hi hows it going i am attempting to fault find a hitachi ducted ac unit model RUA-30HS
the fault that is occering is i am getting normal high discharge pressure and sunction presure i have just replaced the reversing valve as it was faulty but now i am getting this strange fault i am suspecting it could be a faulty checkvalve so can you plz help me out
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
10/31/2015
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, can you tell me if used a dry nitrogen purge while soldering the reversing valve, and a vacuum pump after that work was done and before recharging the system?

Did you replace the refrigerant filter drier, with one that has a two way arrow on it.

We can go from there.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I used dry nitrogen faced system out and replaced filter dryer with a two way filter the comppressor has just recently been replaced also
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks..

Tell me what the outside and inside air temperatures are exactly...at the same time I need to know the head and suction pressures exactly... and what refrigerant you have in the system, and if you liquid charged it, or vapor charged it.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I charged the system by weight I put 8 kg of refrigerant into the system according 2 the sticker on it it requires 10 kg I liquid charged it into the discharge side the refrigant I am using is r22 the suction pressure I am getting is 120 psi and discharge pressure I am getting is around 380 psi also the system is a capillary system so there is no sight glass on systyem outside temp was like 45 c and it was like 35 inside this ducted ac has 2 stages on it and the other compressor pressures were 60 psi and the same discharge pressures
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello again,

Please verify that the house is 35C inside (equivalent to 95F) and that the outside air is at 45C or about 112F... if that is the case, you are way out of range for evaluating the refrigerant charge... the system is not designed to run efficiently at all in those temperature ranges... the pressures.

So far however it looks like the refrigerant charge might very well be entirely correct and that the system is not able cool the house down properly in these conditions (net capacity drops by about 25% as you approach 45C outside... a capillary tube system will then run the indoor coil temperature up to 21 or 22c , and that is not enough to do a lot of cooling,

Tell me the voltage supplied to the unit, and how much each leg of of the 3 phase power at each compressor is reading... it should be very close to full load amperage in these conditions. I need the exact numbers on each leg.

The system is rated at 310,000 btu/hr or around 30 tons, it will typically cool 10,000 to 15,000 square feet of space in a modestly warm not overly humid climate.

Tell me about the space, square footage and type, office space, industrial mfgr, restaurant etc... and the nearest city so that I can assess the weather conditions for you.

We can go from there.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

ooops I typed 'house' it should be building.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the building is a big 200 man mess hall located in mount Isa qld each leg on the compressors is drawing roughly 22 amps each there load limit is 24 each the compressor is also tripping out on internal load which is caused by the high suction pressures what I don't understand though is the other stage on the ducted unit is running all ok drawing the same amps but a normal suction pressure it is like a 30m by 10 m shed 4 metre high and fully insulated the unit has just stared doing this fault would a jammed open check vave located near the capplary line in cause this problem
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Hello again, it does indeed sound like the check valve is bypassing liquid and is driving the suction pressure up. If the check valve you are talking about is fit at the indoor coil, it can be removed, and capped off since the system can no longer go into heating mode.

Before you do that however, I would like to see pictures of the capillary tubes and check valve, taken at several different angles and taken from about 5 feet away so that I can see how the entire coil is piped in that area.

Another picture that shows all 3 compressors, taken from about 10 feet away so that i can see all 3 compressors and the suction line piping will be helpful as well.

You can use the paper clip icon at the right end of the tool bar above, or the '+ attach fines' link to the left of your 'send' button to send me the pictures.

With such a hot building inside, 35C, I would expect the suction pressure to be high..

Tell me what the other stage suction pressure is running, and very importantly I need to know if the suction line on that compressor is running cool, cold or sweating.

We can go from there.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Subject: heat pump system subcooling requirements for a
subject: heat pump system subcooling requirements for a downflow air handler.I have Rheem 6 ton variable speed split heat pump system. My air handler is installed in downflow position. Air handler is … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have 78 low side 231 high side r22 is this due to over
i have 78 low side 231 high side r22 is this due to over charge? … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Billy, I have had the Fedders (remember them) 15K Split HP
Hi Billy, I have had the Fedders (remember them) 15K Split HP for a few years. Last year I had only an 8F inside temp spred so I put a little R410a in to match the gauge outside temp. Inside temperatu… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a Nor norlake walk-in cooler / freezer and the
Hello! I have a Nor norlake walk-in cooler / freezer and the freezer is currently reading 22 deg. And doesn't seem to be kicking on to cool down It's usually at or below zero … read more
ApplianceTech
ApplianceTech
President
Associate Degree
1,599 satisfied customers
I am an HVAC contractor in Southern DE. I have a performance
I am an HVAC contractor in Southern DE. I have a performance issue with a York system that another contractor installed and after going through a few things I believe they mismatched the outside and i… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a rheem unit. Cannot get supply duct temp below 62
I have a rheem unit. Cannot get supply duct temp below 62 degrees 410-ref? … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Have 50HJ066 acutrol metering device changed refrigerant to
Have 50HJ066 acutrol metering device changed refrigerant to 407c unit takes 10 lbs on label but had to charge 16 lbs but metering device freezing … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having trouble getting more that 10 degrees of cooling between the return and the vent. I've adjusted the charge to the spec in the manual for a pi… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
If the reversing valve has a internal short like you said is
if the reversing valve has a internal short like you said is that why my suction psi is ;low… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Three ton goodman spiit pressures are great everything
three ton goodman spiit pressures are great everything runing but not cooling unit is 7 yrs old … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Is the head pressure & discharge pressure same thing? And
Is the head pressure & discharge pressure same thing ? And what about back pressure & suction pressure !… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a reem 2.5 ton unit. The head pressure is 300 PSI. It
I have a reem 2.5 ton unit. The head pressure is 300 PSI. It is now cooling fine but the head pressure seems too high… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm an HVAC Tech in Tennessee and was replacing a scroll
I'm an HVAC Tech in Tennessee and was replacing a scroll compressor in a 1.5 Ton Rheem Heat Pump.After brazing up my compressor and filter dryer, I performed a leak check.After which I pulled a vacuum… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Low head pressure and slightly high suction pressure on a
low head pressure and slightly high suction pressure on a rtu gas pkg … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
My suction pressure is 125 and liquid line pressure is 275.
My suction pressure is 125 and liquid line pressure is 275. This is after I replaced a bad compressor. Outdoor ambient is 95 degrees. Indoor temp was 85 degrees. The indoor coil wet on the lower part … read more
Appliance Guru
Appliance Guru
17,062 satisfied customers
I have low suction pressure and the head pressure is running
hello, I have low suction pressure and the head pressure is running high Checked liquid line temp and it was running very hot Cleaned both coils and checked filter W HAT MIGHT BE THE PROBLEM … read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,961 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x