Reznor waste oil burner won't stay lit. I got a new car cell, it still won't sense the flame. I'm at a loss now........if I take cad cell wires off and "jump" it, it will light and stay running.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
11/12/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,151
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

In this case either the new CAD cell is bad, or waste oil debris has built up and is blocking the line of sight to the burner flame........ or.... the flame safety relay printed circuit card is going bad.

You can test for that... the flame sensing relays close between 750 and zero ohms resistance.. most will close as soon as resistance drops below 750.

To test this buy several resistors, 1,000 ohms, 750 ohms, 500 ohms 200 ohms. and 100 ohms... fit those one at a time across the CAD cell wires with the CAD cell removed... and see how low you have to with the resistors before the flame safety relay allows the burner to stay on.

Let me know what you can discover, we can go from there without a time limit.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

You could also use a variable potentiometer and adjust it to read these various resistances.

Radio shack will have the, so will any electronics supply store in your area. You will only need the smallest and least expensive of those.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the igniter was replaced, and this is "new" cad cell #2. If I move the cad cell and adjust it, it stays lit at times, but not always. Not sure what you're talking about when you say flame safety relay card
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello, when something like this happens, we suspect that a brand new part, directly from the sealed box, could be bad... it happens in 5 or 10% of the cases.

The fact that you have to move the cad cell indicates a carbon deposit build up inside the burner head, that is blocking the CAD cells view of the flame...you can visually inspect for that.

http://screencast.com/t/wakseEe00

Those are pictures of typical flame detection relays that the CAD cell is wired to... just follow the wire from the cad cell, it will terminate at the relay... it is a complex affair about 5" cube in size, with a red button on the top to reset it (do not reset more often than twice, you can flood the boiler with unburned fuel that way and create a fire hazard.)

Look that over, let me know what you can discover, and do the tests with the resisters on the CAD cell wires... if that is no part of your skill sets, tell me which direction you are from the center of the nearest city and will get you a short list of well rated oil burner specialists.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
K the relay is what I called ignition box. Sorry to confuse you. I just replaced it, it's brand new, the burner compartment did have build up, I've cleaned it all out thou. Would the nozzle keep it from staying lit? I'm certain it's boiled down to the sensor not sensing the flame. Question for you, I'm assuming that jumping it to stay on would be regardless of how dirty it was since I bypassed the sensor. Or am I wrong on this?
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello again.

Yes, if you jumper the cad cell to keep the burner pump running, it would not make any difference if the cad cell could not see the flame or not... however you loose the flame safety feature and put the house at risk of fire.

If you have flame, then the nozzle is not the problem, however you could also have a bad nozzle that is causing soot to build up inside the boiler and needs to be replaced... that however would have no effect on flame sensing, since it does not take much light at all to operate the CAD cell.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
K, so if I have that cylinder clean as can be, brand new cad cell and brand new circuit relay card ( the box where the cad cell is plugged into) this thing SHOULD stay lit. Yes I understand the whole flame sensor "hazard" I would never jump it just to make it work. Which is why I'm trying to fix it correctly.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello again, I can't think of anything else that could be wrong, except that you might have gotten a bad CAD cell... you can test it with a flashlight, it should go up to between 10,000 and 20,000 ohms with the light on it, and drop close to zero ohms in the dark... they close below 600 or 700 ohms in most cases, so it is a very broad range device, not at all touchy.

The female side of the plug it connects to could be corroded or suffering a spotty connection.

You can also use a potentiometer to see where the flame protection relay is operating.

Stay in touch, we should be able to figure this out sooner or later.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,151
9,151 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,151 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
When I run out of oil in my Lenox oil burner, the reset
HI when I run out of oil in my Lenox oil burner, the reset button turns red. One quick push and the burner fires up. This morning, no heat. I have oil and the reset button is blinking green, which I'v… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Just moved into new home. One oil burner and 3 air handlers.
Just moved into new home. One oil burner and 3 air handlers. Very strange that one air handler provides for entire 1st floor but no warm air comes out in the master bedroom. I tried blocking the vents… read more
Phil
Phil
Mechanical Engineer
9,151 satisfied customers
I have a beckett oil burner in a floor furnace. It is A-AF.
I have a beckett oil burner in a floor furnace. It is A-AF . I installed it in Oct. 2017 . It got low of oil in the tank and sucked air. I bled it and put a new nozzle in it . I also washed up the ele… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a wei-mclain gold oil burner that stopped firing up.
I have a wei-mclain gold oil burner that stopped firing up. the blinking green indicator light is flashing. the blinking green light goes off while I press the reset button for 45 seconds until I get … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have one zone of an oil burner/forced hot air system that
I have one zone of an oil burner/forced hot air system that is not working. I replaced the zone valve which had a burned out motor. But it appears that no water is circulating through that zone (upsta… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Oil burner Aquastat possible problems. Two days. I have in
The stat is fairly new I think the igniter transformer might be bad or going bad. Which may have led to my problem.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have a Beckett Oil Burner and we currently have no heat I
Hi I am Pete We have a Beckett Oil Burner and we currently have no heat I thought we were low on oil so I just filled up today The green light is flashing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a oil burner assembly off a Shenandoah waste oil
I have a oil burner assembly off a Shenandoah waste oil furnace I have no spark I do have 120 volts at board for the transformer assembly that sits a top the spark electrodes is there a way to test th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an oil burner question, One week, Yes, Please connect
Please connect me with someone who deals with oil burner questions… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Riello 40 series mectron oil burner has issues on cold
Riello 40 series mectron oil burner has issues on cold start … read more
Brian
Brian
Plumbing & Heating Engineer
122 satisfied customers
I Have an old Peerless oil burner with a Aquastat-Protecto
i Have an old Peerless oil burner with a Aquastat-Protecto Relay Unit Type R8182D. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old Vaillant oil burner and I was told the "Gun"
I have an old Vaillant oil burner and I was told the "Gun" is gone … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an international oil burner company mac 1199 and the
I have an international oil burner company mac 1199 and the blower will not cycle off. I can flip the switch to shut it off, but it wont shut off on its own when it reaches temperature. The thermostat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 2 zone house with an oil burner, 2 air handlers and
Hi, I have a 2 zone house with an oil burner, 2 air handlers and 2 AC units. The system is connected to a Taco SR 503 zone controller, with zone 1 being the water storage tank, zone 2 being downstairs… read more
Michael Ferryman
Michael Ferryman
85 satisfied customers
My oil burner was out of oil for a week. I need to bleed the
my oil burner was out of oil for a week. I need to bleed the fuel line. When I got home yesterday my son had pushed the reser twice so I only got 1 try to bleed it and did not get oil out of the line.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My beckett oil burner is out, started today I replaced the
started today I replaced the nozzle and filter for the heck of it all looked good … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x