My UD080R furnace no heat, fan can run I can run the fan

Customer Question
my UD080R furnace no heat...
my UD080R furnace no heat, fan can run
I can run the fan continously with no problem from the switch on the thermostat. As soon as I set the thermostat to "heat" the control panel fuse blows. The fuse will blow even if the thermostat is set to 60 degrees and the thermostat indicates the temperature is 68 degrees.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
11/10/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

Try unplugging one component at a time from the printed circuit board, until the fuse does not blow...the last item was the one with the short and needs to be replaced... if you get all of the plugs pulled from the board, and it still blows a fuse, the the board is bad.

That would be the laymans way of doing it, you will need 4 or 5 spare 3 amp fuses.

If you have a multi meter you can set it on Ohms, and unplug each item at a time and use the ohm meter to see if there are any dead shorts... that takes a bit of skill with the ohm meter.

Let me know what you think, we can go from there without a time limit, however I am off to bed shortly, if I miss you tonight I will pick up your response in the morning.

If you want to get deeper into the trouble shooting, attach a well focused, close up photo of the wiring diagram glued inside the service panel,you can use the paper clipicon at the right end of the toolbar at the top of this dialog box,Include a picture of the thermostat wire connections to the printed circuit board in the same area.

If there is no paper clip icon, look for the '+attach files' link at left of your send button.

I can mark it up with trouble shooting instructions. You will need a multi meter ($30 at a hardware store) and some experience working with appliances, let me know a lot about your skill sets in those regards.

We can go from there in the morning.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have measured it out with my Ohm meter (past electronic technician). I see shorts associated with switches on the thermostat when the batteries not not connected. The batteries skew the readings of the Ohm meter.
I think I already unplugged any optional equipment (AC and Humidifier).
I had a couple people double check the wiring at the furnace and the thermostat.
I was hoping it wasn't the control board, but I am afraid it is the control board, your comments almost confirm it.
Are there any places I can check voltages to confirm a problem with the control board?
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello again, the gas valve, blower motor, inducer fan and igniter relays are all mounted on the circuit board with plugs connecting each of those items to the board... you can unplug them one at a time and check for a dead short.

The problem is not likely to be at the thermostat.

I am off to bed in a few minutes, I will pick up the results of your tests in the morning.

.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
6,022 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,022 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am having problems with my humidifier. An Aprilaire Model
I am having problems with my humidifier. An Aprilaire Model 700.Every time it starts, some water leaks out of the valve as shown in the picture. Not much, would say about an ounce or two. Then the lea… read more
Chad DeYoung
Chad DeYoung
8 satisfied customers
I need help to determine whether my Aprilaire humidifier is
I need help to determine whether my Aprilaire humidifier is working. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,086 satisfied customers
I have a Bypass Humidifier, MODEL 445, and this season it is
I have a Bypass Humidifier, MODEL 445, and this season it is leaking water from the water tray. I went to remove the finger nut that secures the tray and it just split in half. could the finger nut be… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
346 satisfied customers
I have a Honeywell Humidifier Model HE360A1075. I need to
Hi , I have a Honeywell Humidifier Model HE360A1075. I need to get an operation manual to install the humidifier in my home. … read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Trane XV90 with a Aprilaire humidifier (model-440)
I have a Trane XV90 with a Aprilaire humidifier (model-440) attached as well as an air conditioning unit. It is all currently controlled by an Aprilaire thermostat (model 8348). I'd like to replace th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Where can I find a humidifier filter for Kenmore #42 29959?
Where can I find a humidifier filter for Kenmore #42 29959? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an HM512W1005 Direct Injection Humidifier. It
I have an HM512W1005 Direct Injection Humidifier. It currently connects wirelessly to a Honeywell thermostat. I'm trading that out for an Ecobee4 and need help knowing which wires to run from the humi… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am trying to operate a humidifier with 24volts coming from
I am trying to operate a humidifier with 24volts coming from a Nest thermostat. However, when I hook the 10' wire to the Aprilaire humidifier nothing happens. But when it is hooked with a very short w… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
346 satisfied customers
We have an April We have an, aprilAir humidifier 760. There
aprilAir humidifier 760. There is an excessive amount of water coming from a drain line. The unit is turned off, and there is high humidity in the area and crawlspace. Is this normal? Just discovered the leak, but we had a huge water bill for the last month. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Maytag de-humidifier runs but not remove any water from
My Maytag de-humidifier runs but not remove any water from the air. … read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
I have an air-o-swiss humidifier that is 6 years old and it
I have an air-o-swiss humidifier that is 6 years old and it turns on and sends out vapor for about 2 minutes and then stops is there a way to have it repaired or do I need to replace it? … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
I have just had an HE300 humidifier install on a new Trane
I have just had an HE300 humidifier install on a new Trane downflow gas furnace. When the furnace blower is running I can tell a fair amount of air is drawn through the vents on the HE300. It is not r… read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
The water is not running thru the humidifier pad. I took the
the water is not running thru the humidifier pad. I took the solenoid apart thinking it was clogged but forgot to check the water supply first. The water valve was open but not flowing until I worked … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Why is my furnace humidifier cycling on and off? -Rodgers
Why is my furnace humidifier cycling on and off?White-Rodgers HSP2000 Steam. When humidity reaches the control setting, it cycles on and off randomly.… read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Can you respond to an Aprlaire question Humidifier, Just
Can you respond to an Aprlaire question Humidifier … read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
If my Honeywell By-Pass Flow-Through Humidifier HE265B
If my Honeywell By-Pass Flow-Through Humidifier HE265B controller is not giving an error, but stays in Standby status regardless of how high I set the control knob, does that mean the control board is… read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
Just replaced a honeywelll tru steam humidifier with an
just replaced a honeywelll tru steam humidifier with an Aprilaire 800 model. I would still like to use the Visionpro thermostat that has the built in humidifier control. However the Aprilaire humidier… read more
Michael Ferryman
Michael Ferryman
82 satisfied customers
I have two furnaces with humidifiers the solenoid is
I have two Bryant furnaces with humidifiers the solenoid is connected to the HUM and Com terminals as shown in the wiring diagram but when the blower is running the solenoid is not powering up? I test… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x