Customer: I have a Carrier 58RAV down flow/horizontal furnace. The limit switch keeps tripping after every heat cycle (heat comes on, reaches temperature, then turns off and doesn't come on again at next call for heat). Looking at the diagram in the manual, it looks like it's the "draft safeguard tube and switch" that keeps turning off rather than the manual reset limit switches, and pushing it back in again resolves the issue. I follow the manual furnace shut down/start up procedure each time. It's a pain in the butt, as it's cold here and it's taking a lot of time just to keep my family warm!At the same time, our thermostat (the only one in our home) is malfunctioning. I've replaced the batteries, so I feel I can eliminate that variable. It seems to have a mind of it's own; I set the temperature to 70 for example, I *think* it reaches it, then I go to check the thermostat for verification and it shows 65, while the house temperature is registering at 61. I reduce the temperature to below 61 to bring back higher to initiate the call for heat sequence, only to have it start up and get error code 13 on the furnace. I'd like to know if the thermostat malfunctioning is the reason the furnace keeps turning off with error code 13, or is the furnace the reason the thermostat isn't working properly? Also, could it be as simple as me not replacing the furnace door properly and it's getting a draft of air from where it's not secure? The access door doesn't seat properly in the bottom left corner. I tried using electrical tape to hold it in place and it didn't resolve the issue.I hope everything I've said makes sense! Please let me know if there are any points of clarification. Long story short: I'm getting error code 13 on the furnace after one cycle of heat. Thermostat is all over the place. Please let me know what I should be looking for/doing to fix it!
JA: Thanks. Can you give me any more details about your issue?
Customer: I have a Carrier 58RAV down flow/horizontal furnace. The limit switch keeps tripping after every heat cycle (heat comes on, reaches temperature, then turns off and doesn't come on again at next call for heat). Looking at the diagram in the manual, it looks like it's the "draft safeguard tube and switch" that keeps turning off rather than the manual reset limit switches, and pushing it back in again resolves the issue. I follow the manual furnace shut down/start up procedure each time. It's a pain in the butt, as it's cold here and it's taking a lot of time just to keep my family warm!At the same time, our thermostat (the only one in our home) is malfunctioning. I've replaced the batteries, so I feel I can eliminate that variable. It seems to have a mind of it's own; I set the temperature to 70 for example, I *think* it reaches it, then I go to check the thermostat for verification and it shows 65, while the house temperature is registering at 61. I reduce the temperature to below 61 to bring back higher to initiate the call for heat sequence, only to have it start up and get error code 13 on the furnace. I'd like to know if the thermostat malfunctioning is the reason the furnace keeps turning off with error code 13, or is the furnace the reason the thermostat isn't working properly? Also, could it be as simple as me not replacing the furnace door properly and it's getting a draft of air from where it's not secure? The access door doesn't seat properly in the bottom left corner. I tried using electrical tape to hold it in place and it didn't resolve the issue.I hope everything I've said makes sense! Please let me know if there are any points of clarification. Long story short: I'm getting error code 13 on the furnace after one cycle of heat. Thermostat is all over the place. Please let me know what I should be looking for/doing to fix it!
JA: OK got it. Last thing — JustAnswer charges a fee (generally around $18) to post your type of question to HVAC Experts (you only pay if satisfied). There are a couple customers ahead of you. Are you willing to wait a bit?
Customer: how long is a bit?
JA: OK. Now I'm going to take you to a page to place a secure deposit with JustAnswer. Don't worry, this chat is saved. After that, we will finish helping you.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 15 minutes by:
12/29/2015
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,882
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

hello,

are you sure it is the draft safety button you keep resetting?

Billy

Ask Your Own HVAC Question
Customer reply replied 2 years ago
do you have access to the manual for this make/model of furnace? in the diagram, it shows #9 draft safeguard tube and switch....that's what i've been pushing to reset it each time
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

Thank you,

yes I have all the documentation. Have you removed the vent pipe to look for blockage, animal nest etc?....

Ask Your Own HVAC Question
Customer reply replied 2 years ago
not yet....i banged on it with a screwdriver and some sandy material fell out from where the straight ducting met the elbow
Customer reply replied 2 years ago
is that where i should start first?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

When this switch trips...it is always a blockage in chimney or vent. It will keep tripping until the blockage is gone. The thermostat is erratic because everytime this trips, the furnace cuts power to the thermostat

Ask Your Own HVAC Question
Customer reply replied 2 years ago
any tips for anything that'll help loosen the screws holding the ducting together? my drill ain't cutting it...
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

it is usually 1/4" sheet metal screws. 1/4" socket or 1/4" bit in a drillworks well

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok. what about wd-40...is that safe given the heat exposure? (heat's off until this is fixed though)
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

wd wont help much in this case. Plus once project is done you would likely get some odor and smoke..

