I have a lopi gas stove. the pilot lights and burns good but

Customer Question
when I turnt he thermostat...
I have a lopi gas stove. the pilot lights and burns good but when I turnt he thermostat up I get a small flame about 1/2 way across the stove. I can not get the flame very high.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/16/2015
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,365
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Sounds like either the orifice or burners need to be cleaned or you gas valve needs to be replaced. Either a clogged/dirty burner or orifice would block the flow of gas to the burners. So would a gas valve that isn't letting enough gas pressure through.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I agree that some thing is clogged but I can't see how to clean the orifice
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago

You have to remove the burners to get to the orifice so you might as well clean the burner too. The procedure is in the manual and is recommended annually

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I can't find how to remove the burner. there is only 2 nuts on the base of the burner but it still will not come out of the unit.
there is not much room underneath to get a hand it to work on the unit.
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago

Here's the manual. The procedure is on page 22

http://www.lopistoves.com/TravisDocs/100-01153.pdf

Removing the burner pan is in page 28

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I read the instructions on how to remove the burner but it will not slide to the left or right as it states in the instructions
Customer reply replied 1 year ago
are you still there
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago

I can't add anything to the instructions

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago

Instructions say to slide t to the left (not right) then lift it out

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I don't mind paying for your service but it did not help me out at all. the burner does not come out as it states it would.
I am not questioning your expertise but you did not help me at all here. I would like the $16.00 credited back to my account.
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago

ok

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I did slide it to the left and it would not come out. I tried sliding it to the right thinking maybe that it might come out but it does not slide either way
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago

I told customer service you want a refund. I can't be there to show you how to get it out. All I can do is point you in the right direction.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I under stand where you are coming from but there must be a secret here some where as to how to remove it if it doesn't slide out. I appreciate your trying to help me out. thanks
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,365
22,365 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The red emergency on/off switch was accidentally turned off.
The red emergency on/off switch was accidentally turned off. After turning it back on, checking the breakers, and turning the thermostat off, then on and resetting it, I still have no heat. What else … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have an TACO SR502 that controls 2 pumps one for zone1 for
Hello, I have an TACO SR502 that controls 2 pumps one for zone1 for Hot water loop and the other for zone2 for baseboard heat and I also have a new TACO ZVC406 that control one other pump that supply … read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
How do i reset the filter thingy on my thermostat?
how do i reset the filter thingy on my thermostat? … read more
Webb-Guy
Webb-Guy
tech.
78 satisfied customers
My Carrier 98% efficient warm air heater does not reach
My Carrier 98% efficient warm air heater does not reach maximum fan speed in the heating mode. There is an dd - on "A" cooling coil (by Trans) added above the bonnet and the same fan turns fast enough… read more
Webb-Guy
Webb-Guy
tech.
78 satisfied customers
We have an old Auto Flo 244D unit with under duct mounting;
We have an old Auto Flo 244D unit with under duct mounting; it needs to be replaced and we are looking for the make /model with least changes to existing configuration. The area around furnace is tigh… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have central AC sysyem - Spacepak airhandler, York
I have central AC sysyem - Spacepak airhandler, York affinity 3s outside unit and a Honeywell TH8100U1003 thermostat. The outdoor unit has been intermittently cooling but seemed to start working again… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
We have a York furnace. We have no heat. The fan is working
We have a York furnace. We have no heat. The fan is working but the burners will not fire. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
Lighting the pilot on my Rheem updraft is no problem but
Lighting the pilot on my Rheem updraft is no problem but after holding the button for a min. or 2 and releasing, the pilot goes out???? … read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
We just moved into our new place and a handyman bought one
Hi Pearl, we just moved into our new place and a handyman bought one of your honeywell thermostats. It's the programmable RTH221B1039/U1. unfortunately it doesn't appear to want to cooperate. Whenever… read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
We just replaced our old furnace Weil-McLain LGB 8S with a
We just replaced our old furnace Weil-McLain LGB 8S with a brand new one the.same … read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
Just recently had my home appraised and bug inspected to
Just recently had my home appraised and bug inspected to secure a refinance a cash out loan. I live where the rain water settles under the house a couple times a year. It is from a creek down the road… read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
My furnace is calling for heat, but blower doesn't start. I
My furnace is calling for heat, but blower doesn't start. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My unit is not operating correctly. I have it set at a temp,
my unit is not operating correctly. I have it set at a temp, and it doesn't come on when the temp goes below the set heating temp. I have to manually hit the set button and it comes on, but then it do… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Nordyne,furnace, pressure switch open fault is
I have a Nordyne,furnace , pressure switch open fault is indicated. The model of furnace is KG7TC120D45D it is about 6 yrs old., had Hvac Tech come out just about 2 weeks ago. Furnace was firing up. W… read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
Is it unsafe to turn off the fans when using the L38DF gas
Is it unsafe to turn off the fans when using the L38DF gas fireplace for a few hours? … read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
I have a Rheem Marathon water heater that is not producing
I have a Rheem Marathon water heater that is not producing hot water..., any suggestions ? I have power going to both the top and bottom elements. I have tried to push the reset button but it will not… read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
I have a Weil-McLain CGa boiler. The pilot is lit and it
I have a Weil-McLain CGa boiler. The pilot is lit and it sounds like it is switching on and off (when the thermostat is on) but we're getting no heat. Is there something I should be checking? Thanks. … read more
Rick
Rick
HVAC Supervisor
22,365 satisfied customers
Looking for replacement blower motor for an old RUUD gas
Looking for replacement blower motor for an old RUUD gas furnace model HN-175JD blower # RL10-9DUH … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x