In need of help troubleshooting Carrie 8000 ts. I turn on

Customer Question
In need of help troubleshooting...
In need of help troubleshooting Carrie 8000 ts.
I turn on heat switch and blower turns on, but no heat.
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
10/31/2015
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,528
Experience: Furnace, A/C and heat pump specialist.
Verified

Look on blower housing for control board and see if we have a light flashing.If so tell me the pattern of the flash as that will tell us where to start troubleshooting

Ask Your Own HVAC Question
Customer reply replied 2 years ago
LED is constant
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Does it change when furnace fails to light? It should give us an error code such as two short flashes followed by 2 long flashes

Ask Your Own HVAC Question
Customer reply replied 2 years ago
no. LED remains solid. The fan/blower almost immediately turns on.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Does fan stay on or run for 90 seconds and shut off?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the fan will run indefinately. I have to turn off the heat.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Does the little vent motor ever come on? If not do you have ammeter to see if it is getting power on call for heat?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
no. it does not. I have a meter. tell me where to check for power
Customer reply replied 2 years ago
I dont know if it makes a difference,but this unit has another thermostat connected to it as well
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

You may have a zone system if you have two thermostats, but we still should get heat if this is the main thermostat.I actually have a phone call and need to step away.I will open to other experts while I am gone and will check in when I et off phone.

I have opted out of the question to see if perhaps other experts may have more information and can assist.Please do not rate or reply as that will send question back to my desk. Please stand by to see if another expert can assist further.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK I am back. Can you get a volt meter so we can do some troubleshooting? The firdt thing that has to happen is we have to get power to the vent inducer motor.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok. I have a meter. Which wires do I test?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Let me know when you are online.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
It will be tomorrow afternoon. I have to work. Thanks so far
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Tomorrow afternoon is fine.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I'm ready when you are
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Ok on furnace control board where thermostat wires hook up, do you see a C and an R terminal?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have a control board. I can see that it calls up the heat and the blower. I realize that the control board connects up to the furnace board. I'll open the panel and locate them.
Customer reply replied 2 years ago
Holy smokes! There's a half million wires! I believe I have it located.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK what I want you to do is this.first make sure we are getting 24 volts between that R and COM on board.I feel sure we are but want to verify.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
OK. Tested it and am getting 24 v
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Excellent. Next I want you to unplug the wires at the little inducer vent motor. Put meter probes into the connector that you unplugged from motor. Power off then back on to reset board. Then call for heat and see if we get 120v at the plug. (Door button of course needs to be in or panel in place to hold button in.)

Ask Your Own HVAC Question
Customer reply replied 2 years ago
far no voltage. I unplugged the motor (has a red, black, and white wire). I placed the probes into the plug making contact and get no reading (this is with the heat and blower called and door switched in the operating (closed position)
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

But error light is staying solid?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
error light stays solid green which states that it is receiving 24 volts
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK on call for heat, the board checks low heat and high heat pressure switches to verify they are open. If so, inducer should start.If not we should get either a 31 or 32 error code.

Lets do this. On furnace control board lets jumper R to W and see if inducer will start.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. have jumper wire and turned heat on. the blower came on. I have no idea how to interpret the LED but it has a long blink, then a second or so pause then 2 quicker blinks.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK let me know if that changes after 90 seconds

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Gee wiz. Got the heater to come on. While I was typing this up, I could smell the heater and went to check and it is now on
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK that implies the issue is with the thermostat rather than the furnace. Has thermostat been replaced since heater last worked?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No. Interesting though... The thermostat went out last year and had the people that manufactured it (XCI Controls) help troubleshoot it and found it was faulty. The new one I installed is a LUX
Customer reply replied 2 years ago
I assume the jumper makes the heater come on regardless once the door button is depressed. Correct? I am going to let the button out cause it is getting mighty hot
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Jumping R and W bypassed the thermostat. Thermostat is not signaling furnace to come on.Do you know if you have a heat pump outdoor unit?If unsure give me model on outdoor and I can tell you.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the XCI Smartzone-4 board in incorrect? When I turn the temp up to call for heat, I can see the green light (which indicates it is calling for heat) and red light (indicates it is calling for the blower) come on. I believe the wires from the thermostat go to the smartzone board first then to the heater. Correct?
Customer reply replied 2 years ago
It is not a heat pump.. I think. Carrier model 38TXA036330 serial 2703E28850
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Ok tell me what thermostat wires connect where on furnace board.Then lets move to thermostat. Remove front of thermostat and give me model on the thermostat, then tell me what wires are connected where.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

A picture would save a lot of typing if you can take a pic.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Send me one also of thermostat with front removed.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Next tell me model on thermostt

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Next tell me model on thermost

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Make is LUX. guessing model is TX9600TSa
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Lets look at the dip switches as shown on page 18/19 here

http://luxproducts.com/IMG/pdf/tx9600tsa_manual_en.pdf

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

1 should be to right

Ask Your Own HVAC Question
Customer reply replied 2 years ago
all of the switches are to the right. Same as the manual shows
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Ok lets do this. Remove the Red and white wire at thermostat and touch them together or loosen screws and move white over to the Rh slot with red and see if furnace will come on.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Is the jumper wire still to be in place or remove it?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Remove the one at furnace. What we are doing is basically same thing but at thermost

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have the white connected to the Rh. The smartzone board shows the green light and red light on, but only the blower is on. No heater.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

On smatzone board lets check between C and W and see if we have 24v?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I reset the HW button and put the wires back where they are supposed to go and put everything back in order. We are still in the same boat. The thermostat calls up the heat and blower. The blower comes on but no heat.
After I typed the above, I was attempting to check the C and W wires on the smartboard. While I was trying to do that the W2 O/B yellow led light came on. A couple of minutes later the blower turned off, the inducer vent motor turned on, the ignition light came on, but did not light nor did I hear gas being expelled. After approx 10 seconds, both the vent motor and ignition light turned off and the fan came back on and continues to run.
I am still attempting to check for 24 volts. The slots are tiny and there are no exposed portions of the wires. I can disconnect it at the furnace end and check there. Is that acceptable?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Ok it seems like we may have a couple of things going on. First of all. let me say the blower on for 90 seconds is normal when turning power on to furnace.But then when the inducer comes on and igniter does not light we should get an error code on the board telling us what failed in the circuit by giving us a flash code such as three long and one short flash or something.

