We have a Veissman boiler. The pressure gauge is under

Customer Question
10psi, and the registers are...
We have a Veissman boiler. The pressure gauge is under 10psi, and the registers are not getting hot. We're thinking the system may need to be depressurized, but aren't sure we're on the right track or how to get the water in.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
12/13/2015
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,079
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Do you have an error code on the display?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

What happens when you cycle the power OFF then back ON?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
When I turn it off,h e pressure goes up to 10. When I turn it back on, I can hear it turn on, the number (temp indicator?) goes up over 200, then the pressure falls back to 6 and the temp indicator steadily falls to 100, and it stops making any noise.
Customer reply replied 2 years ago
Actually, the temp indicator reads 128.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

I have to step away for a while. I'm going to open this backup to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer. If no one has responded by the time I get back I'll pick up where we left off

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, first step will be to re-pressurize the boiler to 20 psig when the boiler is hot, next step will be to bleed air (in any) from the radiators.

I will be back in a minute after I locate the manual and a video on how to pressurize the boiler.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

https://www.youtube.com/watch?v=eaJDmGY7V9s

Let me know if this is the boiler you have or not and if the copper fill loop is actually in place.

If you manage to get the pressure back up, next thing to do is bleed air from the radiators if that is what you have... if you have in-floor radiant heating loops, we will take a different approach.

Let me know if you need coaching on how to bleed air from the radiators and other high points in the system, air in the system prevents water flow, and will produce the symptoms that the system is exhibiting.

We can go from there without a time limit.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
That's the boiler. I saw this video. We don't have the fill loop. That's why we asked here. I can't figure out how to fill to correct the pressure.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks, ***** ***** what I needed to know.

You can use a USA standard garden hose connector on most of those units.

Tell me what connection is at "C" and attach a close up photo of it here using the paper clip icon at the right end of the tool bar, or use the 'attach files' link to the left of your send button.

http://screencast.com/t/K2opdwmu8PFp

If you can include a photo taken from a low angle, looking up at the bottom of the boiler so that I can see how the plumber installed it, that will help as well.

We can go from there.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

I will stay with you on this, without a time limit until you have the boiler repressurized.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The issue with the garden hose is that it would require a hose with female connectors on both ends. The attachment on the boiler is a regular spigot with a male end.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello again, there are various adapters that will give you two female ends, depends on what your local hardware store carries.

http://screencast.com/t/3RkTpbxOoZLo

Let me know if those directions make any sense on your end or not. Here they are again

http://screencast.com/t/K2opdwmu8PFp

We can go from here without a time limit.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

ooops I forgot to make a link out of it

http://screencast.com/t/K2opdwmu8PFp

that should be a hyperlink, hopefully.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks for letting me work with you. When we are finished,if my answer has been polite, professional, and thorough, please locate the 'rate your expert button' and click one of the ratings .If you still need help let me know!.

Rating will not increase your charges, nor close the question, but is how I earn my living.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,168
9,168 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,168 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My boiler in on but is not working. The lights on the screen
my boiler in on but is not working. The lights on the screen is on but not heat. … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
Rick, I have no DHW. I have a Viessmann Vitodens boiler and
Hi Rick, I have no DHW. I have a Viessmann Vitodens boiler and a Heat-Flo indirect 60 gallon hot water tank. They are controlled by a Tekmar 370, set to DHW priority. I have three radiant heat zones a… read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
Boiler runs for a brief while, then shuts off. A few hours.
I am not a trained service technician. But am hoping it might be a simple easy fix… read more
Phil
Phil
Mechanical Engineer
9,168 satisfied customers
Peerless Boiler Series MI85 Gas Boiler installed 2015. We
Peerless Boiler Series MI85 Gas Boiler installed 2015. We have 3-zone water heat. Furnace works perfectly until outside temp goes into single digits and below. Furnace goes on and off repeatedly tryin… read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
We have a Burnham boiler for our in floor heat.. and it will
Hello, We have a Burnham boiler for our in floor heat.. and it will not heat the floor up past 70 degrees.. we have cleaned it replaced the pump and can't figure out why it won't stay warm … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
I have a Keston Boiler and nothing is displayed on screen
Hi I have a Keston Boiler and nothing is displayed on screen and won't switch on … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a question regarding the boiler temperature setting,
I have a question regarding the boiler temperature setting, water pressure and room thermostat. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
We have an old weil-mclain boiler for radiant heat. Old
we have an old weil-mclain boiler for radiant heat … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
Steam is escaping from the back of the boiler into the
steam is escaping from the back of the boiler into the chimney, is the boiler bad or the flue? … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
I have two questions I have a hot water radiant heat system
I have two questions I have a hot water radiant heat system and an electrical a/c unit can I have them both on the same thermostat? can I wire it so that when the circulator kicks on it will turn on t… read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
I have a Weil McLain Ultra boiler that I use for both
I have a Weil McLain Ultra boiler that I use for both radiant heating and hot water. Our hot water temp for hand washing, etc is to high. How do I adjust? The system was installed in 2007. … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
I have a Weil mclain boiler, and a nest thermostat. the
I have a Weil mclain boiler, and a nest thermostat. … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
Can radiant heat be installed under existing floor? Could it
Can radiant heat be installed under existing wood floor? Could it damage the floor and which is better electric or pex? Is there any danger of heating wood floors that were sanded and sealed with an o… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
Brought a boiler from nome heating. Bought a boiler from
bought a boiler from mike west nome heating for eght thousand dollars need to insurance for my boiler … read more
Rick
Rick
HVAC Supervisor
23,079 satisfied customers
I have electric radiant heating in the ceiling. The
I have electric radiant heating in the ceiling. The thermostat is broken. It is an old GE model, which I cannot find the same type anywhere (don't see a model number on it). I thought Honeywell may ma… read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,353 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x