When all else fails just a basic 1/4" nut driver works.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok, i got screws out of the elbow part, top and bottom. can't quite maneuver it out. the part above it is where the ducting from the water heater meets the ducting from the furnace in a "y" and i'm afraid to mess with what isn't broken in regards ***** ***** water heater ducting.
Customer reply replied 2 years ago
should i just mess with the elbow some more until i can get it out on it's own?
Customer reply replied 2 years ago
should i try to send you a pic of what i'm talking about?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

There are a couple ways.

You can try the elbow or drop a chain down chimney.

Remove directly at chimney.

The end result is there is something in the vent pipe or chimney

Ask Your Own HVAC Question
Customer reply replied 2 years ago
can't drop a chain down the chimney til tomorrow....too dark out to get on the roof. want to resolve this tonight if possible since it's so cold. would like to fix it at elbow if possible
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

you can also remove the water heater all in one piece. Instead of taking it apart...you can lift off

water heater and leave a few pieces together

Ask Your Own HVAC Question
Customer reply replied 2 years ago
was able to get the elbow off and used a broom handle to poke up as far as i could go....didn't feel any obstructions and there wasn't as much sandy stuff as i thought there would be...there was some but not much
Customer reply replied 2 years ago
also just looked up through the whole ducting to the chimney with a flashlight and didn't see any kind of obstructions
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

what about back into the furnace

Ask Your Own HVAC Question
Customer reply replied 2 years ago
awaiting your response before putting ducting back together
Customer reply replied 2 years ago
nope, nothing down there either...poked and looked with flashlight.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

start briefly with pipe off just to see if fan throws anything out

Ask Your Own HVAC Question
Customer reply replied 2 years ago
is that safe? should i just follow the basic furnace start up procedure?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

we are not starting burner...we just want the exhaust fan to run a few seconds with pipe off and then turn off

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i should turn on the gas control knob, turn the gas back on, then turn on the furnace breaker in that order?
Customer reply replied 2 years ago
then off in that reverse order?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

leave gas knob off

leave gas valve off

just turn on breaker

then thermostat

as soon as the fan attached to the vent pipe runs a couple seconds...turn off.

Then put pipe back together

then gas knob on

gas valve on

breaker on

thermostat to heat

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok, fyi the air coming out of the open ducting didn't feel very forceful...should it?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

that depends on blower speed and if filter is clean...

Is the unit running a cycle right now?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
nope, i just had the breaker on and turned the thermostat to fan rather than auto so that the heat wouldn't come on
Customer reply replied 2 years ago
just put ducting back together
Customer reply replied 2 years ago
i checked the filters yesterday and they are super clean
Customer reply replied 2 years ago
going to try to heat now
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

thank you

Ask Your Own HVAC Question
Customer reply replied 2 years ago
turned on heat to 70, says it's 60 in the house now
Customer reply replied 2 years ago
i'll keep you posted as to what happens
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

just respond as you can

Billy

Ask Your Own HVAC Question
Customer reply replied 2 years ago
it just reached 70, and though the house temp reads 70 while it shows 63 on the right where there should be a 70 as well (the left side number shows the house temp., the right side number shows the temp. i'd like the temp to be). i checked to see if there would be an error code blinking on the furnace as there usually is when this happens, but the light is staying steady.
Customer reply replied 2 years ago
i'm hoping that it's been resolved, as there not being a 13 error code gives me hope. i'll keep ya posted.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

so what is the update today on the furnace?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
well, it seemed to be working fine all night with multiple heat cycles. this morning when we got up the heat setting was at 67, as i had set it before bed, and the house temp. read 63. i reduced the heat setting to below 63 to initiate the call for heat cycle and went to the furnace to see what happened. the furnace started but got error code 13 again but rather than stay blinking at 13 it went back to a steady red light. this is different than before i cleaned the ducting...it would just blink a steady 13 continuously then.
Customer reply replied 2 years ago
i pushed in the draft safeguard switch again and turned the thermostat up and the heat came on, which it is now...
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

ok if it recovered on its own...without pressing a button...it is an over heat temp inside furnace and not the vent trip.

