HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC

I have a ac unit 460v three phase, there is one leg from a

Customer Question
contactor has 460v to the...
I have a ac unit 460v three phase, there is one leg from a contactor has 460v to the ground, why is that?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
11/10/2015
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,805
Experience: Furnace, A/C and heat pump specialist.
Verified

Sounds like you have what is known as a Delta or stinger leg,This is not uncommon with 3 phase power.It is considered a stinger leg or a hot leg.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
what does it mean?
Customer reply replied 2 years ago
A bad contactor?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

The Delta Wye is just an electrical service provided to buildings such as large industrial plants or buildings where high voltage is used. The only thing you need to be concerned about is that the transformer in thee units is supplied by the normal legs rather than the "hot" leg.

I once asked a technician fro the local power company to explain this and he told me I would almost have to be mathematical scientist to understand the angle and phasing of the electrical triangle.

The delta leg is not going to be an issue with the contactor.

If you would like ,I can send this to category mods and ask them to refund your deposit and then you can ask the question requesting an electrical engineer rather than an HVAC tech.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have a inducer motor not running which is 1 phase 460v, one leg supply from that contactor and the other leg from the control board and the leg from the control board is also 460v to ground
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Let me get you t do this. Check between the two wires that go to the inducer, If we are getting 460v between them, that is fine.The only thing we need to make sure the stinger is not going to is the transformer.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
It only got 0v, since both leg are 460v to ground
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

You should be getting 460 between these legs.I am going to open this to other experts who may be able to assist better with this.I have opted out of the question to see if perhaps other experts may have more information and can assist.Please do not rate or reply as that will send question back to my desk.Please stand by to see if another expert can assist further.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thankyou
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

No problem, Please stand by to see if another expert has more ideas.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Well i need to update the info, either leg to ground has 280v only and when i measure across it has 0v
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

WE should have the 460 between them, Disconnect from motor and see if we have it on the wires.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok so i read the schematic repeatly and realize one leg is suppose to connect to the dummy terminal of contactor 2, but somebody plug it straight to terminal 1 at contactor 2, so now i got 460v. Thankyou
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

So is it working now?

Ask Your Own HVAC Question
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,805
8,805 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I cannot find ANY installation videos that match my
Hi....I cannot find ANY installation videos that match my Honeywell RTH22B thermostat that I just bought. I don't understand how to get the wires into the black part … read more
David Bowden
David Bowden
Owner
473 satisfied customers
I have a Rheem Classic Super Quiet 80 that just stopped
I have a Rheem Classic Super Quiet 80 that just stopped heating our house this am. We had 40mph gusts today and I suspect they blew the pilot light out.… read more
airheatman
airheatman
HVAC Technician
8,805 satisfied customers
I have a 394gaw furnace the main burners light, stay lit for
I have a Bryant 394gaw furnace the main burners light, stay lit for 30 seconds then go out the pilot stays lit the whole time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Ruud water heater is leaking from the pressure valve on
My Ruud water heater is leaking from the pressure valve on top of the tank. The power is off. Earlier I flushed the tank, but not very good. Now when I turn on the main water valve to the tank I notic… read more
airheatman
airheatman
HVAC Technician
8,805 satisfied customers
I have a Honeywell he 311 and it keeps going off the purge
I have a Honeywell he 311 and it keeps going off the purge light stays on for a few then off and the machine never goes on … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have a carrier thermostat. Fan is working. However I'm
Have a carrier thermostat. Fan is working. However I'm unable to set a temperature and the heat won't come on. Has an error saying HP … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Trying to add Aprilaire 600M to Lennox furnace with iComfort
Trying to add Aprilaire 600M to Lennox furnace with iComfort tstat. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I've recently installed a HM700A1000 steam humidifier and
I've recently installed a HM700A1000 steam humidifier and everything is working fine except that it's not shutting off. It has the yellow LED constantly on which indicates the water level is to high w… read more
airheatman
airheatman
HVAC Technician
8,805 satisfied customers
Yesterday we completed installing a Goodman 60,000 BTU
Yesterday we completed installing a Goodman 60,000 BTU 80%eff furnace, brand new or if the package. It fired right up. Turned it off for the night after turning up to 80 to get s blast of heat before … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Installed new Goodman split heat pump outdoor unit runs even
Installed new Goodman split heat pump outdoor unit runs even with all low voltage disconnected … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
41 satisfied customers
Well j, Well just replaced a motor, No never dealt with you
Well j JA: I'll do all I can to help. How long have you been dealing with this? Customer: Well just replaced a motor JA: Do you plan on doing the work yourself? Customer: No never dealt with you befor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
A Rheem 40 gal gas hot water heater is flashing error code
A Rheem 40 gal gas hot water heater is flashing error code 11. What does it mean? Any danger? How to correct? … read more
airheatman
airheatman
HVAC Technician
8,805 satisfied customers
Goodman furnace acts as if it's not getting gas. Slightly
We just went through about 2wks of extreme cold temps. For whatever reason when the furnace has a lead time that lapses the furnace shuts down.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The thermostat to my fireplace reads er and the fireplace
The thermostat to my fireplace reads er and the fireplace won't come on … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My name is *********, and I have a Furnace and Heatpump.
hello Pearl, My name is *********, and I have a Bryant Furnace and Heatpump. Just this morning I set my heat up to 72 degrees to take the chill out of the house and after a few minutes the temp on my … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My 1962 Tappan Oven started squealing today out of the blue.
Hi, my 1962 Tappan Oven started squealing today out of the blue. Are we in imminent danger? And what can we do to fix it? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
After the burners are turned off, the clicker for the
After the burners are turned off, the clicker for the igniter continues to slick and has for about 1 hour. What can I do and is there a danger of fire. Thanks … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Carrier gas furnace won't ignite. Fault code 31. It will run
Carrier gas furnace won't ignite. Fault code 31 JA: Did you double-check the thermostat? And what about the pilot light? Customer: It will run blower after 5 minutes JA: Do you plan on doing the work … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question