I have a Takagi Jr 2 that is about 4 years old at our

Customer Question
Hello. I have a Takagi Jr...
Hello.
I have a Takagi Jr 2 that is about 4 years old at our cottage. Over the past year the hot water output has been intermittently turning off. It's been getting worse as of late, running from anywhere from 1-2 mins up to maybe 5 min before going cold. But now it won't turn on at all. The unit ignites for about 1-2 secs then the flame goes out. After three tries it throws an error code 12, flame sensor I think it's called. I have checked most of the troubleshooting items, cleaned the flame sensor, but makes no difference. Still ignites for about 1-2 secs and retries 3 times then throws error code 12.
I do not suspect propane as the problem as it is running off a 100lb tank which currently is full and all other gas appliances are running flawlessly.
I suspect it is the main pc board but would like to ask an expert first.
Thanks in advance, Steve
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 17 minutes by:
9/13/2015
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,064
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Do you have the manual? Did you check the other possible causes in the manual?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have downloaded the troubleshooting manual. Error code 12 flame loss.
1. Check high limit switch... Ok
2. Check gas supply... Gas Ok
3. Check gas pressure... OK
4. Check that the clear plastic tube connecting the proportional gas valve to the combustion chamber is
attached... Cannot find this tube. Maybe refers to a different model??
5. If the flame comes on for 1‐2 seconds but then goes
out, clean the flame sensor... Yes it does! Cleaned flame sensor using 220 grit sandpaper being careful to not bend the probe. Was not that dirty to begin with. Still same problem. No change.
6. The overheat cutoff fuse may have been compromised... Check continuity. OK
7. Check for blockages in venting, such as bird nests, animals, or trash... OK
8. PC Board fault or Gas Solenoid fault... Have not checked solenoid and unable to test board.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Are there any visual defects on the board, like a burn or discoloration? Does the burner ignite then go out or not light at all? If it doesn't light do you hear a buzzing/ticking sound when it should fire up? An visible leaks from the heat exchanger? did you check for broken wires/bad connections?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Cannot see any visual defects. The burner does ignite but then goes out a few seconds later. Visually everything looks perfect.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Could be a bad flame sensor rod. The next step would be to replace it. It's unlikely but if the burner is clogged near the flame sensor that could be causing this.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Ok. I will order one and get back to you. I only have weekends to work on it as it is at our weekend cabin.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

If the burner hasn't been cleaned/checked in a while you should do that first

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have already cleaned it. No change.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Ok, if you're sure about the connections then you're down to the sensor or the board.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Do you know what the voltage is supposed to be coming back from the sensor when the flame is on?
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Typically 4 to 12 micro amps. Note that's micro amps not milli amps

Ask Your Own HVAC Question
Customer reply replied 2 years ago
not really measureable.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

It is measurable but you need a meter that can read micro amps.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Thought I might have found it. A slightly corroded connection at the probe where the wire attaches. Started working again, but now it's back to how it was a few weeks ago. On for a few minutes then cuts out. Then back on again. Then cuts out. No errors.
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

Given the extremely low voltage signal from the sensor the connections must be flawless. the behavior you describe, in light of past errors, still indicates a flame rectification issue. Since you don't have any errors showing now it does cast more doubt on the board. But if you don't have a meter that can read micro amps I'd replace the flame sensor rod primarily because it's a lot cheaper than a new board.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I think I'll buy both. It may be the sensor but I also know the board is problematic so either way I'll have a spare of one or the other. I'll have to let you know how it goes in a week or so.
Do you have know of a preferred supplier preferably in Canada?
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago

I'm in NH, I don't know any suppliers North of the border.

Ask Your Own HVAC Question
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,064
23,064 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Centurion 2 not working with the flashing indicator
I have a Centurion 2 not working with the green flashing indicator 4 time. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Collector flue box gets extremely hot to touch. It's a
Collector flue box gets extremely hot to touch JA: Just to clarify, what type of fireplace is this? Customer: It's a furnace JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything else… read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick
Rick
HVAC Supervisor
23,064 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have Yorx High efficiency tubular heat exchanger, im not
Hi, my name is***** have Yorx High efficiency tubular heat exchanger, im not sure wich model though GY9S , GM9S, or GF9S. There is water leaking from the white PVC pipes, can I just cut them out and r… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x