From the blower motor are wires that attach to the circuit board...can you tell me which wire of those is attached to a terminal labeled HEAT

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

ok bottom right hand corner.

you will see a block of 4 wires...black yellow blue and red.

The black is on top of a blue....just switch the black and blue...

Thaat way the blue is on top and black on bottom

Ask Your Own HVAC Question
Customer reply replied 2 years ago
all done. what did that do?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

that raised the blower speed. This should run more air through furnace and lower the temp.

Now you can try for a day or 2 and see if the limit trip (13) stops

Ask Your Own HVAC Question
Customer reply replied 2 years ago
great! so it's safe to start up again now?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

correct...all set

Ask Your Own HVAC Question
Customer reply replied 2 years ago
just now getting to turn on the heat, and it just went straight to error code 13
Customer reply replied 2 years ago
the heat didn't come on at all
Customer reply replied 2 years ago
my bad, didn't turn the gas back on
Customer reply replied 2 years ago
ok, update: turned the heat back on, came on for a bit, then shut off with error code 13 after about 5 minutes and well before reaching set temperature. the fan is still running in the furnace, but the blower has shut off. what next?
Customer reply replied 2 years ago
the fan just shut off. error code 13 blinking continuously now. one long, three short
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

ok the code is not 13....it is 31.....verify by counting the short blinks first and then long

31 is an entirely different situation

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i apologize, there was nothing in the manual that explained how to read the error codes. my bad....what's the course of action now? should i switch back the black and blue wires on the circuit board?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

no problem...now we need to key in on the exhaust fan....

is it running consistently? Does this motor ever not start or stop during a cycle? Is 31 ever present when exhaust is NOT running?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the exhaust fan is what pumps the heat into the house? it only comes on during the heat cycle; not running consistently.
Customer reply replied 2 years ago
i mean constantly, not consistently. if i turn on the fan rather than auto switch on the thermostat, then it runs constantly
Customer reply replied 2 years ago
is the exhaust fan what's called the blower motor in the manual?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

the exhaust fan is what blows air out of the vent pipe/chimney

Ask Your Own HVAC Question
Customer reply replied 2 years ago
how would i test that?
Customer reply replied 2 years ago
should i switch the wires back on the circuit board before troubleshooting anything else?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

switch the black and blue back where they were.

You would need to remove the exhaust motor to see if all the fins are in place and no feathers in blower wheel. Can you take the exhaust fan off the front wall?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i can reach around the side where the circuit board is and feel the inside of the blower, but can't see inside of it
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

I will need pic from bottom section

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

the black plastic wheel is attached to the back of the exhaust fan

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok, so what should i do with it?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

the round metal plate will come off ...there are only 4-5 screws and that whole motor and wheel pull straight out...we need to see inside that

Ask Your Own HVAC Question
Customer reply replied 2 years ago
that round plate is all i need to take off, not the black wheel and all the housing in front of it?
Customer reply replied 2 years ago
will it be easy enough for me to put back after checking it without messing it up?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

all of that comes out in one piece. Once you remove the few screws that mount the assembly the whole thing slides out.

As far as installation it just slides back in place....all depends on your comfort level.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
from sewing machine repair i know that some motors have "timing" that's really hard to dial back in without being a professional....does this have that?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

no this is simply a free rotating fan with no sequence to match

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago
Ask Your Own HVAC Question
Customer reply replied 2 years ago
i checked it out and there seem to be 3 screws holding it in. i feel i've reached the point of what i can do on my own, as the video link you sent is WAAAAAAY over my head. is there any other possible way to troubleshoot this issue from my limited experience without tinkering in the exhaust fan?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

how do you feel about just removing those 3 screws and sliding it out....looking...and sliding back in with 3 same screws?,,,,nothing else?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i'm not sure i have the proper tools, as 2 of the screws are recessed behind the triangular plate and i don't have the proper drill bit to get them out. i want to be sure that i can at least have the furnace working as much as it had been and am worried that if i don't put it back properly i won't even be able to do that.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

I understand. I am afraid this is the last point. The code and operation all center on this fan or something inside the fan.

