I have a trane model 4tyk85a1p0caa after moving it to a new

Customer Question
location last year it worked...
I have a trane model 4tyk85a1p0caa after moving it to a new location last year it worked perfectly. after about 9 months it developed a problem dripping water down the wall and freezing up. We cleaned coils and check drain it was clear. Now consistently it drips down the wall. I checked low side pressure about a month ago and it was 160psi. Today I rechecked and the low side was 50 psi and both ac lines are very cold
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
10/9/2015
HVAC Technician: Tim H., HVAC Professional replied 2 years ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Please provide all information I request as it makes it more difficult to troubleshoot something when I'm not there onsite. Essentially, you become my eyes and ears. Thanks for the opportunity to help. At the end of our dialog, you will have a chance to rate my service, but please wait until we are finished and you're satisfied you have all the information you need.

I'm sorry to hear about your issues with your mini split. It sounds like it has lost charge and this most likely happened as a result of the move. The dripping water can be caused by the coil icing up and melting on the off cycle.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
It worked fine for 9 months after we moved it. OK so if I understand correctly here I need to add refrigerant. How do I know when I have an adequate charge? Also in your your response you indicated you needed more information. Is that correct?
Customer reply replied 2 years ago
one thing that's not adding up for me is if it is low on charge why does it still blow ice cold? And why are both ac lines cold my experience is that small line would be hot and the large line cold?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Sorry, was out doing service calls all day. On these mini split systems, most of them have what's called a "critical charge". That is, you weigh in an exact amount of refrigerant. This must be done by removing what's in there, and then using a refrigerant scale, an exact charge weighed in according to the manufacturers specs. The reason both lines are cold is because the system is not doing what it's supposed to be doing due to low charge issues.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I'm going to recharge this weekend I will let you know if my problem gets resolved
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

OK, thanks for the update.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Did you have additional questions on this? Otherwise, good luck! Thank you for using Just Answer and please don't forget to rate my service as that's how experts get paid (Thanks in advance for any bonus left). Otherwise experts work at their own time and expense. Feel free to post back with any additional questions.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I still had not gotten around to recharging system and today unit started spitting ice balls. I once again revisited low side pressure reading and now it is 150 I had gotten that reading a couple of months back. What are your thoughts on that?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Have you zeroed out your gauges before checking?? Sure they are accurate?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
they are accurate
Customer reply replied 2 years ago
gauge zero out the gauges are accurate
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

If there was a restiction, it may have broken loose. 150 PSI is about a 53 degree coil, about right for an average day. Which is why I asked about guages. However, if it is freezing up, then that indicates a problem.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
What do you suggest I do next,?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

Probably will need to evacuate system and purge with nitrogen, then vacuum and recharge. I would also pressure the system with nitrogen when the charge is out and see if it holds pressure to make sure you have no leaks. It doesn't make sense that the pressure was low one day and (almost) back to normal the next unless there is a restriction in the system. Also, make sure it is not an intermittent blower issue because loss of evap blower would cause low side pressure to go way down and coil to freeze.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Evaporator motor blows very strong I will check pressure again in the morning and report any changes
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

OK, thanks

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Good morning Tim H. This morning no icing at evaporator but a small amount of water is dripping down the wall both lines at condenser cold and dripping a small amount of water room is not as cold as usual pressure reading is now 130. What are your thoughts now?
Customer reply replied 2 years ago
Did you get my last message?
HVAC Technician: Tim H., HVAC Professional replied 2 years ago

I still think you need to do the evacuation and purge as mentioned previously, then weigh in an exact charge.

Ask Your Own HVAC Question
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
3,971 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
72 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit,
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit, Model MS-A12WA). That recently started leaking a pretty significant amount of water. The water must be building up inside the unit and then at s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Fault code 26 and 59 at same time. Evaporator frozen
Fault code 26 and 59 at same time. Evaporator frozen condensation drain was blocked now open .blower mother will not run when set to fan only… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
My refrigerador compressor is running so is the condenser
My refrigerador compressor is running so is the condenser and evaporator fan and all the lights but it wont cool at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,078 satisfied customers
In my AC unit outside, there is condensate on the ground. I
In my AC unit outside, there is condensate on the ground. I am sending a picture. The condensate usually is taken inside isn't it? What could be the problem?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have a gibson C5BA-T42C- evaporator coil. Had a new
I have a gibson C5BA-T42C- B evaporator coil. Had a new condenser put in. they didn't change the coil. Said it would be ok. They used r410a freon. Case on this coil say r22. Is this coil going to work… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a furnace with an evaporator pump that i had to
I have a furnace with an evaporator pump that i had to repace all the relays and also the thermostat. After all is done it worked great for the winter except in order for it to work i had to put the t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x