Rheem Criterion not heating and green LEDs are on.

Customer Question
I have a Rheem Criterion...

I have a Rheem Criterion II RGPH-12NARJR that is not heating. The blower runs continuously even with the G wire disconnected.

The two green LED's are ON, but the yellow (flame) LED is off and does not come on at all.

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
12/1/2015
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,357
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Have you turned power off to furnace to reset faults. If not turn off and back on. If it lights and goes back off.

The flame sensor needs cleaning. It is located next to last burner. Long rod inserted into flame. Clean with sandpaper or steel wool. Let me know.

Ask Your Own HVAC Question
Customer reply replied 2 years ago

Yes I have unplugged the unit and re-plugged several times. No it does not light and go off. It never tries to light. Green lights go on as soon as door switch is closed- no blinks. Yellow light never comes on.

HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Ok. Lets test thermostat. Open door to blower compartment you will see furnace board. Place a wire between R and W and see if furnace fires. We are bypassing thermostat. Make sure door switch is pushed in. Green light means control is powered. Let me know. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago

I did that- no change. Also disconnecting G wire from Thermostat does not stop fan.

HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Both lights on with fan running all the time and no fault codes. Indicates bad board. If tin was limit or pressure switch you would get a fault code flash. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No- that was my conclusion before- I was hoping you might have a better suggestion how to get it to work.
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Sorry according to flow charts bad board. You jumped the R and W nothing happened. You should have at least had fault code on board. Sequence of operation is the thermostat calls for heat.

The small induce blower starts for 20 seconds, igniter glow for 10 seconds and gas valve opens. Any problem with any of the sequence the fault code will start blinking.

Thanks,

Russ.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,357
5,357 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My Rheem Criterion II furnace will light and run but when it
My Rheem Criterion II furnace will light and run but when it reaches temperature set on thermostat, the gas shuts off but the induction blower and main blower keep blowing and won't shut down … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem Criterion II gas furnace Model RGPH-04EAUSR The blower
Rheem Criterion II gas furnace Model RGPH-04EAUSR The blower turns on for a few seconds then turns off. The thermostat is set to OFF. This happens randomly for no reason. I have unplugged the thermost… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem Criterion II burner does not stay lit, on seconds then
Rheem Criterion II burner does not stay lit, on for 5 seconds then off. 2 green lights on on the circuit board. Blew & sucked on tube to pressure switch(gurgling sound).… read more
Rick
Rick
Supervisor
24,392 satisfied customers
I have a Rheem Criterion II Model #RCBA-2457GG14XI small
I'm Mack - I have a Rheem Criterion II Model #RCBA-2457GG14XI for and small industrial office. I have two green Lit LEDs - but nothing is work - no exaust blower, not fan motor and it's not igniting. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace is a Rheem Criterion II model RPGH-12EARJR and wont
My furnace is a Rheem Criterion II model RPGH-12EARJR and won't start. I've replaced the batteries in the control panel and set the temp 10 degrees higher than room temperature and verified the circui… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem Criterion II furnace that will not ignite.
I have a Rheem Criterion II furnace that will not ignite. The call for heat comes, then the ignition blower comes on, then I can see the pressure switch suck back, but the spark igniter does nothing. … read more
GOTOGUY62
GOTOGUY62
4 satisfied customers
MFG: Rheem Criterion II Model: RGPH-10EAMER Hello. HVAC
MFG: Rheem Criterion II Model: RGPH-10EAMER Hello. HVAC Newbie here. Here's my scenario. I turned on the A/C. The outdoor unit runs and pumps cold air into indoor unit. The blower fan does not engage.… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,357 satisfied customers
I have Rheem Criterion II furnace. installed in 2000 natural
I have Rheem Criterion II furnace. installed in 2000 natural gas, downflow unit. The fan runs continously whenever the power is on to the furnace. Thermostat fan switch is set to auto. doesn't matter … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
No Heat. Rheem criterion 2 board# XXXXX Power light
No Heat. Rheem criterion 2 board# XXXXX Power light on on circuit board with green LED next to it flashing 3 times. At first updraft motor would run and then the blower would kick in and run for a few… read more
hvac-technician
hvac-technician
Service Manager
Vocational, Technical or Trade Scho
62 satisfied customers
Rheem Criterion II furnance 10 years old. Heat and blower
Rheem Criterion II furnance 10 years old. Heat and blower comes on, when room temp is reached, heat turns off blower keeps running. When temp drops below thermostat setting heat comes back on but blow… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
have a split system, rhem criterion II, model rgph-05naver,
have a split system, rhem criterion II, model rgph-05naver, furnace 50,000 btu's, when I turn the heater on from the thermostat, everithing works, but the flame stays on just for 1 1/2 or 2 seconds, t… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a Rheem Criterion II with a programmable Aprilaire thermostat.
I have a Rheem Criterion II with a programmable Aprilaire thermostat. Problem is that I get a clearing fan and ignition and a temperary flame(about 10 seconds) then flame is gone but fan still runs th… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
We have a Rheem Criterion II Model# RQOG12EARJR, the blower
We have a Rheem Criterion II Model# XXXXX the blower fan run continuously and won't let the furnace cycle to heat. If you unplug the unit and let it sit for a minute, then repower it the furnace will … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a rheem criterion ii. will not come on. 2 top green
I have a rheem criterion ii. will not come on. 2 top green leds come on no flashing for trouble codes. replaced damaged transformer & still will not come on, cannot find any fuses followed flow chart … read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Rheem criterion II rglh-o5eauer Will not ignite. everything
Rheem criterion II rglh-o5eauer Will not ignite. everything works normal, blowers work and even after gas shuts off main blower comes on and stays on. flame sensor works as its not on without flame an… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
My Rheem Criterion Furnice will not light. The fan runs and
My Rheem Criterion Furnice will not light. The fan runs and will not turn off until you kill the power to furnace. ???? Even with the thermostate turned off and even disconnected from wiring. Help Not… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,357 satisfied customers
I have a Rheem Criterion II heating system. The problem is
I have a Rheem Criterion II heating system. The problem is the fan continuously runs. The heat however does fire when called upon. Any ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Rheem Criterion II LXE Model Number RGPH-12EARMR that
I have Rheem Criterion II LXE Model Number RGPH-12EARMR that just stopped working. When I unplug and replug in a couple of minutes, the green LEDs come on and then the red LED for the motor starts bli… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,357 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x