be sure to turn the power off to the boiler while you are purging and it’s best to let the boiler cool down to around 100 degrees (if it’s currently hot) before purging. Dumping a lot of cold water into a hot boiler is not beneficial.

You need to shut the valve, attach a hose to the hose fitting then open the hose "faucet". Some all-in-one fittings close the valve and open the hose at the same time so be sure your hose is attached first if you have one of these fittings. If you have zone valves with multiple purge stations all the zone valves should be opened manually. The common theme here is that you want to push the water through the loop and have it come out the drain. If you don’t stop the flow below the drain no air will be purged. You don’t want the water to go directly from the boiler and out the drain/hose. Closing the shut off next to the drain forces the water through the piping loop/zone. If you have zone valves and only 1 purge station then you need to open the zone valves one at a time and fully purge a zone before opening the next valve and closing the valve you just purged. You also need to jack up the pressure while you are doing this but you need to keep the pressure under 30 psi.

This is done by increasing the pressure at the feed (pressure reducing) valve.

Some types have a lever that you flip up from a "horizontal" position to straight up. This is the easiest type to use. Some require that you tighten the screw at the top of the valve. Some have a lever that moves from side to side. You should be warned that if this valve hasn't been touched in a while disturbing it in this manner can cause it to fail in which case it will need to be replaced. A feeder failure would mean that the feeder lets too much or too little water pressure into the boiler. This device is located on the water supply line to the boiler.

You need to let the water run until you hear no more bubbles coming out of the hose for several minutes. You then shut the hose off at the same time you return the feed valve back to it's original position. Then open the shutoff. Be sure the pressure on the boiler is between 10 & 15 psi when you are done and before you turn the power back on. The boiler you have has no bearing on this process. It is the same what ever type you have. Having said all that this is not something I would recommend that you try yourself unless you feel confident about doing it. You may have to call a plumber anyway if the feed valve fails.

Ask Your Own HVAC Question
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,064
23,064 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My boiler in on but is not working. The lights on the screen
my boiler in on but is not working. The lights on the screen is on but not heat. … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
BOILER WON'T START, JUST REPLACED CONTROL PANEL WITH THE
BOILER WON'T START, JUST REPLACED CONTROL PANEL WITH THE SAME RESULT. ALL I GET IS A GREEN LIGHT WITH NO MOTOR OPERATION … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
I have a triangle tube Challenger combination Boiler and
I have a triangle tube Challenger combination Boiler and water heater . It is locked out with a code of 15 P . … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
385 satisfied customers
Peerless Boiler Series MI85 Gas Boiler installed 2015. We
Peerless Boiler Series MI85 Gas Boiler installed 2015. We have 3-zone water heat. Furnace works perfectly until outside temp goes into single digits and below. Furnace goes on and off repeatedly tryin… read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
We have a Burnham boiler for our in floor heat.. and it will
Hello, We have a Burnham boiler for our in floor heat.. and it will not heat the floor up past 70 degrees.. we have cleaned it replaced the pump and can't figure out why it won't stay warm … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
I have a Keston Boiler and nothing is displayed on screen
Hi I have a Keston Boiler and nothing is displayed on screen and won't switch on … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a question regarding the boiler temperature setting,
I have a question regarding the boiler temperature setting, water pressure and room thermostat. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Emerald boiler doesn't seem to be working. System isn't that
Emerald boiler doesn't seem to be working. System isn't that old. Says Standby WTR 155F … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a utic a gas boiler that was running ok but not
I have a utic a gas boiler that was running ok but not heating all my wall heaters so I shut it off and tried to restart it but cannot get the pilot to light.… read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
How to insure my burnham boiler?? Five years. No no
how to insure my burnham boiler?? JA: I'll do all I can to help. How long have you been dealing with this? Customer: five years JA: Do you plan on doing the work yourself? Customer: no no experience J… read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
We have a boiler that is only heating the downstairs pipes
Hi there we have a boiler that is only heating the downstairs pipes and no heat upstairs. We have 2 thermostats and we have forced hot water which is working fine. Just no heat upstairs … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
My boiler is not firing. Has power. Circulating pump is
My boiler is not firing. Has power. Circulating pump is working but seems no power to burner controls … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
My boiler seems to be working fine, but my house is not
my boiler seems to be working fine, but my house is not getting to the temperature I have it set for. have it set at 70 or above, but temp only gets to about 65 … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
Steam is escaping from the back of the boiler into the
steam is escaping from the back of the boiler into the chimney, is the boiler bad or the flue? … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
Brought a boiler from nome heating. Bought a boiler from
bought a boiler from mike west nome heating for eght thousand dollars need to insurance for my boiler … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x