I have a goodman 14 seer condensing unit new just instslled.

Customer Question
There us no low side...
I have a goodman 14 seer condensing unit new just instslled. There us no low side pressure. And yes both valves at the conpressor are open. Is this a condensing unit defect?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
1/9/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,894
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

hello,

is suction line temp hot warm cool cold?

And what is head pressure during this?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No low side pressureModel Number: Gsx140601ka
What have you tried so far?: Ran unit 30 minLines are room temp hi side is about 180psi
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago
Kcrand36
Kcrand36, HVAC Mechanic
Category: HVAC
Satisfied Customers: 80
Experience: Owner at Advantage Repair
Verified

Good Afternoon, I am Kevin, one of the Tech's here on JA.

is it fixed orifice or TXV?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Txv on the evap coil
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

line set or hard piped? and has the problem been here since day 1 startup? Are you the start up tech? or homeowner?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Harg pipe. Yes since day one which was yesterday about 5pm. Also no freon comes out if low side schrader valve when depressed
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

system off or on at this time?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No low side pressure or freon from schrader valve with system on or off
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

but you have high side pressure still?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have hi side pressure and yes the valve at the unit us open
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

so this is a new system, new evap coil with txv, new condensing unit, hard piped....

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Istalked yestetday. We installed 2, the other is operating fine
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

ok, did you pressure test with nitrogen or helium?

Ask Your Own HVAC Question
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

where did you introduce the gas? in the high or low side of the system?

Ask Your Own HVAC Question
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

the pressure test gas, I'm talking about......

Ask Your Own HVAC Question
Customer reply replied 2 years ago
At the schrader valves on the condensing unit
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

yes, but which side? high or low?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Can't remember. Probably the low side
Customer reply replied 2 years ago
It is a sigle pase unit and it sounds kind of like the compressor is running backwards
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

ok, so you cannot determine at this point if you had a good install or not, because if you had placed it in the high side, and it bled through to the low side you would know that you didn't braze a plug in the pipe causing a restriction.

You definitely have a restriction, if you have high side pressure and no low side pressure, you have a restriction. The problem is , where is the restriction. I once remembered and never forgot, when I was an apprentice I did a "hard pipe", forgot to remove the plug in the end of the pipe. Brazed the SOB in and later figured out I had an issue. Like you, I opened up the ports though, let loose the charge. later figured out where my plug was because heating it, broke down the rubber plug enough to create a restriction just enough to frost the line, yes, I did have to cut insulation and reseal, but I knew where my joints were. Getting back to your problem.

attach a temp probe to inlet and outlet of TXV, get your delta T, After that, start looking at the piping and what you may have forgot to do during install.

Ask Your Own HVAC Question
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

we all make mistakes..... just making them right and not making the customer pay for them is the difference between good and bad.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The supplyer has replaced the unit. The caps were removed. Before installing new unit i will check to make sure i have air flow through the coil via refrigerant lines.. what do you think? I have installed over 100 of this same system
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I don't understand how it could be the Condensing unit. You have a TXV, you have high side pressure, you have nothing bleeding to the low side of the system. Unless you have a defective king valve, which you have already determined that the high side opened, because you have high side pressure and you have a vacuum on the suction, how could it be anything else but a restriction?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The blickage has to be inside the condensing unit. After i disconnected, i opened the low valve , notjing csme out. Then the high side valve and there is still plenty if freon inside the unit
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

exactly, you have high side pressure to your restriction. whether it be on the liquid line, txv or suction line, your restriction is in the system, NOT in the condensing unit!

Ask Your Own HVAC Question
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

remember your "BASIC REFRIGERATION CYCLE". Factor in the AC condensing unit.......... you have high side pressure at the king valve on the condensing unit. You have a vacuum on the low side king valve. If the system is off, the high side pressure should bleed through the TXV to the low side, regardless if you have bad compressor or not. This is NOT happening according to what your telling me. so you MUST have a restriction after it leaves the condensing unit and prior to it reaching the king valve of the suction line of the condensing unit.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
If i draw a vaccum on the low dide at the condenser will thst bleed over and draw a vaccum on the hi dide?
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

It may, it may not.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Whay about draeing from the high side?
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

what kind of situation are you in?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The same one
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I would start by recovering the refrigerant, at this point, you have probably introduced air and you don't want to give the customer a "non condensable system".

pressurize with nitrogen through the high side only.. if it bleeds to the low side, pretty rapidly, ok, if not, you have a restriction. Start thinking where you could have messed up.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
If the king valve were stuck would i have the same simptoms?
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

think, if the king valve was closed, you would not be reading the suction of the compressor. You stated you were in a vacuum, therefore, you are getting the suction of the compressor. you are NOT getting pressure back to the compressor, wether it be on the liquid line feeding the txv, or after the outlet of the evap coil. This is all part of pressure test and start up. You should have known this the second you pressure tested BEFORE you unloaded the charge into the system.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Condenser contractor chattering is it bad? Just notice
We had very cold weather down to 10 degrees, fan not been running until today thouzght was running's. On heat strips. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rental hot water tank - serviced and insulated pipes Oct
rental hot water tank - serviced and insulated pipes Oct 2017 by Reliance tech-ice build up at elbows on insulated outside plastic pipe - when fan comes on -can hear running water outside from inside … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,417 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,894 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x