spd tap to reduce cfm...
How can I reduce the rpm of furnace blower motor on just one spd tap to reduce cfm. Motor has 3 spd taps but all are too much cfm for cooling coil. What a mess.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
11/18/2015
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,763
Experience: Furnace, A/C and heat pump specialist.
Verified

The 80,000 furnace is not designed to perform with a 2 ton system .This is a 3.5/4 ton furnace.

You will need a smaller furnace or will have to do some experimental rigging .You could try replacing the motor with a lower hp motor, but will have to make sure the amp draw does not exceed rating on new motor

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I was thinking of maybe using choke coil on one winding to achieve this.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Not sure how that would work.I a not familiar with doing this as a solution to slow down a 120v AC motor .Would you like me to open he question to see if other experts may know?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Not at this time.
Thanks
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Ok good luck with this.If I can assist further, let me know.I would probably get one of those universal "trip saver " motors that adjustable from 1'8 to 1/3 hp motor and experiment with speeds to find a speed that will move air slow enough across coil to maintain at least 17 degree drop and amp draw stay within parameters.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.

Leaving a poor service rating will not automatically refund your money,but reflects poorly on your expert. You have to request a refund if not satisfied with the information provided being accurate.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
If I had a equivalent motor with 5 spd taps that would probably serve my customer but this one of those jobs where someone has sold equipment they had to sell not what the customer needed and I'm trying to clean it up for them as inexpensive as possible. I need to keep heating cfm as is though.Thanks again
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

I am thinking about using the trip saver shown at link below.You can cut the spade clips off that go to the taps and wire nut the wires to different speed wires. Maybe use 1/5 for cool and 1/4 for heat if you need heat to move more air than cool.

http://www.myhvacparts.com/store/Trip-Saver-Motor-115%20volt.php

Ask Your Own HVAC Question
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,763
8,763 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Concord 90 furnace blower runs wont stay lit. I blew out
concord 90 furnace blower runs wont stay lit JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: yes JA: Anything else we should know to help y… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My 59SC2b furnace blower running time and blow cold air
My 59SC2b furnace blower running long time and blow cold air after heating cycle. … read more
airheatman
airheatman
HVAC Technician
8,763 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
airheatman
airheatman
HVAC Technician
8,763 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace blower stopped suddenly. I live in about 2,000sq
My furnace blower stopped suddenly. I live in about 2,000sq feet single family home. I called an HVAC technician. They arrived and installed a new motor. However, after they left I run the furnace and… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have an older luxaire commerical furnace blower motor runs
have an older luxaire commerical furnace blower motor runs all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My furnace blower wiil not start. Hopefully. Furnace tries
my furnace blower wiil not start JA: Did you check the furnace's filters? Customer: no JA: Do you plan on doing the work yourself? Customer: hopefully JA: Anything else we should know to help you best… read more
airheatman
airheatman
HVAC Technician
8,763 satisfied customers
My evcon furnace blower fan cycles every day at 8:20 with no
My coleman evcon furnace blower fan cycles every day at 8:20 with no demand and no exhaust fan operation. It just co es on runs for 2 minutes then shuts down, and there was no previous heat dema d … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Nordyne furnace blower starts immediately when I turn on
My Nordyne furnace blower starts immediately when I turn on the switch. The LED light on the control board flashes 5 times. There is no flame. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My '92 Carrier model 58ssc furnace blower motor has finally
Hi! My '92 Carrier model 58ssc furnace blower motor has finally quit. I wonder what I can replace it with … read more
airheatman
airheatman
HVAC Technician
8,763 satisfied customers
We have a question about a furnace blower that is not
We have a question about a Bryant furnace blower that is not working. The model number is ***** We have noticed a blinking light error that has two short and four long blinks. … read more
airheatman
airheatman
HVAC Technician
8,763 satisfied customers
I have a loud noise coming from furnace blower motor. Do i
I have a loud noise coming from furnace blower motor. Do i need to oil up the motor? Its a lennox g40uh (x) … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I'm replacing a furnace blower motor and assumed it would be
I'm replacing a furnace blower motor and assumed it would be plug and play. Old motor had 5 wires; white, brown, black, red and blue. The brown and white went to the cap, with another white wire comin… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
383 satisfied customers
My furnace blower won't shut off. Have confirmed it's not
My furnace blower won't shut off. Have confirmed it's not the thermostat (by disconnecting same). Could the fan relay cause this? … read more
derekh1966
derekh1966
0 satisfied customers
Our lenox furnace blower doesn't come on when on auto
Our lenox furnace blower doesn't come on when on auto setting. Still comes on when set to on. Ideas of what maybe going on? … read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
Furnace blower cycle on and off even when thermostat is in
furnace blower cycle on and off even when thermostat is in the off position. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x