You will need to call for service to go any further.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok, thank you SO MUCH for all of your help! it's been so frustrating not being able to figure this out on my own. i'm used to being able to fix things! and it's important for my family to be warm AND save $ on having someone come out. i really, really, REALLY appreciate all your guidance and expertise. in the off chance i can get the right drill bit, is there a way i can contact you directly to go through the process of removing the fan?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 2 years ago

all you need to do is respond to this same thread in your account. Plus after the service is rated I am available for 30 days of free followup

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok billy, i've got a theory here....bear with me:i've been observing the thermostat..it's been driving me nuts. it has been running fine at night and most of the issues i've told you about occur during the day. i was able to dig up the thermostat manual and this kind of thermostat has to be programmed with a heating AND cooling program. i was confused when i didn't hear the click on the thermostat for heat until it got over 67, even though it should have come on at a lower temp. according to the house temp. reading. when i checked the 'view program' button, it showed 67 as the programmed temp. i think the furnace was tripping when i was trying to get heat during the pre-programmed cooling cycle. you think that could be it?
Customer reply replied 2 years ago
at this time of year, i don't want any kind of cooling program, and don't understand how/why to program it in addition to a heat program. i just want the house to be a certain temperature, and when it dips below that temperature, for the heat to come on....
Customer reply replied 2 years ago
it also just seems to be not registering the proper temps....it's reading 63 for house temp when it's definitely warmer than that while the heat temp says 72...it shut off at 63. this does not happen at night.
Customer reply replied 2 years ago
it was a corroded battery terminal on the thermostat the whole time!
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,882
22,882 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have a richmond hot water heater. It is lp with a power
We have a richmond hot water heater. It is lp with a power vent. The unit was was fired up with no problem yesterday but today it will not ignite or even try to ignite. The unit shut itself down. Is t… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I've got amtrol water heater WH-9Z, it's been installed in
Hi my name is*****'ve got amtrol water heater WH-9Z, it's been installed in 2000... Since yesterday, hot water is of yellowish, unclear color. What do you think might be a reason? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We are having to re light are water heater about every 2
we are having to re light are water heater about every 2 week can you tell me what is wrong, is only 6 yr old … read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
I have an Apollo 50 gal water heater, installed Nov 2011,
I have an Apollo 50 gal water heater, installed Nov 2011, and use it for home heat since this is the original heating system. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I just installed a 40 gallon LP gas water heater. The pilot
I just installed a 40 gallon LP gas water heater. The pilot lights up and will continue to burn. It will blink Blue 2 times and then go to blinking 5 Red error code. The furnace has never been fired u… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I installed a Reliance 19.9 gallon water heater in a
I installed a Reliance 19.9 gallon water heater in a friend's mobil home today. The supply lines come into the tank from the side. There is a blue plastic lining material in each 3/4" nipple (cold inl… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I changed the thermocouple on my water heater but the pilot
I changed the thermocouple on my water heater but the pilot will not stay lit … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My tankless water heater will not run, breaker not tripped
My tankless water heater will not run, breaker not tripped and when I push sw1 or sw2 it starts running while pressed in. What is my problem? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Honeywell gas hot water heater modelis leaking around where
Honeywell gas hot water heater model(###) ###-####is leaking around where temp sensor goes into tank. Is it possible that control unit can be replaced or do I need new water heater? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a water heater question! I have a RTE-13 water heater
I have a RTE-13 water heater where the reset button keeps popping. It has been going on for a week now … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Its the thermostat on my water heater... it seems stuck and
Its the thermostat on my water heater... it seems stuck and wont turn to the off position … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have a tank less hot water heater that will not come on. It
Have a tank less hot water heater that will not come on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Rheem Marathon water heater that is not producing
I have a Rheem Marathon water heater that is not producing hot water..., any suggestions ? I have power going to both the top and bottom elements. I have tried to push the reset button but it will not… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
If a gas water heater with an FVIR is installed in a room
If a gas water heater with an FVIR is installed in a room with a washing machine, can cleaning products such as liquid laundry detergent and chlorine bleach trip the FVIR? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My water heater won't light. Yesterday. Trying. Is there a
my water heater won't light JA: How long has this been going on? And how severe is the problem? Customer: yesterday JA: Do you plan on doing the work yourself? Customer: trying JA: Anything else we sh… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A WHIRLPOOL HOT WATER HEATER WITH A HONEYWELL
I HAVE A WHIRLPOOL HOT WATER HEATER WITH A HONEYWELL FLAMABLE VAPOR SENSOR LOCKOUT. MY BASEMENT GOT 2 TO 4 INCHES OF WATER DUE TO RECENT HEAVY RAINS AND APPEARS TO HAVE TRIGGERED THE LOCKOUT. MY QUEST… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need service on my water heater. Water heater still under
I need service on my water heater. Water heater still under warranty. Who do I contact for service asap? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x