To be honest with you I am not real familiar with the smartzone board and how it operates. Rather than mislead you I feel it fair to you that I opt out and see if maybe another expert familiar with the board pick up here.

Be sure if another expert picks up the question to explain that you have this smartzone board and make sure they are familiar with the board and how it works in conjunction with your furnace.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. Thanks thus far. Glad we got the furnace to ignite.
While I was up there trying to get a voltage reading (it has happened twice now) the process of attempting to light has repeated itself with no flame. I will continue watching to see if an error code comes up.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

I will keep monitoring the question to see if anyone picks it up or if you reply with a code.

PLease wait to see if we can help before rating answer.

Leaving a poor service rating will not automatically refund your money,but reflects poorly on your expert. You have to request a refund if not satisfied with the information provided being accurate.

If no expert can help and you are unsatisfied, we can request a refund of your deposit

Ask Your Own HVAC Question
Customer reply replied 2 years ago
No worries. You guys have done great. Well worth the money.
So if I change out the thermostat, it should potentially run correctly? If so, I sure don't mind getting one and going that route.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Possibly but I am still concerned why you are not getting an error code when ignition fails

Ask Your Own HVAC Question
Customer reply replied 2 years ago
It has not tried to reignite again. I will try through the evening and see if it will do it again. Seems when I was messing with the wiring is when it would cycle but I never looked at the furnace LED sensor. Next time it happens, I'll be watching it.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Sounds good.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I spoke with the people that make the XCI board and told them everything we have done to date. They said that if you are not getting 24V at the furnace (since the thermostat goes to the XCI board, then goes to the furnace), then the SmartZone board is out and needs replaced. Make sense to you? I am going to wire the thermostat wires directly to the furnace and see if the furnace works that way. If it does, problem solved. It will be a few hours before I get to do that but will send you the outcome. Thx
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Makes sense .Please let me know.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. I have wired the thermostat to the furnace and it works as it should. Conclusive evidence that the XCI SmartZone board is the problem. The XCI guys said specifically the W is what is out after talking to them again. The board is approximately $150 and can pick it up tomorrow locally.
I would have pulled my hair out trying to figure this out by myself and probably spent way more just troubleshooting this without your help. Thanks again.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

I am not real familiar with that board but knew we weren't getting signal all the way to furnace.Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.

Ask Your Own HVAC Question
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,528
8,528 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier Furnance that is making intermittent
I have a Carrier Furnance that is making intermittent squeaking noises at startup, while running but always just prior to shutting off. I feel the furnace works fine except to this. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier 58MCA080 gas furnace with continuing
I have a Carrier 58MCA080 gas furnace with continuing issues. Need some help diagnosing current problem.… read more
airheatman
airheatman
HVAC Technician
8,528 satisfied customers
Trying to identify thermostat wires from an old Carrier
Trying to identify thermostat wires from an old Carrier Comfort Zone to review options for upgrading the thermostat. … read more
airheatman
airheatman
HVAC Technician
8,528 satisfied customers
I have a 20 year old carrier gas hot air furnace. For the
Hi, I have a 20 year old carrier gas hot air furnace. For the last three years have had the occasional issue with the furnace not coming on. I look at the unit for obvious things like lose wires, etc.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have carrier c48175d. changed thermostat to honeywell.
i have carrier c48175d. changed thermostat to honeywell. carrier shows green to A yellow to B white to C and red to D. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Just bought a Nest, but it's incompatible with my Carrier
Hi Hi. Just bought a Nest, but it's incompatible with my Carrier Infinity system. what to do? Rewire? Or find a different thermostat? If so, which one? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH NEEDS TO BE REPLACED. DO YOU RECOMMEMD A ONLINE PART. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Is there a battery on my carrier infinity thermostat? The
Is there a battery on my carrier infinity thermostat? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Carrier TP-PRH01-A programmable thermostat but it
I have a Carrier TP-PRH01-A programmable thermostat but it is not WiFi capable. I would like to replace it with a Honeywell WiFi programmable thermostat. Can you tell me which model(s) you would recom… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently replaced my furnace control board. The furnace is
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Boar… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an amana furnace control board with an led flashing 3
I have an amana furnace control board with an led flashing 3 times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need help with my -Rodgers furnace control board 50e47-060
I need help with my White-Rodgers furnace control board 50e47-060 on a Trane furnace. It has a blinking red light. On the unit it says " steady red light- replace control, blinking red light-referred … read more
type2technician
type2technician
253 satisfied customers
I have a nordyne KG7TC-080D, with a furnace control board
I have a nordyne KG7TC-080D, with a furnace control board #624790/920916. this is a 2-stage upflow unit. Furnace ignites but goes out wihin seconds. flame sensor replaced, still the same issue. Has in… read more
airheatman
airheatman
HVAC Technician
8,528 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.