I have a 373LAV furnace with a 33 code. I changed my filter

Customer Question
I have a Bryant 373LAV...
I have a Bryant 373LAV furnace with a 33 code. I changed my filter at the beginning of October, checked it today and it's still clean. My blower stays on and it does not ignite. In checking my 33 code possibilities, my flame rollout switches both have .4 ohm resistance when checking across the terminals. I do not have the red-button type. Ideas?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
11/6/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

There are two (2) blowers on your furnace... the small inducer fan (blower) and the main blower that circulates warm air through the house... I need to know very specifically which blower you mean.

LISTENTO FURNACE START UP
Stand next to the furnace after the thermostat has been turned off for 5 minutes. Listen intently as someone else turns the thermostat to heat and sets it for 85F.

You should hear the small inducer fan start right away.. then a faint click after 1 to 3 seconds, that is the pressure switch closing.

....then in 15 to 45 seconds you should hear 2 more faint clicks, that is the ignition relay and gas valve relay closing.

....then within 5 seconds you should hear the main burner fire..

----------

If the main burner goes off after 2 to 5 seconds or within a minute or so tell me about it and the number of seconds involved.

Repeat that a few times until you get familiar with the sounds, then tell me in detail how far the sequence goes before it stops.

It is also a good idea to replug all of the connections in the unit, that burnishes any oxidized terminal connections and will sometimes solve the problem,especially at the printed circuit card and in any sensor molex connectors. Do that with the power off to the unit of course.

We can go from there and get to the bottom of this quickly by these means... there will be subsequent tests on the printed circuit board. Using a volt ohm meter is very useful in very many cases, but not all cases, in some cases those reads can be *entirely misleading due to feed back in AC electronic circuits (not seen by the way in automotive DC circuits).

Ask Your Own HVAC Question
Customer reply replied 2 years ago
As soon as I put the cover panel back on, the big blower that fills the house with air comes on. It does not matter what my thermostat is set at - in fact, it is set to OFF. The 33 code gives me a short list of things to check. I am at the flame rollout switch stage.
Customer reply replied 2 years ago
I have to go to work now. I will be back at this issue around 4 pm PST.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks,

I will be in to about 10 pm tonight, then back all day tomorrow.

There are several things that will cause the blower to stay on at all times.

- a bad printed printed circuit card, fan relay contacts burned closed. (70% chance at this point)

- The furnace high limit switch is tripped, the card programming runs the fall all the time in that

case to insure the furnace does not over heat, (20% chance)

- Flame roll out switch open, 0 to 5% chance.

Please attach a well focused, close up photo of the wiring diagram glued inside the service panel,you can use the paper clip icon at the right end of the toolbar at the top of this dialog box,Include a picture of the thermostat wire connections to the printed circuit board in the same area.

If there is no paper clip icon, look for the '+attach files' link at left of your send button.

I can mark up the wiring diagram with trouble shooting instructions.

You can also perform a heat stress test on the printed circuit card..it is about 70% reliable.

Use a hair drier to slowly and gently warm the card to 120F(warm to the touch but not hot and not over140F)... if you get any change in behavior that means the card is bad...

A micro crack has opened in the printed circuit at a solder joint, or inside its CPU in that case .... or a short circuit has developed as the card expanded when you heated it.

Constant expansion and contraction as these electronics heat and during their duty cycles over the years is what wears these cards out.

It is also a good idea to replug all of the connections in the unit,that burnishes any oxidized terminal connections and will sometimes solve the problem, especially at the printed circuit card and in any sensor molex connectors. Do that with the power off to the unit of course.

We can go from there.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
6,022 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,022 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Which symbol on the Friedrich heating/cooling unit is for
Which symbol on the Friedrich heating/cooling unit is for heat? Thank you! … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My lennox heater is not heating. The thermostat is set. I
The thermostat is set. I did not check the filter, but it is only 10 months old and the fan is running, when I just trun on the fan … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace 58mcb080-20 gas valve will not open... i
carrier furnace 58mcb080-20 gas valve will not open... i confirmed 24 volts going to valve... replaced the valve and same problem... i jumped 24 volts from the transformer and it opens no problem... n… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I tried to install new Honeywell WiFi thermostat
Hi. I tried to install new Honeywell WiFi thermostat th9320wf5003. And it doesn't show display. In … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Weil-Mclain boiler that keeps going int lock out
Hello we have a Weil-Mclain boiler that keeps going int lock out mode. It runs for about 20 seconds and then shut off with a solid red light. We now have an amber and red solid light. Can you help? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Lady hru? I'm troubleshooting an American Standard Freedom
Good evening lady hru? I'm troubleshooting an American Standard Freedom 80 furnace that's indicated to me the thermal protection device is open. What do I need to do to fix the issue? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a question about an electric tankless or on demand
hello, I have a question about an electric tankless or on demand water heater … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace won't start. Furnace is in attic. I disconnected
Yes, I disconnected thermostat and read no voltage on any leads … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 19.9 Rheem 120 volt water heater it does not have a
I have a 19.9 Rheem 120 volt water heater it does not have a drain valve . how do I drain it ? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Trying to install Honeywell lyric t5 wi fi thermostat to
Trying to install Honeywell lyric t5 wi fi thermostat to control heat pump with 7 wires … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
I have an enviro gas heater 828, is repairs possible ??
Hi I have an enviro gas heater 828, is repairs possible ?? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The last couple days there has been a bleech like smell
The last couple days there has been a bleech like smell throughout our house. I think I can smell it around our furnace. What could this be? Our whole house stinks. Central air, LP furnace with electr… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My 3 year-old gas boiler has been flipping the spill switch
My 3 year-old gas boiler has been flipping the spill switch and turning off in very cold or windy weather. I have had a plumber and chimney person look at the problem and they are saying my boiler is … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old crown dg35 furnace and suddenly the,burner
Hi, I have an old crown dg35 furnace and suddenly the,burner flame is way too high. Why would the flame change by itself and how do I adjust it down? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
JUst put in a new flame sensor on an Amana Commander 80 but
JUst put in a new flame sensor on an Amana Commander 80 but still have the problem of the furnace flame starting then stopping … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a reznor f50 heater I am tying to get in use. I see
i have a reznor f50 heater I am tying to get in use. I see two wires n do not know where they go. It seems they are on some ECO part … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My screen is unresponsive. I change I changed the batteries
my screen is unresponsive. I change I changed the batteries and it will not respond. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have a charmglow electric fireplace and it blows hot air and
have a charmglow electric fireplace and it blows hot air and turns to cold air … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,078 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x