I have a GE power vent hot water tank it stop heating and was giving a error code for preasure switch not close. I toggled the blower switch off and back on and the blower started and the burner ignited. At first I thought I was going to have to replace the preasure switch but now not so sure. Any advice would be appreciated.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
12/18/2015
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Please provide all information I request as it makes it more difficult to troubleshoot something when I'm not there onsite. Essentially, you become my eyes and ears. Thanks for the opportunity to help. At the end of our dialog, you will have a chance to rate my service, but please wait until we are finished and you're satisfied you have all the information you need.

It sounds like you have a "finicky" pressure switch which is sometimes working, sometimes not. These switches typically go bad. Another thing to check, make sure your exhaust piping is clear and nothing blocking it.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Let me know if you have additional questions on this. Otherwise, good luck! Thank you for using Just Answer and please don't forget to rate my service as that's how experts get paid (Thanks in advance for any bonus left). Otherwise experts work at their own time and expense. Feel free to post back with any additional questions.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,972
3,972 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My carrier furnace, model 58PAV070-12 does not come when the
My carrier furnace, model 58PAV070-12 does not come when the thermostat calls for heat, but if I cycle the power coming into the unit, it comes on and lights. Any suggestions? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our furnace keeps trying to start. The fan will start first
Our furnace keeps trying to start. The fan will start first like normal but the heat does not come in after a few minutes, then the fan stop. Then repeats about every five minutes. We have a Bryant 32… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a rheem criterion gas furnace that won't light. It
I have a rheem criterion gas furnace that won't light. It was accidentally powered off the other day, now the power is back on. I thought it was the thermostat and replaced it. Its calling for heat an… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My 8 year old furnace stopped working. its a dual zone
my 8 year old furnace stopped working. its a dual zone located in the upstairs attic space. i replaced the blower motor as it was making a loud clanking noise, not producing heat and giving a error co… read more
Appliance Guru
Appliance Guru
18,166 satisfied customers
Have lennox g61mpv fault code 2 = 3 can find nothing wrong
have lennox g61mpv fault code 2 = 3 can find nothing wrong has preasure but no preaure switches working.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Lennox G60V Furnace error code: (4+1) "watch guard: burner
Lennox G60V Furnace error code: (4+1) "watch guard: burner failed to light, exceeded maximum retries." I have clean and reinstalled the flame sensor. changed the batteries in the wall thermostat and f… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Nothing comes on and when I disconnect a wire from the gh
Nothing comes on and when I disconnect a wire from the high limt switch or thermo stat the blow then kicks on The panel light blinks three times that say it the preasure Switch witch I replace the Swi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am troubleshooting a Beacon tubular gas fired heater. I am
Hello all. I am troubleshooting a Beacon Morris tubular gas fired heater. I am familiar with home furnace circuitry and firing sequence, etc. My problem with this unit is with the inducer motor. It wi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane XR80 furnace, vent motor runs, no gas flow. Flame rollout
Trane XR80 furnace, vent motor runs, no gas flow. Flame rollout is good. Changed gas valve still no good.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace that just started blowing cold air.
I have a Carrier furnace that just started blowing cold air. I have gone through the steps to remove the front panels, turn off the internal switch, kill the power from the breaker, leave it for 30 mi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a GMT power vented multi-position gas furnace that stopped
I have a GMT power vented multi-position gas furnace that stopped heating. Blower runs on manual, furnace fan runs for 3 or 4 minutes on auto with temp set high - but no blower or fire. Status light s… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier 58 rav furnace/ac unit in the attic, circa
I have a Carrier 58 rav furnace/ac unit in the attic, circa 1995. Honeywell Chronotherm III stat. When calling for heat furnace won't start. But, sometimes it will start normally. I read led codes (21… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our business uses a Ruud Power Vent Model # XXXXX Currently
Our business uses a Ruud Power Vent Model # XXXXX Currently it is not working due to an error where the pressure switch remained open longer than 5 seconds after the combustion blower energized. I hav… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a Bryant Plus 80 high efficiency furnace. The furnace
I have a Bryant Plus 80 high efficiency furnace. The furnace has difficulty keeping the house up to temperature that is requested form the thermostat (72deg). I have performed some diagnosis myself ba… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Lennox Elite Series heater is not working. First time turned
My Lennox Elite Series heater is not working. First time turned on this year. The thermostat was not working so I changed the batteries and that worked. Took the cover off the furnace, and there are t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier 58pav070-1-08 furnace with a problem. The
I have a Carrier 58pav070-1-08 furnace with a problem. The blower comes on, but it never ignites. It is giving me error code: 31 & 12. There doesn't seem to be any air blockage on the unit. Could it b… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
Bryant Furnace (Approximately 10 Years Old) Product 373LAV036070AJJA
Bryant Furnace (Approximately 10 Years Old) Product: 373LAV036070AJJA Series J Model: 373LAV036070 3 Burners. History: Uncertain. Last week the entire Ignition Sequence works and heat the home to the … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier 58MXA060-12 gas furnace. I had the heat exchangers
I have a Carrier 58MXA060-12 gas furnace. I had the heat exchangers changed out on the class action law suit 1 year ago. Now the furnace has been cutting out leaving the blower motor running. Error co… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x