My Trane furnace red led blinks 3 times.

Customer Question
My Trane furnace red led blinks 3 times.
Submitted: 2 years ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 1 minute by:
11/21/2015
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 17,579
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello and thanks for using this service, if you have been waiting do not worry or get upset I am just one of the techs on here and I try to get to as many customers as I can and I just picked up your question now. Please give me time to respond sometimes I get your replies late so there may be a significant delay in responses. Please be patient and often I will ask you questions to narrow down the issue to get is diagnosed correctly.

Have you checked the port where the tube connects, use a small paperclip or wire to make sure the port is clear often they get clogged up and that is what is causing that code.

We are on the honor system for our time, all I ask is please rate my service using the STAR RATING LINK on your page before you leave. If you are not happy with the service please let me know before leaving a negative rating. This is the only way I am paid or credited through the site for my time. This will also allow you to get directly back to me for FREE follow up questions and tips are greatly appreciated! Thanks

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi,
Yes, I used a piece of coat hanger to make sure the vacuum port was clear.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

If you do not feel a light suction off the nipple itself when the inducer fan is running I would say something is blocked in the exhaust tube or check the condensate drain line for a blockage.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi,
Yes, I used a piece of coat hanger to make sure the vacuum port was clear.I ran a piece of hose from the outside all the way through to the furnace where the inducer fan connects. It came all the way through with no blockage. I have the condensate hose, from the bottom of the inducer fan housing, unattached currently, to ease with the fan removal.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Pull the fan out and check it out, but put the condensate hose back on when trying it as it needs to be in place for proper vacuum.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi,
Yes, I used a piece of coat hanger to make sure the vacuum port was clear.I ran a piece of hose from the outside all the way through to the furnace where the inducer fan connects. It came all the way through with no blockage. I have the condensate hose, from the bottom of the inducer fan housing, unattached currently, to ease with the fan removal.I initially removed the fan to check its operation, it works properly. The outlet blows with great force, and the inlet does create quite a vacuum when you place you palm over it. I will go down right now and reattach the condensate hose and give it a go. I will report back in a few minutes.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

ok sounds good

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi,
Yes, I used a piece of coat hanger to make sure the vacuum port was clear.I ran a piece of hose from the outside all the way through to the furnace where the inducer fan connects. It came all the way through with no blockage. I have the condensate hose, from the bottom of the inducer fan housing, unattached currently, to ease with the fan removal.I initially removed the fan to check its operation, it works properly. The outlet blows with great force, and the inlet does create quite a vacuum when you place you palm over it. I will go down right now and reattach the condensate hose and give it a go. I will report back in a few minutes.No luck, even with the condensate line reattached, it still does not create a vacuum at the nipple for the pressure switches.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

You could have a restriction on the exchanger? This would cause no suction on the port. Is the condensate line off the exchanger all clear?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi,
Yes, I used a piece of coat hanger to make sure the vacuum port was clear.I ran a piece of hose from the outside all the way through to the furnace where the inducer fan connects. It came all the way through with no blockage. I have the condensate hose, from the bottom of the inducer fan housing, unattached currently, to ease with the fan removal.I initially removed the fan to check its operation, it works properly. The outlet blows with great force, and the inlet does create quite a vacuum when you place you palm over it. I will go down right now and reattach the condensate hose and give it a go. I will report back in a few minutes.No luck, even with the condensate line reattached, it still does not create a vacuum at the nipple for the pressure switches.I will check that now.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

ok

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi,
Yes, I used a piece of coat hanger to make sure the vacuum port was clear.I ran a piece of hose from the outside all the way through to the furnace where the inducer fan connects. It came all the way through with no blockage. I have the condensate hose, from the bottom of the inducer fan housing, unattached currently, to ease with the fan removal.I initially removed the fan to check its operation, it works properly. The outlet blows with great force, and the inlet does create quite a vacuum when you place you palm over it. I will go down right now and reattach the condensate hose and give it a go. I will report back in a few minutes.No luck, even with the condensate line reattached, it still does not create a vacuum at the nipple for the pressure switches.I will check that now.I checked the condensate line off of the exchanger and it looks clean and clear.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Other than the inducer not running to speed there would have to be a blockage in the unit. Now the suction is very very light so are you certain there is no suction? Make sure the rubber tube is not cracked either.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Hi,
Yes, I used a piece of coat hanger to make sure the vacuum port was clear.I ran a piece of hose from the outside all the way through to the furnace where the inducer fan connects. It came all the way through with no blockage. I have the condensate hose, from the bottom of the inducer fan housing, unattached currently, to ease with the fan removal.I initially removed the fan to check its operation, it works properly. The outlet blows with great force, and the inlet does create quite a vacuum when you place you palm over it. I will go down right now and reattach the condensate hose and give it a go. I will report back in a few minutes.No luck, even with the condensate line reattached, it still does not create a vacuum at the nipple for the pressure switches.I will check that now.I checked the condensate line off of the exchanger and it looks clean and clear.I checked all of the rubber hoses to and from the pressure switches, all look intact and clean.I feel no vacuum at the nipple, but that is with my fingertips, I didn't put a vacuum gauge on it. What chamber is it that is trying to be sucked into a vacuum? What is sealing this particular chamber as to not let vacuum escape through a hole or something?
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

The exhaust blower is drafting air through the exchanger and burners so if the heat exchanger is blocked that will cause no vacuum on that port like a clogged vacuum filter. If you are certain everything is clear you may have to have the exchanger scoped out by an HVAC company to see if it is blocked up.

Ask Your Own HVAC Question
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 17,579
17,579 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Centurion 2 not working with the flashing indicator
I have a Centurion 2 not working with the green flashing indicator 4 time. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Collector flue box gets extremely hot to touch. It's a
Collector flue box gets extremely hot to touch JA: Just to clarify, what type of fireplace is this? Customer: It's a furnace JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything else… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have Yorx High efficiency tubular heat exchanger, im not
Hi, my name is***** have Yorx High efficiency tubular heat exchanger, im not sure wich model though GY9S , GM9S, or GF9S. There is water leaking from the white PVC pipes, can I just cut them out and r… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x