Tom, I have an Amana 90 furnace that will run but not bring the temp up to what the thermostat is set at. It runs a short cycle 6-8 minutes and then cuts out and will try to relight for 3 attempts and go into lockout. I reset and then the same thing happens again, bad high heat sensor??? Changed filters, etc. but to no avail.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 31 minutes by:
11/19/2015
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to help answer your question(s). Please provide all the information I ask for since I'm not onsite. At the end of our dialog you will be asked to rate my service, but please wait until then and all your question(s) have been answered satisfactorily. Thanks for your business!

Have you tried cleaning the flame sensor?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
sir
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

What did you clean it with, can I ask?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Steel wool
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

OK, that sounds right. Can I get full model number, please? What LED flash code are you getting when it shuts down?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Model # *****1-flash
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Are the burners lighting at all?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
running a short cycle 6-8 minutes then goes into lockout. I reset it and then same thing.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

When they light, watch them. Do they light smoothly and all the way across quickly?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
they do. Flame is steady blue without color change.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

One thing to check is that front cover pressure switch. Is the front cover on securely when you try to run it?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
That was my initial thought too. I will double check it and get back to you.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

OK, thanks.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Tim - Front cover pressure switch does not appear to be the culprit. What is the best way to rule out an issue with the thermostat?
I have a honeywell 5+2 day programmable model.
Thinking that I should jump the wires and see if it stays going. It is probably not the issue, but...I have a 4 wire system, the back of the thermostat has G-W-Y-R/Rc, which ones should I jump to call for continuous heat?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

If it was a thermostat issue, it would NOT lockout with a flash code. It just wouldn't be on at all.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok, thanks. I have been watching it for the last few attempt and the thermostat calls for heat, blower kicks in, igniter lights, but no fuel. I cannot hear the valve try to open. Any thoughts?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

You may have a bad gas valve. Get a voltmeter and set to "volts AC" and put one probe on each of the two terminals of the valve. Watch it through a few cycles. If the valve gets voltage, but no gas, and you have good gas pressure, valve may be bad.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Did a complete 1min reset, flipped main and the furnace fired and ran for 7 and a half minutes then abrupt fuel shutoff. Main blower ran for 2-3 seconds and stopped. Now it's trying to restart, but the gas valve is not opening.
Customer reply replied 2 years ago
What could be telling the gas valve to close and then not allow it to open?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

The valve could be getting voltage from the board, but if it's working intermittently, could cut out, hence that's why we need to confirm voltage.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
What sensors/switches would shut the gas off, then sit idle for a period of time and then allow it to open? There is something not allowing the gas valve to open for a set period of time. It seems like the furnace operates once every hour for 6-8 minutes and then goes into lockout for an hour, runs... Any ideas???
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Please start by checking voltage to the valve through several cycles. I want to confirm that we don't have a bad valve. What we are looking for is voltage to the valve (24 volts), but no gas coming out, and yet the gas supply to the unit is still there.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
When burners light I have 24 volts, when it doesn't no power to the valve.
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

As long as there is a call for heat, you should have 24 volts to the valve. If it drops off, you may have a bad board.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

You can try jumping R to W at the board after first shutting power off. This will simulate a call for heat when you power back up. The inducer should start, pressure switch will close and then ignitor will light and you will get 24 volts to the valve. This voltage should remain as long as you have R to W jumped.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

It s also possible that the furnace could shut down if flame isn't sensed. Even though you cleaned flame sensor, it may need replacement. Make sure you have a good ground from the board to the burner area.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok Tim, I definitely follow your thought on the flame sensor. I have 24v at the gas valve. Furnace comes on runs 6-8 minutes and then gas valve closes and system tries to relight 3 times and then is locked out. Approx. 1 hr goes by and then the system starts again runs 6-8 minutes and then gas valve closes, tries to relight 3 times, lockout and then the same cycle... What changes over the course of an hour, system reset of some sort?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Yes, it will try 3 times, then go into a lockout for a period of time. Again this could be a weak ignitor or even the flame not being sensed (poor ground from board to burner area, bad flame sensor.). The problem with this 1 flash code is there are SO MANY THINGS it could be. You saw the list. I'm just trying to eliminate some of them.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Did you have additional questions on this?

