I have a burnham v-16-a-t oil fired tankless coil system.

Customer Question
Last year I replaced the...
i have a burnham v-16-a-t oil fired tankless coil system. Last year I replaced the thermostat control unit ( rebuilt) my circulator pumps do not turn on unless the unit has fired regardless of temp. I also have to keep the hi and lo setting at 140 H and 120 L to keep it from going over 180. Is the thermostat control bad?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
10/7/2015
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,332
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Could be a bad control or at least one that's out of calibration (nothing you can do to re-calibrate). Keep in mind the circs won't run unless the boiler temp is above the lo limit set point. The lo limit is what maintains boiler water temp for DHW. The hi limit is the space heating function.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
if the lo limit is set to 150 and the hi limit is 180 and the water temp is 160 the circs should run, even if the calibration is off. so what is keeping them from running? and why do they only run once the unit has fired?
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Yes, if the control is functioning as designed. The circs should run as long as there is a call for heat (unless the boiler temp is below lo set point). The burner runs when there is a call for heat and the boiler temp is below the high limit. During a call for heat once off on limit the burner won't fire again until temp drops below hi less diff. Lo should always be set below hi less diff.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
right now I am 180 hi 150 lo and 15 on the dif. and the heat wont circ. when I turn on thermostat, is my control unit bad? It only activates the circ. pumps while fired.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

What's the boiler temp? If it's below 150 the circs won't run and the burner should be firing.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

The only time the circs will run and the burner not fire is if there is a call for heat and the burner runs up to hi limit then shuts off on limit. While the temp is falling back to hi - diff only the circ will run.

Ask Your Own HVAC Question
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,332
22,332 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My carrier thermostat control 's display just went blank. I
My carrier thermostat control 's display just went blank … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Trying to connect new wires to a Weil-McLain Cga boiler.
Trying to connect new wires to a Weil-McLain Cga boiler. They are connected into plastic clips or plugs that are then connected to the circuit board. I'm not sure how to remove the wires from the plug… read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
Gas boiler thermostat controles circulating pump hot water
gas boiler thermostat controles circulating pump hot water remains hot and is distributed by convection, how correct … read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
I have a Hydrotherm Boiler that needs a pressure switch
Second opinion] I have a Hydrotherm Boiler that needs a pressure switch BM8026. Model of Boiler is HI-165B. Can you help me … read more
Elliott Oxton
Elliott Oxton
NVQ Level 2
4 satisfied customers
I have a Hydrotherm Boiler that needs a pressure switch
I have a Hydrotherm Boiler that needs a pressure switch BM8026. Model of Boiler is HI-165B. Can you help me … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Burnham boiler will not start. It was way over filled. I
Burnham boiler will not start. It was way over filled. I have drained mostly clean water out. Site glass is two inches empty. Red light on black box comes on when I switch the unit on. Other units in … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Boiler is calling for HW but nothing is on? Cadet heating
trying if its easy enough and not required plumbing work … read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
My Utica boiler will not come on. A week. I tried the
a week. I tried the circuit breaker, that's on. I drained the boiler. everything looks fine … read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
Boiler furnace is working well and heating the home nicely
Boiler furnace is working well and heating the home nicely but we run out of hot water after 15-20 minutes of showering. There is a boiler mate that I suspect is the issue but am not knowledgeable eno… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a Weil mclain boiler, and a nest thermostat. the
I have a Weil mclain boiler, and a nest thermostat. … read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
I have a -Rodgers model 1F97-371 thermostat controller. How
I have a White -Rodgers model 1F97-371 thermostat controller. How do I get it out of the lock mode?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Brought a boiler from nome heating. Bought a boiler from
bought a boiler from mike west nome heating for eght thousand dollars need to insurance for my boiler … read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
Is there a zigbee thermostat controller for a gree ptac? I'm
is there a zigbee thermostat controller for a gree ptac? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Where is the fuse in my hvac unit. The thermostat control
Yes. The thermostat control shorted out. I suspect a blown fuse.… read more
Rick
Rick
HVAC Supervisor
22,332 satisfied customers
I need to replace a Zone Perfect Plus thermostat controlling
Hi, I need to replace a Bryant Zone Perfect Plus thermostat controlling two zones. My contractor is quoting $1300 plus to replace it and says there are no cheaper alternatives. Is there any simpler af… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
What is the best attic exsaust fan thermostat controlled for
What is the best attic exsaust fan thermostat controlled for an 1800 sf house? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
My honeywell thermostat control panel displays only 5 empty
My honeywell thermostat control panel displays only 5 empty boxes on the bottom of the display screen … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x