Ask Your Own HVAC Question
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
3,971 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The red emergency on/off switch was accidentally turned off.
The red emergency on/off switch was accidentally turned off. After turning it back on, checking the breakers, and turning the thermostat off, then on and resetting it, I still have no heat. What else … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I changed my thermostat and then put the original back nd
I changed my thermostat and then put the original back nd not it will not light up at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
I have 4 honeywell rlv4305 thermostats. they are all hot on
Hello, I have 4 honeywell rlv4305 thermostats. they are all hot on the top right corner. they are all in standby mode. Is this an issue, or are they hot, because they are not calling for heat right no… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
I recently had a bosch geothermal CE035 installed in my
i recently had a bosch geothermal CE035 installed in my home. i am wondering how do I change the setting to keep the auxiliary heat off longer ? … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
Thermostat keeps returning to 70 degrees even tho I cancel
Thermostat keeps returning to 70 degrees even tho I cancel present temp by pressing run and put a new lower temperature in and it still returns to apparently a programmed 70 which comes in during the … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
My Carrier 98% efficient warm air heater does not reach
My Carrier 98% efficient warm air heater does not reach maximum fan speed in the heating mode. There is an dd - on "A" cooling coil (by Trans) added above the bonnet and the same fan turns fast enough… read more
travis webb
travis webb
tech.
2,153 satisfied customers
How do i reset the filter thingy on my thermostat?
how do i reset the filter thingy on my thermostat? … read more
travis webb
travis webb
tech.
2,153 satisfied customers
Pressure switch error on my trane xl14c unit. Looking for a
Pressure switch error on my trane xl14c unit. Looking for a reset button but can't locate it … read more
travis webb
travis webb
tech.
2,153 satisfied customers
I have an TACO SR502 that controls 2 pumps one for zone1 for
Hello, I have an TACO SR502 that controls 2 pumps one for zone1 for Hot water loop and the other for zone2 for baseboard heat and I also have a new TACO ZVC406 that control one other pump that supply … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Furnace fan won't stop running after the heating cycle is done
My furnace fan won't stop running after the heating cycle is done. The only way to shut it down is to turn off the main power switch located near the furnace. I replaced the limit switch a while back … read more
Tim H.
Tim H.
HVAC Professional
3,971 satisfied customers
Having a issue with my early rudd gas pack. I can hear lift
Having a issue with my early rudd gas pack. I can hear lift motor come on and burner lights .burner gos out in under a min. … read more
Chad DeYoung
Chad DeYoung
8 satisfied customers
I have developed a continuous humming sound that I cannot
I have developed a continuous humming sound that I cannot figure out where it is coming from. It can be heard throughout the house but my neighbor who is attached on the bedroom wall does not hear it.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Honeywell Honeywell TH8320R1003 outdoor sensor reads -29F.
Honeywell Honeywell TH8320R1003 outdoor sensor reads -29F. Have 2 sensors both read the same. Sensor resistance is 109K … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
My Gibson furnace stopped working. Could you advise how I
My Gibson furnace stopped working. Could you advise how I can turn it back on? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My 3am fuse blows up every time when I start heating my
My 3am fuse blows up every time when I start heating my house. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
We have an old Auto Flo 244D unit with under duct mounting;
We have an old Auto Flo 244D unit with under duct mounting; it needs to be replaced and we are looking for the make /model with least changes to existing configuration. The area around furnace is tigh… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My Hydrotherm HC-100B boiler is about 30 years, I don't know
my Hydrotherm HC-100B boiler is about 30 years, I don't know the last time the gasket Flange was change but it is leaking, I was told that by a heating company that its a 50/50 chance that if they bre… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
346 satisfied customers
Our furnace is brand new and it comes on for one minute and
Our furnace is brand new and it comes on for one minute and shuts off and does this three times and then quits and it flashes three red and three red . Model mg95080c16mp11c serial number wic7512698 … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x